WIRING DIAGRAM, MILLENNIUM MODEL Y K (STYLE D) LIQUID CHILLERS MICROCOMPUTER CONTROL CENTER WITH ELECTRO-MECHANICAL STARTER
JOB DATA:
CHILLER MODEL NO. YK ________________________________________________________NO. OF UNITS _____________
COMPRESSOR MOTOR ______________ VOLTS, 3-PHASE, _____________ Hz
OIL PUMP MOTOR _____________ VOLTS, 3-PHASE, _____________ Hz, _____________FLA
REMARKS:
2
YORK INTERNATIONAL
E L E M E N T A R Y D I A G R A M
R E V . 035-15977 (R E V . A
)
FORM 160.52-PW1
FORM 160.52-PW1
3A YORK INTERNATIONAL3
YORK INTERNATIONAL
FORM 160.52-PW1
4
3B YORK INTERNATIONAL YORK INTERNATIONAL
FORM 160.52-PW1 NOTES:
1.This wiring diagram describes the standard electronic
control scheme for use with an electromechanical starter.
For details of standard modifications, refer to Product Form 160.49-PW13.
2.Field wiring to be in accordance with the National Elec-
trical Code as well as all other applicable codes and specifications. See Product Form 160.49-PW10 for field wiring connections.
3.Numbers along the left side of diagram are line identifica-
tion numbers. The numbers along the right side indicate the line number location of relay contacts. An underlined contact location signifies a normally closed contact.
4.Main control panel Class 1 field wiring terminal connec-
tion points are indicated by numbers within a rectangle,
i.e. 15 . Main control panel factory wiring terminal con-
nection points are indicated by numbers within a triangle,
i.e. 5 . Component terminal markings are indicated by
numbers within a circle, i.e. C1 . Numbers adjacent to circuit lines are the circuit identification numbers.
5.To cycle unit on and off automatically with contacts other
than those shown, install a cycling device between ter-minals 1 & 13 (line 37) (see note 9). If a cycling device is installed, jumper must be removed between terminals
1 & 13 .
https://www.wendangku.net/doc/299857849.html,pressor motor starter with starter interlock contacts
(rated 0.5 to 1.0 amp @ 24 volts A.C.) must be per Form 160.45-P A5.1. Control panel shall be grounded.
7.Units installed in Canada must have a field supplied
CSA approved 30 Amp disconnect switch and a 20 Amp dual element fuse mounted external to control panel for 115 volt control supply.
8.To stop unit and not permit it to start again, install a stop
device between terminals 1 & 8 (Line 33) (see note 9).
A remote start-stop switch may be connected to termi-
nals 1 , 7 & 8 (Lines 32 & 33) (see note 9). Remote start-stop switch (Line 32) is operative only in the “re-mote” operating mode.
9.Device contact rating to be 5 milliamperes @ 115 volts
A.C.
10._____________
11.Contact rating is 5 Amp resistive @ 120 volts A.C. or
240 volts A.C.
12.Three phase oil pump must be properly phased L1, L2
& L3 corresponding to phase sequence A, B & C. 13.To check motor rotation on initial start-up, install mo-
mentary switch between terminals 24 & 25 (line 41).
Depress start switch. After approx. 30 seconds, jog mo-tor with momentary switch. When proper rotation is ob-tained, replace momentary switch with jumper. Switch must have a minimum contact rating of 2 FLA., 10 LRA at 115 Volts A.C.
14.Motor overload (CM) is set to trip at 105% FLA. During
momentary power interruption (power fault), contact opens for 1 second.
15.For high and low voltage units, the factory supplied
jumper between 1 & 53 must be removed when elec-tromechanical starter overloads and/or safety devices are used. For high voltage (2300-4160) UL and CUL approved units only, electromechanical compressor motor starter overloads (normally closed) must be con-nected between 1 & 53 .
16.Contact rating is 5 Amps resistive @ 250 Volts A.C. & 30
Volts D.C., 2 Amp inductive (.4 PF) @ 250 Volts A.C. & 30 Volts D.C.
17.Each 115VAC field-connected inductive load: i.e. relay
coil, motor starter coil, etc., shall have a transient sup-pressor wired in parallel with its coil, physically located at the coil. Spare transient suppressors and control cir-cuit fuses are supplied in a bag attached to the top of the hinged panel.
LEGEND
5 YORK INTERNA TIONAL
CONNECTION DIAGRAM
6YORK INTERNATIONAL
(CONTINUED ON PAGES 8 & 9)FORM 160.52-PW1
LD03132
YORK INTERNA TIONAL7
CONNECTION DIAGRAM (Cont’d)
8YORK INTERNATIONAL
FORM 160.52-PW1
YORK INTERNATIONAL
9
LD03133
YORK INTERNA TIONAL
10
WIRING FOR 230V AND 460V UNITS
OIL PUMP MOTOR
OIL PUMP FUSING
FULL
MAXIMUM VOLTS-PH-HZ LOAD
DUAL ELEMENT AMPS
FUSE SIZE
230-3-60 6.715460-3-60 3.357.5575-3-60 2.65
YORK INTERNA TIONAL
11
FORM 160.52-PW1
WIRING FOR 346V AND 600V UNITS
Proud Sponsor of the 1998
U.S. Olympic Team
36USC380
P .O. Box 1592, Y ork, Pennsylvania USA 17405-1592Subject to change without notice. Printed in USA
Copyright ? by Y ork International Corporation 1997ALL RIGHTS RESERVED
Form 160.52-PW1 (698)
Supersedes: 160.52-PW1 (1297)
LD02609
*Function provided by condenser transducer.
**
See operator’s manual for a detailed description of low oil pressure and high oil flow shutdowns.?Applicable if unit was shut down for 30 mins. or less.
??
Applicable if unit was shut down for greater than 30 mins.