PRODUCT DRAWING

YORK INTERNATIONAL CORPORATION

P .O. Box 1592, Y ork, PA 17405

CONTRACTOR _______________________PURCHASER ____________________________________________ORDER NO.__________________________JOB NAME _______________________________________________YORK CONTRACT NO._________________

LOCA TION _______________________________________________YORK ORDER NO.____________________

ENGINEER ______________________________________________

REFERENCE

DA TE ________

APPROVAL DA TE ________

CONSTRUCTION DA TE _________

Supersedes: 160.52-PW1 (1297)Form 160.52-PW1 (698)

WIRING DIAGRAM, MILLENNIUM MODEL Y K (STYLE D) LIQUID CHILLERS MICROCOMPUTER CONTROL CENTER WITH ELECTRO-MECHANICAL STARTER

JOB DATA:

CHILLER MODEL NO. YK ________________________________________________________NO. OF UNITS _____________

COMPRESSOR MOTOR ______________ VOLTS, 3-PHASE, _____________ Hz

OIL PUMP MOTOR _____________ VOLTS, 3-PHASE, _____________ Hz, _____________FLA

REMARKS:

2

YORK INTERNATIONAL

E L E M E N T A R Y D I A G R A M

R E V . 035-15977 (R E V . A

)

FORM 160.52-PW1

FORM 160.52-PW1

3A YORK INTERNATIONAL3

YORK INTERNATIONAL

FORM 160.52-PW1

4

3B YORK INTERNATIONAL YORK INTERNATIONAL

FORM 160.52-PW1 NOTES:

1.This wiring diagram describes the standard electronic

control scheme for use with an electromechanical starter.

For details of standard modifications, refer to Product Form 160.49-PW13.

2.Field wiring to be in accordance with the National Elec-

trical Code as well as all other applicable codes and specifications. See Product Form 160.49-PW10 for field wiring connections.

3.Numbers along the left side of diagram are line identifica-

tion numbers. The numbers along the right side indicate the line number location of relay contacts. An underlined contact location signifies a normally closed contact.

4.Main control panel Class 1 field wiring terminal connec-

tion points are indicated by numbers within a rectangle,

i.e. 15 . Main control panel factory wiring terminal con-

nection points are indicated by numbers within a triangle,

i.e. 5 . Component terminal markings are indicated by

numbers within a circle, i.e. C1 . Numbers adjacent to circuit lines are the circuit identification numbers.

5.To cycle unit on and off automatically with contacts other

than those shown, install a cycling device between ter-minals 1 & 13 (line 37) (see note 9). If a cycling device is installed, jumper must be removed between terminals

1 & 13 .

https://www.wendangku.net/doc/299857849.html,pressor motor starter with starter interlock contacts

(rated 0.5 to 1.0 amp @ 24 volts A.C.) must be per Form 160.45-P A5.1. Control panel shall be grounded.

7.Units installed in Canada must have a field supplied

CSA approved 30 Amp disconnect switch and a 20 Amp dual element fuse mounted external to control panel for 115 volt control supply.

8.To stop unit and not permit it to start again, install a stop

device between terminals 1 & 8 (Line 33) (see note 9).

A remote start-stop switch may be connected to termi-

nals 1 , 7 & 8 (Lines 32 & 33) (see note 9). Remote start-stop switch (Line 32) is operative only in the “re-mote” operating mode.

9.Device contact rating to be 5 milliamperes @ 115 volts

A.C.

10._____________

11.Contact rating is 5 Amp resistive @ 120 volts A.C. or

240 volts A.C.

12.Three phase oil pump must be properly phased L1, L2

& L3 corresponding to phase sequence A, B & C. 13.To check motor rotation on initial start-up, install mo-

mentary switch between terminals 24 & 25 (line 41).

Depress start switch. After approx. 30 seconds, jog mo-tor with momentary switch. When proper rotation is ob-tained, replace momentary switch with jumper. Switch must have a minimum contact rating of 2 FLA., 10 LRA at 115 Volts A.C.

14.Motor overload (CM) is set to trip at 105% FLA. During

momentary power interruption (power fault), contact opens for 1 second.

15.For high and low voltage units, the factory supplied

jumper between 1 & 53 must be removed when elec-tromechanical starter overloads and/or safety devices are used. For high voltage (2300-4160) UL and CUL approved units only, electromechanical compressor motor starter overloads (normally closed) must be con-nected between 1 & 53 .

16.Contact rating is 5 Amps resistive @ 250 Volts A.C. & 30

Volts D.C., 2 Amp inductive (.4 PF) @ 250 Volts A.C. & 30 Volts D.C.

17.Each 115VAC field-connected inductive load: i.e. relay

coil, motor starter coil, etc., shall have a transient sup-pressor wired in parallel with its coil, physically located at the coil. Spare transient suppressors and control cir-cuit fuses are supplied in a bag attached to the top of the hinged panel.

LEGEND

5 YORK INTERNA TIONAL

CONNECTION DIAGRAM

6YORK INTERNATIONAL

(CONTINUED ON PAGES 8 & 9)FORM 160.52-PW1

LD03132

YORK INTERNA TIONAL7

CONNECTION DIAGRAM (Cont’d)

8YORK INTERNATIONAL

FORM 160.52-PW1

YORK INTERNATIONAL

9

LD03133

YORK INTERNA TIONAL

10

WIRING FOR 230V AND 460V UNITS

OIL PUMP MOTOR

OIL PUMP FUSING

FULL

MAXIMUM VOLTS-PH-HZ LOAD

DUAL ELEMENT AMPS

FUSE SIZE

230-3-60 6.715460-3-60 3.357.5575-3-60 2.65

YORK INTERNA TIONAL

11

FORM 160.52-PW1

WIRING FOR 346V AND 600V UNITS

Proud Sponsor of the 1998

U.S. Olympic Team

36USC380

P .O. Box 1592, Y ork, Pennsylvania USA 17405-1592Subject to change without notice. Printed in USA

Copyright ? by Y ork International Corporation 1997ALL RIGHTS RESERVED

Form 160.52-PW1 (698)

Supersedes: 160.52-PW1 (1297)

LD02609

*Function provided by condenser transducer.

**

See operator’s manual for a detailed description of low oil pressure and high oil flow shutdowns.?Applicable if unit was shut down for 30 mins. or less.

??

Applicable if unit was shut down for greater than 30 mins.