The Technical Specifications of Transformer Protection and Monitoring Device

Guodian Nanjing Automation Co.,Ltd.

GUODIAN NANJING AUTOMATION CO., LTD

Statement of the Version

This technical specification which vision is V1.22 applies to PST 645U transformer protection and monitoring device.

a)Software

PST 645U V1.22

b) Hardware

Revision history Table of PST 645U transformer protection and monitoring device hardware module version.

NO. Name of the

module Initial vision (2006-02) Modified version of the

first(2008-08)

Modified

version of the

second

1 AC module PST 640U-AC.A-A

2 CPU module EDP 03-CPU.A-A E03-CPU.BA

3 Panel module EDP 03-PNL.A-A

4 DIO module PSL 640U-DIO.A-A

5 TRIP module PSL 640U-TRIP.A-A PSL640U-TRIP.A-B

6 Power module EDP 03-PWR.A-A

7 Basis module EDP 03-MB.A-A

8 Communication

module

EDP 03-COM.B-A

9 Clock

synchronization

module

EDP 03-CLK.A-A

Revision history Table of PST 645U transformer protection and monitoring device product instruction.

10

9

8

7

6

5

4

3 V1.22

2 V1.10

1 V1.00

NO. Manual Version

Number

Modified Abstract

Directory

Version of the Statement

1.Outline (1)

1.1.Protection function settings (1)

1.2.Monitoring and controlling function settings (1)

2.Technical parameters (2)

2.1.Precise scope of work on protection components (2)

2.2.Setting error on protection components (2)

2.3.Protection of the entire set of action time (2)

2.4.Technical parameters of measurement and control functions (2)

3.Protection function and principle (3)

3.1.Phase over-current protection (3)

3.1.1Low-voltage blocking elements (3)

3.1.2Negative sequence overvoltage blocking elements (3)

3.1.3White current inverse time protection (3)

3.2.Overload protection (4)

3.3.Zero sequence over-current protection (4)

3.4.Zero sequence overvoltage protection (4)

3.5.Low-voltage protection (4)

3.6.Acceleration (4)

3.7Non-power protection (4)

3.8Tripping logic matrix (5)

3.9TV break (5)

4.Terminal Description (6)

4.1.Total terminal plans (6)

4.2.AC module terminal definition of X1 (6)

4.3.CPU module terminal definition of X2 (7)

4.4DIO module terminal definition of X3 (8)

4.5DIO module terminal definition of X4 (8)

4.6TRIP module terminal definition of X5 (8)

4.7TRIP module terminal definition of X6 (9)

5.Setpoint tuning instructions (10)

5.1List and instruction of protection value (10)

5.2 List and instruction of operating parameters (12)

5.3 List and instruction of Soft platen (12)

6.Device information code table (14)

6.1Event information table (14)

6.2Alarm information table (14)

6.3Soft platen information table (15)

6.4Remote Communication information table (15)

6.5Remote measurement information table (16)

6.6 Remote controlling information table (16)

7.Device of secondary wiring diagram (18)

1.Outline

PST 645U transformer protection and monitoring device applies to the non-direct grounding system or low resistance grounding station which voltage level is below110KV.It can be screened or installed grounding.

1.1Protective function configuration

1)three sections of the composite voltage lockout over-current protection(III segment can be set to the inverse time)

2)The three sections of high-pressure side of the zero-sequence over-current protection(III segment alarm/trip option)

3)The three sections the low pressure side of the zero-sequence over-current protection(III segment can be set to the inverse time)

4)overload(alarm/trip option)

5)zero sequence overvoltage protection(alarm/trip option)

6) Low voltage protection

7)Hand accelerate protection

8)4-way non-power protection

1.2monitoring and controlling functions configuration

1)22-way external switch input and tele-signal collection;

2)The circuit breaker position,manual switching accident tele-signal collection;

3) normal breaker which switching is remote;

4)2 pulse input,accumulated electrical;

5) time of GPS is adaptive when input.

2Technical parameters

2.1 precise working scope or protection of components Voltage: 1.0V ~ 150.0V;

Current: 0.04IN ~ 20IN;

Zero Sequence Current: 0.02A ~ 12.0A.

Note: IN the rating, the same below.

2.2Protection element setting error

Current components: ≤ ± 2.5%or±0.01IN;

The voltage element:≤±2.5%or±0.005UN;

The time element:definite time≤(% 1setting value) +40ms.

Note: V oltage is rating,the same below.

2.3protecting the entire group of action time

Instantaneous trip current:1.5 times of the setting value is not greater than40ms.

2.4Technical parameters of monitoring and controlling functions

R efer to PS 640U series protection and monitoring device manual

3.Protection function and principle

3.1 phase over-current protection

Device in the implementation of the three-stage cross-flow discriminant is logically consistent and its operation conditions are as follows:

1) Iφ> Idn; Idn is the current setting of the n segment ; Iφ is phase current; 2) T> Tdn; Tdn is the delaying value of the n segment .

Its low pressure blocking element and negative sequence voltage blocking element is decided according to controlling word .

3.1.1 Low voltage lockout element

Action when any one of the low voltage components in the three line voltage below the low voltage setpoint, the open latch protection element. Using this component, you can guarantee that the device does not appear in the case of non-fault motor feedback malfunction. 3.1.2 Negative sequence overvoltage lockout components

When negative sequence greater than the negative sequence overvoltage setting, open lockout protection components. Together constitute the the composite voltage blocking element, with low voltage blocking element with over-current elements constitute the composite voltage over-current protection.

3.1.3 phase current inverse time element

Inverse time protection component size naturally with the action time limit protection circuit current protection devices, by panning action curve, you can very easily with across the board. The device provides the common characteristics of the three types of inverse time, that is the standard inverse, very inverse, extremely inverse and inverse-time characteristics by setting the value of the corresponding inverse time index tuning. Inverse time characteristics of the following formula:

1) Normal inverse

1)(14.002.0-=

Ip

I

tp t 2) Very inverse time

1)(35.1-=

Ip

I

tp

t

3) Extremely Inverse

1)(802

-=

Ip

I tp

t

: tp is the time coefficient, and the range is from 0.05 to 1; IP is a current reference value; I is a

fault current; t is the tripping time.

Inverse time the value of the portion of the tuning for the value of the product of the molecules in the above expression, in seconds, the tuning range is from 0.005 to 127.

It also applies to Inverse time for a long time . Long time inverse expression is as follows:

1)(120-=

Ip

I

tp

t

Phase-to-phase current protection device can be controlled by setting the relevant bit of the word select definite time or inverse time. When the the select inverse time, automatically exit definite time over-current paragraph III protection, section III of the phase current function plates inverse time function of the phase current .

3.2 overload element

Overload element monitoring a three-phase current, and its operating condition: The the MAX (Iφ)> Ifh, which for the overload current setting Ifh. By the corresponding control word is set to alarm or trip. 3.3 zero sequence over-current protection

Device provides each of the three sections of the high and low side zero sequence over-current protection, in which the high-pressure side of the zero-sequence III segment control word is set to alarm when the high-pressure side of the zero-sequence current as a trip or alarm, zero-sequence current operating parameters introduction of control word a bit KG1.7 dedicated select zero sequence current by external zero sequence CT, or generated by the software production for the device defaults to the high-pressure side of the zero-sequence current external.

Low pressure side of the zero-sequence III section protection by the control word is set to inverse-time protection and zero sequence protection inverse time characteristics of inverse time element with phase current.

3.4 Zero sequence overvoltage protection

Zero sequence overvoltage element operates when the following conditions are met: 1) zero-sequence voltage is higher than the zero-sequence overvoltage setting value; 2) the circuit breaker is in the aggregate bit; 3) the delay time meets.

Through the corresponding control word can be set to alarm or trip, when zero sequence overvoltage is selected as the alarm device to discriminate self 3U0 zero sequence voltage. 3.5 Low voltage protection

That the system voltage is lower than the tuning voltage determines whether removes the load. The criterion of low voltage components:

1) three phase-to-phase voltage is lower than the low voltage setting; 2) three-phase current is less than a set value. 3) the circuit breaker in the aggregate bit; 4) the delay time. 3.6 acceleration

the device includes late acceleration by hand and its start conditions are as follows. 1) The time of the circuit breaker is in the OFF position over 30s;

2) the circuit breaker by the sub-gate to closing, accelerated to allow time broadening 3s;

Device independent current accelerating current setting and the corresponding time setting is set.

3.7 Non-electrical protection

The device provides four open into the non-power protection, the by soft platen select trip or alarm. When the the soft platens investment, the non-power movement is in the trip;, non-power signs only when the soft platen exits.

The device panel lights shows only non-electricity and non-electricity, non-power and non-power 4 of four signal for flexibility. The non electricity significance engineering terminal access. Under normal circumstances, the default non-power inputs of heavy gas, non-electricity to the input end of the light gas, non-electricity input of the pressure release and non-power input of high oil temperature.

3.8tripping logic matrix

The protection tripping logic of the device setting tuning protection components operation export tripping password is set by the export group.Tripping password is a16-bit binary code,and the tuning range is from 0000to FFFFH.When the protection elements act,the trip password is set to1, and then jump to the respective outlet,and respective outlet does not move when it is 0.

Position outlet Setting value

0 trip 1

1 X5:1-

2 0

2 X5:3-4 0

3 X5:5-6 0

4 X5:7-8 0

5 reserved 0

6 X3:1-2 0

7 X3:3-4 0

8 X3:5-6 1

9 X3:7-8 0

10 X3:9-12 0

11 reserved 0

12 reserved 0

13 reserved 0

14 reserved 0

15 reserved 0

Example: action of over-current segment I needs to jump to the export "trip", "X3 :5-6’, which corresponds to the export of setting the value of the binary number 0000000100000001, four to a set,and is calculated according to 8421 yards. In the setting menu ,items of "over-current trip segment ⅰ password" is set to 0101H.

3.9 TV break

When operating parameters control word KG1.5 = 0 and selecting star wiring, criterion of bus TV breaking is as follows:

1) When the phase voltage is less than 8V and some phase (a or c phase) current is greater than

0.04IN ,it is sentenced for three-phase voltage loss;

2) three-phase voltage is greater than 8V, the minimum line voltage is less than 16V;

3) That three-phase voltage is greater than 8V ;the maximum line voltage and minimum line voltage difference is greater than 16V is sentenced to two-phase or single-phase TV break.

When the operating parameters of the control word KG1.5 = 1 ",select angle wiring corresponding bus PT taking VV wiring and its breaking criterion is as follows:

1) negative sequence voltage is greater than 8V;

2) one phase or two-phase line voltage is less than 70V pressure value;

3) three-phase line voltage is less than 70V pressure value and a phase current is greater than 0.04IN.

TV wiring in these two meets after the breaking criterion any conditions 10s, the device sent busbar TV disconnected "message and lit warning lights.

When TV break is detected, the device can be under the control word KG1.13 and choose to exit the band voltage components paragraphs protection or voltage components. The TV disconnection detection function can be controlled by the word "KG1.14".

4Terminal Description

4.1Total terminal plans

4.2AC module terminal definition of X1

Terminal X1 Definition Description

1 L+ positive supply

2 L- negative supply

3 DYJG1 device of losing power output contacts

4 DYJG1

5 24V+

6 24V-

7 U0 zero sequence voltage input polarity end

8

zero sequence voltage input non-polar end

,

U

9 Ia A phase current input polar end

10

,

a I

A phase current input non-polar end

11 Ib B phase current input polar end

12

,

b I

B phase current input non-polar end

13 Ic C phase current input polar end

14

,c I

C phase current input non-polar end

15 10g High-voltage side of the zero-sequence current input polar

end

16

,

10g High-voltage side of the zero-sequence current input

non-polar end

17 CIa A phase measuring current input polar end

18

,

a

CI

A phase measuring current input non-polar end

19 CIb B phase measuring current input polar end

20

,

b

CI

B phase measuring current input non-polar end

21 CIc C phase measuring current input polar end

22

,

c

CI

C phase measuring current input non-polar end

23 10d Low voltage side of the zero-sequence current input polar

end

24

,

d

10Low voltage side of the zero-sequence current input

non-polar end

25~28 reserved reserved

29 Ua A phase voltage input polar end

30 Ub B phase voltage input polar end

31 Uc C phase voltage input polar end

32 Un V oltage input non-polar end

The serial terminal wiring diagram(the terminal description is only for the EDP 03-CPU.BA plug) Definition Terminal NO. Definition

232_RXD 1 2 232_CTS

232_TXD 3 4 232_RTS

232_GND 5 6 232_GND

485_1_A 7 8 485_2_A

485_1_B 9 10 485_2_B

485_1_GND 11 12 485_2_GND

4.3CPU module terminal definition of X2

Terminal X2 Definition Description

1 switch to X2:1

2 switch to X2:2 spring discharged input

3 distant status 0:ground 1:the distant status

4 repairing status 0:normal operation1:repairing status

5 switch to X2:5

6 switch to X2:6

7 switch to X2:7

8 switch to X2:8

9 switch to X2:9 the over-current by running parameter is set to a hard platen

10 switch to X2:10 the over-current by running parameter is set to

11 switch to X2:11

12 switch to X2:12 set to the input pulse P by the operating parameters

13 switch to X2:13 set to the input pulse Q by the operating parameters

14 switch to X2:14 set to the External reset by the operating parameters

15 Switch to public

negative terminal

16 GPS(+) GPS on positive input

17 GPS(-) GPS on negative input

18 signal GND When GPS switches to RS485ways,the GPS device485

interface connects to GND to prevent common mode

interference.

Serial terminal wiring diagram

Definition Terminal NO. Definition

232_RXD 1 2 232_CTS

232_TXD 3 4 232_RTS

232_GND 5 6 232_GND

485_1_A 7 8 485_2_A

485_1_B 9 10 485_2_B

485_1_GND 11 12 485_2_GND

4.4DIO module terminal definition of X3

Terminal X3 definition description

1 outlet8 reserved

2

3 outlet9 reserved

4

5 Outlet10 reserved

6

7 Outlet11 reserved

8

9 Outlet12 Jumper JUMP1 = 1-2 the choice without

QDJ atresia. JUMP1 = 2-3 select after QDJ

atresia (silent the default setting).

10

11 Outlet12

restart X3:9-10 restart contacts

12

13 reserved

14

4.5DIO module terminal definition of X4

Terminal X4 definition description

1 reserved

2

3 Switch to 15 Non-electricity:heavy gas

4 Switch to 16 Non-electricity:light gas

5 Switch to 17 Non-electricity:pressure release

6 Switch to 18 Non-power4:high oil temperature

7 Switch to 19

8 Switch to 20

9 Switch to 21

10 Switch to 22

11 Switch to public negative terminal

12~16 reserved

4.6 The terminal X5 definition of the TRIP module

The terminal X5

definition

Description

1

X5:1-2 Remote tripping output contacts 2

3

X5:3-4 Remote closing output contacts 4

5 X5:5-6

Jumper JUMP1 = 1-2 the choice

6 without QDJ atresia. JUMP1 = 2-3 select after QDJ atresia (silent

The default setting).

7

X5:7-8 Jumper JUMP2 = 1-2 choice without QDJ to lockout. JUMP1 = 2-3 select after QDJ atresia (silent The default setting).

8

9

X5:9-10 Protection action signal ,STJ parallel output contacts

10

11 X5:11 Signal node public end

12 X5:12 Protection action signal

13 X5:13 Alarm signal

14 X5:14 Control circuit break 4.7 The terminal X6 definition of the TRIP module

The terminal X6 definition Description

1 Total signal of the

accident By TWJ, KKJ contact series output

2

3 +KM The positive terminal of Control power input

4 Common terminal

Position contact

5 Tab

6 Co-bit

7 Trip

Protection trip output contacts 8 Spare

9

Circuit breaker

closing

operation loop The HWJ coil negative

terminal to TQ

To the circuit breaker trip coil,

this access end should not be

through the pressure contacts

atresia.

10 Manual trip into The input end of the manual trip, remote tripping or external protection tripping (atresia reclosing)

11 Trip into Protection trip input (not blocking reclosing)

12 To the trip coil TQ Access circuit breaker trip coil

13 Closing into Reclosing, manual or remote control switch on the input of

14 To the closing coil HQ Access breaker closing coil

15 TWJ coil negative

terminal to HQ

The end of this access should not

pressure or spring energy to the

circuit breaker closing coil

contacts atresia.

16 -KM The negative terminal of Control the power input

5 Given value of the tuning instructions 5.1 Protection setting list and said

1) Protection setting list

No Setpoint name Range Unit Setting

value

Remark

1 Control word one 0000~

FFFF

No

See control word (KG1)

definition

2 Control word two 0000~

FFFF

No Spare

3 I segment current over-current 0.04In

~20In

A In Rated current: 5A or 1A

4 II segment current over-current 0.04In

~20In

A

5 III segment current

over-current

0.04In

~20In

A

6 Complex depress voltage

setting

1.0~

120.0

V Line voltage

7 Complex to pressure negative

sequence voltage setting

1.0~

120.0

V

8 Ⅰtime over-current 0.0~

100.0

s

9 Password of over-current trip

segment Ⅰ

0000~

FFFF

No

10 II time over-current 0.1~

100.0

s

11 Password of over-current trip

segment II

0000~

FFFF

No

12 III time over-current 0.1~

100.0

s

13 Password of over-current trip

segment III

0000~

FFFF

No

No Setpoint name Range Unit Setting

value

Remark

14 Overload current 0.04In

~20In

A

15 Overload time 0.1~9000.0

s

16 Overload tripping password 0000~

FFFF

No

17 High side of the zero-sequence

current segment Ⅰ

0.02~

100.0

A

18 High side of the zero-sequence

current segment II

0.02~

100.0

A

19 High side of the zero-sequence

current segment III

0.02~

100.0

A

20 High side zero sequence time I 0.0~

100.0

s

21 I0G Ⅰsegment tripping

password

0000~

FFFF

No

I0G: high-pressure side of

the zero-sequence

22 High side zero sequence time II 0.1~

100.0

s

23 I0G II segment tripping

password

0000~

FFFF

No

I0G: high-pressure side of

the zero-sequence

24 High side zero sequence time

III

0.1~

100.0

s

25 I0G III segment tripping

password

0000~

FFFF

No

I0G: high-pressure side of

the zero-sequence

26 Low side of the zero-sequence

current segment Ⅰ

0.04~

100.0

A

27 Low side of the zero-sequence

current segment II

0.04~

100.0

A

28 Low side of the zero-sequence

current segment III

0.04~

100.0

A

29 Low side zero sequence time I 0.0~

100.0

s

30 I0D Ⅰsegment tripping

password

0000~

FFFF

No

I0D: the low pressure side

of the zero sequence

31 Low side zero sequence time II 0.1~

100.0

s

32 I0D II segment tripping

password

0000~

FFFF

No

I0D: the low pressure side

of the zero sequence

33 Low side zero sequence time

III

0.1~

100.0

s

34 I0D III segment tripping

password

0000~

FFFF

No

I0D: the low pressure side

of the zero sequence

No Setpoint name Range Unit Setting

value

Remark

35 Over-current inverse time

benchmarks

0.04In

~20In

A

36 Inverse time over-current 0.005~

127

s

For inverse time

molecular formula values

37 Over-current FSX tripping

password

0000~

FFFF

No FSX: inverse time

38 The zero-sequence inverse time

benchmarks

0.1~

12.0

A

39 Zero-sequence inverse time 0.005~

127

s

For inverse time

molecular formula values

40 The zero sequence FSX

tripping password

0000~

FFFF

No

FSX: inverse time

41 Inverse time index 0.01~

10.0

No

Set 0.02,1, or 2

42 Acceleration phase current 0.04In

~20In

A

43 Acceleration phase time 0.0~

100.0

s

44 The acceleration segment

tripping password

0000~

FFFF

No

45 Zero sequence overvoltage

setting

1.0~

120.0

V

46 Time of zero sequence

overvoltage

0.0~

100.0

s

47 Zero sequence overvoltage trip

Password

0000~

FFFF

No

48 Low-voltage protection setting 1.0~

120.0

V

49 Time of low voltage protection 0.0~

100.0

s

50 Low-voltage lockout current 0.04In

~20In

A

51 Low voltage tripping password 0000~

FFFF

No

52 Non-power tripping password 0000~

FFFF

No

2) setting control word (KG1) defined:

Bit the meaning when Set to 1 the meaning when Set to 0 Setting value

1 I segment by the low-voltage lockout The Ⅰsegment without low

voltage lockout

2 II segment by the low-voltage The II segment without low

lockout voltage lockout

3 III segment by the low-voltage

lockout

The III segment without low

voltage lockout

4 I segment by the negative pressure

lockout

The Ⅰsegment without negative

pressure lockout

5 II segment by the negative pressure

lockout

The II segment without negative

pressure lockout

6 III segment by the negative pressure

lockout

The III segment without negative

pressure lockout

7 High side zero sequence III segment

trip

The high side of the zero-sequence

III Section Alarm

8 Low side zero sequence III segment

inverse time

The low side of the zero-sequence

III segment definite time

9 Overload tripping Overload alarm

10 Zero-pressure tripping zero-pressure alarm

11 Control back to the disconnection

alarm exit

Control back to break alarm inputs

12 Spare Spare

13 The TV disconnected exit related

segment

The TV disconnected exit related

components

14 The TV disconnected discrimination

invested

The TV disconnected

discrimination exit

15 TA rated current 1A TA rated current 5A

Note:

1) The setting of control word: Control word can enter the hexadecimal value ;We can also enter controlling word menu to set it by item and the method is as follows: when the cursor is in the corresponding controlling word, long press the ">" key to enter the controlling word to the screen.Press the "∧" key"∨"key to turn the line and press the "+" key and the "-" key to choose the corresponding function..Press the Enter key to exit the screen after choose the given value menu following continued to set other setting and then fix the given value.

5.2 Operating parameters list and the description

For some protection functions other than functions the, PST645U device provides operating parameters to be set.Operating parameters and the protection given values are equally important, and they must be set according to the actual situation, in order to ensure the correct use of related functions.

1)Parameter setting

No. Setpoint name Range Unit Setting

value

Remark

1 Control word one 0000~FFFF No See the definition of parameter control word one

2 Away aggregate export

pulse width 1

0.08~1.000 s

Remote closing relay contact

output remains Time

3 Away jump export

pulse width 2

0.08~1.000 s

The Remote Trip relay

contact output remains Time

4 Telemetry compression

factor

0.001~1.000 No

See Note (1), the factory

default value is 0.005

Note:

(1)The definition of telemetry compression factor:

Telemetry compression factor = measurement value of the current value - measured value last on the value of the send | ×100 / full scale value

If the change of the current measured value is greater than the telemetry compression factor, the penalty telemetry more limited, and then paste-limit signs and take the initiative to uploadthe measured value.Telemetry pressure The scale factor setting is generally recommended factory defaults.If there is no special reason, narrow telemetry compression factor is generally not recommended.

2)Parameters control word definition

bit the meaning when Set to 1 the meaning when Set to 0 Setting value

0 The Three Methods calculated power The Two Methods calculated power

1 The high side of the zero-sequence

current self

The high side of the zero-sequence

current external

2 X2: 12 open into the pulse P X2: 12 to ordinary telesignalling

3 X2: 13 open into the pulse Q X2: 13 to ordinary telesignalling

4 X2: 14 for distant reversion X2: 14 to ordinary telesignalling

5 PT-angle wiring PT for star wiring

6 X4:3 to ordinary telesignalling X4: 3 non-power open into

7 X4:4 to ordinary telesignalling X4: 4 non-power open into

8 X4:5 to ordinary telesignalling X4: 5 non-power open into

9 X4:6 to ordinary telesignalling X4: 6 non-power open into

10 X2: 9 over-current hard platen X2: 9 to ordinary telesignalling

11 X2: 10 zero flow hard platen X2: 10 to ordinary telesignalling of

12

15

Spare Spare 5.3 Soft platen list and description

No. Platen name

Setting value

Enabled / disabled)

Corresponding function

1 Ⅰsegment

over-current

Ⅰsegment over-current protection

function to vote back

2 II segment over-current Over flow Ⅱthe segment functions voted retire

3 III segment over-current Over-current III segment vote back or over-current inverse-time function to vote back

4 The Ⅰsegment of the

high side of zero flow

Ⅰsegment of the high-pressure side of

the zero flow function vote back

5 The II segment of the

high side of zero flow

II segment of the high-pressure side of

the zero flow function vote back

6 The III segment of the

high side of zero flow

III segment of the high-pressure side of

the zero flow function vote back

7 The Ⅰsegment of the

low side of zero flow

The low pressure side of the zero stream

function segment Ⅰvote back

8 The II segment of the

low side of zero flow

The low pressure side of the zero stream

function segment II vote back

9 The III segment of the

low side of zero flow

Inverse-time function of the low pressure

side of zero flow Ⅲsegment features

cast back or low pressure side of the

zero-sequence to vote back

10 Overload Overload functions vote back

11 Zero-sequence voltage Zero sequence overvoltage function vote back

12 Low V oltage Low voltage vote back

13 Accelerate The hands to acceleration cast retire

14 Non-electricity 1 A function of the non-electricity 1 switching

15 Non-electricity 2 A function of the non-electricity 2 switching

16 Non-electricity 3 A function of the non-electricity 3 switching

17 Non-electricity 4 A function of the non-electricity 4 switching

Description: non-power switching non-power protection features to protect the soft platen.When the the soft platen investment, the non-power protection acts in trip;When the soft platen exits, non-Power protection act letter.

6 Device code table

6.1 Event Information Table

No. Event Name Entry ID Remark

1 Protect the boot 01H

2 Ⅰsegment over-current 02H

3 II segment over-current 03H

4 III segment over-current 04H

5 Inverse-time over-current 05H

6 The Ⅰsegment of the high side of zero flow 06H

7 The II segment of the high side of zero flow 07H

8 The III segment of the high side of zero flow 08H

9 The Ⅰsegment of the low side of zero flow 09H

10 The II segment of the low side of zero flow 0AH

11 The III segment of the low side of zero flow 0BH

12 Zero flow inverse time 0CH

13 Overload 0DH

14 Over-current accelerate 0EH

15 Zero sequence overvoltage 0FH

16 Low Voltage 10H

17 Non-electricity 1 actions 11H Default: heavy gas

18 Non-electricity 2 actions 12H Default: light gas

19 Non-electricity 3 actions 13H Default: pressure release

20 Non-electricity 4 actions 14H Default: high temperature trip 6.2 Alarm information table

1) System exception information table

No. Event Name Entry ID treatment measures

1 Means electrically 01H Exit protection, notify the manufacturer processing

2 Memory error 02H Exit protection, notify the manufacturer processing

3 The run setting area invalid 03H Exit protection, notify the manufacturer processing

4 Setpoint checksum error 04H Exit protection, notify the manufacturer processing

5 Open into the open abnormal 05H Exit protection, notify the manufacturer processing

6 Sampling anomaly 06H Exit protection, notify the manufacturer processing

7 Program checksum error 07H Exit protection, notify the manufacturer processing

8 Monitoring module alarm 08H Exit protection, notify the manufacturer processing

9 ~64 Spare 09H ~40H Spare

2)Protection alarm event information table

No. Event Name Entry ID Unit reactor treatment measures Remark

1 Overload alarm 41H Call

2 Zero flow alarm 42H Call

3 Zero-pressure alarm 43H Call

4 TV break 44H Call Overhaul TV circuit

变压器保护定值整定

变压器定值整定说明 注:根据具体保护装置不同,可能产品与说明书有不符之处,以实际产品为主。 差动保护 (1)、平衡系数的计算 1 2 3 4 5 侧的二次电流。如果按上述的基准电流计算的平衡系数大于4,那么要更换基准电流I b,直到平衡系数满足 0.1

I n 为变压器的二次额定电流, K rel 为可靠系数,K rel =1.3—1.5; f i(n)为电流互感器在额定电流下的比值误差。f i(n)=±0.03(10P ),f i(n)=±0.01(5P ) ΔU 为变压器分接头调节引起的误差(相对额定电压); Δm 为TA 和TAA 变比未完全匹配产生的误差,Δm 一般取0.05。 一般情况下可取: I op.0=(0.2—0.5)I n 。 (3) I res.0(4) a I Δm 2=0.05; b 、 式中的符号与三圈变压器一样。 最大制动系数为: K res.max =res unb.max rel I I K Ires 为差动的制动电流,它与差动保护原理、制动回路的接线方式有关,对对于两圈变压器I res = I s.max 。 比率制动系数:

K= res.max res.0res.max op.0res.max /I I -1/I I -K 一般取K=0.5。 (5)、灵敏度的计算 在系统最小运行方式下,计算变压器出口金属性短路的最小短路电流I s.min ,同时计算相应的制动电流I res ;在动作特性曲线上查出相应的动作电流I op ;则灵敏系数K sen 为: K sen = op I I 要求K sen ≥(6)(7 式中:I K I e (81、低电压的整定和灵敏度系数校验 躲过电动机自起动时的电压整定: 当低电压继电器由变压器低压侧电压互感器供电时, U op=(0.5~0.6)U n 当低电压继电器由变压器高压侧电压互感器供电时, U op=0.7U n 灵敏系数校验

PST642U变压器保护测控装置技术说明书V1.1(精)

国电南自 Q/GDNZ.JB051-2007 标准备案号:708-2007 PST642U 变压器保护测控装置 技术说明书国电南京自动化股份有限公司GUODIAN NANJING AUTOMATION CO.,LTD PST642U 变压器保护测控装置技术说明书 编写 审核 批准 V1.10

国电南京自动化股份有限公司 2009年04月 本说明书适用于PST642U变压器保护测控装置V1.10版本。 a软件 PST642U V1.10 b硬件 PST642U变压器保护测控装置硬件模件版本修改记录表 序号模件名称初始版本(2006-02第一次修改版本(2008-08第二次修改版本1交流模件PST640U-AC.A-A CPU模件EDP03-CPU.A-A EDP03-CPU.B-A 面板模件EDP03-PNL.A-A DIO模件PSL640U-DIO.A-A TRIP模件PSL640U-TRIP.A-A PSL640U-TRIP.A-B 电源模件EDP03-PWR.A-A 母板模件EDP03-MB.A-A 通信模件EDP03-COM.B-A 时钟同步模件EDP03-CLK.A-A PST642U变压器保护测控装置产品说明书版本修改记录表 10

V1.10改进版本PST642UV1.102009.04 1V1.00初始版本PST642UV1.002007.04序号说明书版本号修改摘要软件版本号修改日期 *技术支持电话:(025******** 传真:(025******** *本说明书可能会被修改,请注意核对实际产品与说明书的版本是否相符 *2007年4月第2版第1次印刷 *国电南自技术部监制 录 版本声明 1概述 (1 1.1保护功能配置 (1 1.2测控功能配置 (1 2技术参数 (2 2.1保护元件精确工作范围 (2 2.2保护元件定值误差 (2 2.3保护整组动作时间 (2 3保护功能及原理 (3 3.1相间过电流保护 (3 3.2过负荷元件 (3

DMP300型微机变压器差动保护测控装置说明书

一、简介 1.概述 DMP300型微机变压器差动保护测控装置,适用于110KV及以下电压等级的三圈变或两圈变,具有开入采集、脉冲电度量采集、遥控输出、通讯功能。其中DMP321适用于三圈变,DMP322适用于两圈变。 保护功能:a)差电流速断保护 b)二次谐波制动的比率差动保护 c)CT断线识别和闭锁功能 d)过负荷告警 e)过载启动风冷 f)过载闭锁有载调压 遥信量采集:a)本体轻、重瓦斯信号 有载轻、重瓦斯信号 压力释放信号 变压器超温告警 b)主变一侧开关的弹簧未储能、压力异常闭锁、报警 c)从主变一侧开关操作箱中采集开关跳、合位,手跳、手合开关量脉冲电量:一路有功脉冲电度、一路无功脉冲电度 遥控:遥控主变一侧开关 2.特点: 1)差动保护中各侧电流平衡补偿由软件完成,中低压侧电流不平衡系数均以高压侧为基准。变压器各侧CT二次电流相位也由软件自动校正,即变压器各侧CT二次回路可接成丫型(也可选择常规接线),这样简化了CT二次接线,增加了可靠性。 1)变压器保护的差动保护与后备保护完全独立,各侧后备也完全独立,独立的工作电 源、CPU实现真正意义上的主、后备保护,极大地提高了主变保护的可靠性。 2)通过菜单可直接查看主变各侧电流值的大小、相位关系,差电流大小,方便用户调 试与主变投运。 3)选用高性能、高可靠性的80C196单片机,高度集成的PSD可编程外围芯片;宽温军 用、工业级芯片;高精度阻容元件;进口密封继电器。 4)抗干扰、抗震动的结构设计

全封闭金属单元机箱,箱内插板间加装隔离金属屏蔽板;高可靠性的进口接插件,加装固定挡条。 5)独到的多重抗干扰设计 单元装置采取了隔离、软硬件滤波、看门狗电路、智能诊断各种开放闭锁控制,ALL IN ONE的主板电路设计原则,新型结构设计等多种抗干扰措施,取得了良好的效果。 6)体积小、模块化,既可安装于开关柜,构成分散式系统,又可集中组屏。 7)大屏幕液晶汉字显示运行参数、菜单,具有极好的人机界面,操作简单、直观、易 学、易用。 8)所有保护功能均可根据需要直接投退,操作简单。 9)软件实现交流通道的模拟量精度调整,取消了传统的采保通道的误差补偿电位器, 不但简化了硬件,更方便了现场调试、校验,还提高了精度。 10)独到的远动试验菜单功能。装置中设有“远动试验”菜单,通过菜单按钮进行远动信息 传输试验,如“差动速断动作”、“高压侧CT断线告警”等,无需试验接点真正闭合,可在线试验,方便了远动调试。 11)多层次的PASSWORD:运行人员口令、保护人员口令、远动人员口令。 12)事件记录分类记录32条故障信息,32条预告信息,8条自检信息,并具掉电保持功 能。

WBH801A变压器保护装置作业指导书

WBH-801系列主变保护装置测试技能实训指导书 调试组: 调试人员: 调试日期: 国网技术学院 2012年4月

1试验过程中应注意的事项 1)断开直流电源后才允许插、拔插件,插、拔交流插件时应防止交流电流回路开路; 2)存放程序的EPROM芯片的窗口要用防紫外线的不干胶封死; 3)打印机及每块插件应保持清洁,注意防尘; 4)调试过程中发现有问题时,不要轻易更换芯片,应先查明原因,当证实确需更换芯片时, 则必须更换经筛选合格的芯片,芯片插入的方向应正确,并保证接触可靠; 5)试验人员接触、更换芯片时,应采用人体防静电接地措施,以确保不会因人体静电而损 坏芯片; 6)原则上在现场不能使用电烙铁,试验过程中如需使用电烙铁进行焊接时,应采用带接地 线的电烙铁或电烙铁断电后再焊接; 7)试验过程中,应注意不要将插件插错位置; 8)因检验需要临时短接或断开的端子,应逐个记录,并在试验结束后及时恢复; 9)使用交流电源的电子仪器(如示波器、毫秒计等)进行电路参数测量时,仪器外壳应与保 护屏(柜)在同一点接地; 2 安全措施 1)检查模拟断路器位置,确保一次设备停电(#1主变:5011、5012、201、301开关,#2主变:5022、5023、202、302开关)。 2)检查并记录主变保护屏所有压板位置后退出所有压板 3)检查并记录主变保护屏后三侧电压空开位置后断开。 4)检查并记录主变保护屏电压、电流端子连接片位置,断开电压回路、电流回路与外部回路 的连接: 电压回路:在端子排U1D处打开端子U1D1、U1D2、U1D3 、U1D5(分别是UHa、UHb、UHc 、UH0);U2D1、U2D2、U2D3、U3D5(分别是UMa、UMb、Umc、 UL0);U3D1、U3D2、U3D3、U3D5(分别是ULa、ULb、Ulc、UL0). 注:电压空开后电压端子1U1D、1U2D、1U3D端子连片均应处于连接位置。 电流回路:在端子排1I1处打开端子1I1D1、1I1D2、1I1D3(分别是I1Ha、I1Hb、I1Hc);1I1D9、1I1D10、1I1D11(分别是I2Ha、I2Hb、I2Hc);1I2D1、1I2D2、1I2D3(分别是IMa、IMb、IMc);1I3D1、1I3D2、1I3D3(分别是ILa、ILb、ILc);1I3D9、1I3D10、1I3D11(分别是Ira、Irb、Irc);1I4D1、1I4D2、1I4D3、1I4D9(分别是Iga、Igb、Igc、Igc0) 3通电前检查 1)退出保护所有压板,断开所有空气开关; 2)检查装置内、外部无积尘、无异物;清扫电路板的灰尘; 3)检查保护装置的硬件配置,各插件的位置、标注及接线应符合图纸要求;

变压器说明书

配电变压器安装使用说明书 三相树脂绝缘干式电力变压器 适用范围 二、 环氧树脂浇注干式变压器的特点 (2) 三、 使用条件 (2) 四、 产品主要规格型号 (2) 五、 产品结构概述及主要技术原理 (3) 六、产品主要技术参 数 ...................................... . (6) 七、运输和起吊 ......................................... .... (10) 丿八、 ............................................ 验收、保管和储存 .. (11) 沈阳 安装使用说明书 殳备制造有限公司 目 录

九、产品安装 ............................................. ?. (12) 十、现场交接试验 ....................................... .. (13) 十~、变压器试运行15 十二、变压器的维护 (18) 十三、安全注意事项......................................................... . (18) 一、适用范围 本说明书适用于我公司生产的额定容量20000kVA及以下,电压等级为35kV及以下无 励磁和有载调压环氧树脂浇注薄绝缘干式变压器的装卸、运输、仓储保管、安装、使用及维护。 二、环氧树脂浇注干式变压器的特点 环氧树脂浇注干式变压器具有低损耗、低局放、防爆、难燃、环保无污染、免维护、抗短路能力强等特点。 三、使用条件 1. 环境温度不高于40 °C,海拔高度不超过1000m若环境温度高于40 °C或海拔超过1000m时,应按GB6450的有关规定作适当的定额调整。 2.外壳防护等级有IP20、IP23等型式。The protection degree of enclosure is IP20 、IP23. 3.冷却方式有空气自冷(AN和强迫风冷两种。对空气自冷(AN和强迫风冷(AF)的变压器,均需保证变压器的安装环境具有良好的通风能力,当变压器安装在地下室或其他通风能力差

变压器微机保护装置的设计方案原理

变压器微机保护装置的设计原理 1、设计背景

键盘输入和液晶显示模块又称为人机接口模块,主要负责参数的输入和状态的显示,这里采用的是小键盘输入和LCD1602液晶模块。 电流检测模块采用的是Maxim公司生产的Max471芯片,电压检测模块采用AD736,温度监测模块选用Maxim公司的MAX6674。在电压、电流分别通过电压互感器和电流互感器后,再经过电流、电压监测模块,进行对数据的采集与转换;变压器的温度直接通过温度监测模块进行收集,接着把转换过的数据通入单片机中进行处理,最后报警并显示变压器当前的参数值并自动地控制、调整变压器的运行。 三、系统模块的设计 从总体上看,变压器智能保护系统可以分为以下模块:CPU模块、温度信号处理模块、电流信号监测处理模块、电压信号监测处理模块及<显示)输出模块、通信模块。下面我们就一一进行较为详细的阐述。 1、CPU模块 在本设计中采用的微处理器

ING-6024变压器后备保护装置技术及使用说明书

ING-6024 变压器后备保护装置技术及使用说明书

1. 概述 ING-6024变压器后备保护装置(以下简称装置),主要适应于6KV-220KV变压器的后备保护和测控。 主要功能 保护功能: a) 速断保护 b) III段复合电压闭锁过流保护 c) 过负荷保护 d) 零序电流保护 e) 过电压保护 f) 低电压保护 g) PT断线告警 h) 控制回路断线告警 遥测功能: 三相电流、三相电压、三线电压、频率,功率、功率因数、零序电流、零序电压 遥控功能: 断路器分合闸,装置信号复归,保护软压板投退 遥信功能: 8路遥信开入量

其它: 网络对时和手动对时功能 全隔离RS-485通讯接口,国际标准ModBUS-RTU通讯协议 2.技术数据 AC输入电流 额定5A:15A连续;短时250A 1秒 极限动态范围:625A持续1周波(正弦波) 功耗:5A 时0.16V A,15A时1.15V A 额定1A:3A连续;短时100A 1秒 极限动态范围:250A 持续1周波(正弦波) 功耗:1A 时0.06V A,3A时1.18V A 输出接点 符合IEC 255-0-20:1974,采用简单评估法 5A持续 30A接通符合IEEC C37.90:1989 100A持续1秒 启动/返回时间:<5ms 分断能力(L/R = 40ms): 24V 0.75A 10,000次 48V 0.50A 10,000次 125V 0.30A 10,000次

250V 0.20A 10,000次 循环能力(L/R = 40ms): 24V 0.75A 每秒2.5次 48V 0.50A 每秒2.5次 125V 0.30A 每秒2.5次 250V 0.20A 每秒2.5次 光隔输入 在额定控制电压下,每个光隔输入的电流为5mA。 额定电源 110伏:88 - 132Vdc或88 – 121Vac 220伏: 176 - 264Vdc或176 - 242Vac 额定5.5瓦, 最大8.5瓦 例行绝缘 试验电流输入端:500Vac 60秒不小于10M 电源、光隔输入及输出接点:500Vac 60秒不小于10M 带CE标志的装置进行下列IEC255-5:1977绝缘测试; 模拟输入:500Vac 60秒不小于10M 电源、光隔输入及输出接点:500Vac 60秒不小于10M 工作温度-10℃~+55℃(+14°F~+131°F)。 老化从室温到+75℃(+167℉)每次48小时以上。一共二十(20)次温度循环。 装置重量 2.5kg(5磅8盎司)。

WBZ-500H变压器保护装置技术说明书

国电南自
Q/GDNZ.J.09.44-2002
WBZ-500H 微机变压器保护装置
技术说明书 使用说明书
国电南京自动化股份有限公司
GUODIAN NANJING AUTOMATION CO. LTD

WBZ-500H 系列 微机变压器保护装置
技术说明书 使用说明书
V 2.5
国电南京自动化股份有限公司
2002 年 12 月
*本说明书可能会被修改,请注意最新版本资料 *国电南自技术部监制

第一部分 技术说明书

目次
1 装置概述
1
2 技术参数
2
2.1 工作环境
2
2.2 额定参数
2
2.3 主要技术指标
2
2.4 保护动作精度
3
2.5 绝缘性能
3
2.6 抗电磁干扰
4
3 硬件说明
5
3.1 概述
5
3.2 机箱结构
5
3.3 AC 交流输入模件
6
3.4 AD 转换模件
6
3.5 主 CPU 模件
6
3.6 出口跳闸模件
6
3.7 信号模件
6
3.8 打印管理模件
7
3.9 显示模件
7
4 保护原理
8
4.1 启动算法
8
4.2 差动保护
8
4.3 后备保护
11

4.4 非电量保护
17
4.5 分差保护
17
4.6 短引线保护
17
5 整定值的计算及整定
18
5.1 定值清单
18
5.2 变压器各侧的额定电流 TA 二次电流 Ie
18
5.3 差动保护
18
5.4 分差保护
18
5.5 短引线保护
18
5.6 分差保护
21
5.6 短引线保护
22

983变压器说明书.

NEP983 数字式变压器测控保护装置 说明书 国电南京自动化股份有限公司 2003年3月

NEP983 数字式变压器测控保护装置 说明书 编写:于剑东 审核:陈雪峰 批准:郭效军 版本号:Ver 3.0

国电南京自动化股份有限公司 二00三年三月

目次 1 装置概述 (1) 2 主要技术指标 (2) 3 功能介绍 (3) 4装置出口配置 (4) 5原理 (4) 6 操作说明 (7) 6.1 键盘排列及显示 (7) 6.2 键的功能 (7) 6.3 液晶显示及键盘操作说明 (7) 7 订货须知 (10) 附图一装置面板布置图 (11) 附图二装置电原理图 (13) 附图三装置出口原理图 (14) 附图四装置背板端子图 (17) 附图五装置安装尺寸图 (18)

·装置概述· 1 装置概述 NEP983数字式变压器测控保护装置是在消化吸收国内外先进经验的基础上专门为发电厂、变电站开发(可与各类综合自动化配套)的产品。该类产品可将变压器的测量、保护、操作回路集成在一个机箱内,结构小巧,可在恶劣的工业环境下(如高温、低温、震动、有害气体、灰尘、强电磁干扰等)长期可靠地运行。产品可集中组屏组柜运行,也可按功能就地安装在开关柜上,并具有远传、记忆各种操作或故障信息等功能,同时亦提供独立的中央信号空接点。 特点: ●采用Motorola高性能32位单片机。 ●采用一对一的方式,调试、安装及维护均非常便利。 ●人机界面友好,液晶中文显示。显示信息丰富、直观、各种操作亦非常方便。 ●完善的自我诊断功能,不需人为干预,故障可定位到某集成块。 ●最近100条事件记录(记录事件时间和类型)、10条事故记录(包含故障前360毫秒,故障后600毫秒,记录事故时间、类型、定值、控制字、交流量幅值及采样点)及200条遥信变位信息(记录遥信变位时间和类型),方便分析。 ●集保护、遥测、遥信、遥控四项功能于一体,可按功能就地安装,同时亦可提供独立的中央信号空接点。 ●高测量精度: I、U精度:0.2级 P、Q、Cosφ精度:0.5级(特殊要求精度可达到0.2级) ●高抗干扰性能,能满足: GB/T 14598.10-1996 快速瞬变干扰试验Ⅳ级 GB/T 14598.13-1998 脉冲群干扰试验Ⅲ级 GB/T 14598.14-1998 静电放电干扰试验Ⅲ级 功能:速断、定(或反)时限过流保护;过电压保护;低电压保护;定(或反)时限零序电流保护;零序电压保护;过负荷保护;本体保护;手动(遥控)跳合闸以及两瓦特表或三瓦特表法测量有功、无功、功率因素、电度量及各种开关量变位信息等功能。 通信:本装置具有422或485及CAN通讯网络可供选择,通信协议请见NEP980通信协议说明书。

上海思源弘瑞UDT-531变压器保护测控装置技术及使用说明书

UDT-531变压器保护测控装置技术和使用说明书(传统) (Version 1.03) 上海思源弘瑞自动化有限公司 Shanghai SHR Automation Co.,Ltd.

前言 感谢您使用上海思源弘瑞自动化有限公司的产品。为了安全、正确、高效地使用本装置,请您务必注意以下重要提示: 本说明书仅适用于UDT-531变压器保护测控装置。 请仔细阅读本说明书,并按照说明书的规定调整、测试和操作。如 有随机资料,请以随机资料为准。 为防止装置损坏,严禁带电插拔装置各插件、触摸印制电路板上的 芯片和器件。 请使用合格的测试仪器和设备对装置进行试验和检测。 装置如出现异常或需要维修,请及时与本公司服务热线联系。 本说明书和产品今后可能会有小的改动,请注意核对实际产品与说 明书的版本是否相符。

目录 1装置简介 (1) 1.1 应用范围 (1) 1.2 性能特点 (1) 1.3 功能配置 (2) 2技术指标 (5) 2.1 额定数据 (5) 2.2 装置功耗 (5) 2.3 环境条件 (5) 2.4 抗干扰性能 (5) 2.5 绝缘性能 (7) 2.6 机械性能 (7) 2.7 保护定值整定范围及误差 (7) 2.8 装置测量精度 (8) 2.9 触点容量 (8) 3装置硬件 (9) 3.1 机箱 (9) 3.2 主要模件 (9) 4装置功能 (28) 4.1 主保护 (28) 4.2 后备保护 (34) 4.3 测控功能 (45) 4.4 装置故障告警 (47) 4.5 辅助功能 (47) 5用户压板定值说明 (49) 5.1 软压板 (49) 5.2 硬压板 (51) 5.3 UDT-531AN定值及参数 (52) 5.4 UDT-531BHN定值及参数 (54) 5.5 UDT-531BLN定值及参数 (57) 5.6 UDT-531D定值及参数 (59) 5.7 UDT-531BHN跳闸矩阵 (60) 5.8 UDT-531BLN跳闸矩阵 (61) 6使用说明 (62) 6.1 面板说明 (62) 6.2 指示灯 (62) 6.3 显示说明 (65) 6.4 菜单结构 (66)

NSS低压变压器保护说明书V

NS 913 低压变压器保护测控装置 说明书 V1.1 南京南自科技发展有限公司 2003年12月 *本说明书可能会被修改,请注意最新版本资料

目录 1.概述 (1) 2.主要技术参数 (3) 3.保护功能 (6) 4.测量、控制以及事件记录功能 (8) 5.硬件结构说明 (9) 6.使用操作说明 (11) 7.装置参数一览 (13)

1 概述 NS 913S低压变压器保护测控装置适用于低压变压器的保护、测量及控制。可以在开关柜就地安装,也可以集中组屏安装。 1.1 装置主要特点 ?高速的DSP处理器 采用高性能DSP芯片,提供了高速的数据处理能力,保证了高性能实时算法的实现,提高了装置的可靠性和整体性能。 ?快速、高精度采样 采用快速14位高精度采样芯片,并采用频率自动跟踪技术,保证了很高的保护和测量计算精度。 ?强大的通讯功能 采用CAN网作为主通讯接口,传输速率可达1Mb/s,系统响应速度快。 ?可靠的操作箱功能 独立的跳、合闸启动和保持回路设计。 ?高可靠的电磁兼容设计 标准背插式工业机箱,电路板采用表面贴装技术以及多层板工艺,选用快速瞬变电压抑制器件,使装置具有很强的电磁兼容能力。 1.2 保护功能配置 ?相间过流保护 ◆速断保护 ◆定时限过流保护 ◆反时限过流保护 ◆过负荷保护 ?高压侧零序过流保护

?低压侧零序过流保护 1.3 数据采集功能 ?实时采集电流、电压、有功、无功、功率因数、频率 ?8路遥信量 1.4 事件记录及故障录波 ?保护动作记录 ?告警事件记录 ?遥信变位记录 ?操作命令记录 1.5 控制功能 ?就地/远方分闸、合闸控制 ?远方定值修改 ?远方保护投/退 1.6 操作箱功能 ?跳位、合位指示 ?可靠的自保持及防跳设计 1.7 通信功能 ?CAN总线 ?RS-485总线

微机配电变压器保护测控装置

YH-B2100PDB型 微机配电变压器保护测控装置技术说明书 Ver 1.0

第一章概述 YH-B2100PDB型微机配电变压器保护测控单元作为新一代数字式变电站线路保护测控装置,适用于110KV及以下电压等级的各种箱式变压器、出线变压器等配电变压器,对其进行控制、保护、测量、远动通信、故障录波、事件记录等功能。该装置既可单独供货,亦可与YH-B2100型系统其他装置及监控系统一起组成变电站综合自动化系统。 该装置具有以下特点: ★采样元件采用精密电压电流互感器,体积小,重量轻,负载小。 ★测量采用12位A/D转换器,精度达0.5级,并计及11次谐波,符合国家对RTU 的要求。 ★人机界面采用128×64全汉化大屏幕液晶显示器,界面友好直观,操作简单,使用方便。 ﹡就地及远方定值整定功能(定值、时限独立整定); ﹡实时显示运行参数及保护定值功能; ﹡远方就地位置显示。 ★软硬件均采用标准化模块设计,适用于各种配置要求,能方便的实现用户不同要求的保护组合,硬件通用性好,互换性强。 ★提供一路CANBUS接口和一路232接口,支持与变电站综合自动化系统相关单元通信。 ★ CANBUS波特率为33333 BPS,报文具有优先级,可主动上发报警,大大提高了故障响应时间。 ★可显示测量和保护电量参数的幅值及相位,便于用户检查接线。 ★可记录保护动作前3个周波、故障后5个周波,跳闸前8个周波的电压电流波形,通过CANBUS总线传至后台机或录波显示及打印单元打印或显示。 ★事件顺序记录。 ★可通过就地的分合按钮或后台机遥控命令,控制一台断路器。 ★断路器压力异常闭锁功能。 ★双层印制电路板布线技术及SMT表面贴装工艺,抗干扰能力强。 ★体积小的全密封装置,安装方便,外形美观,内部结构紧凑合理。 第二章工作原理 本单元集远动通信、保护、控制、测量、故障录波、事件记录为一体,采用交流采样技术,采样频率为1200HZ,保护电量的基波及谐波通过数字滤波,用差分和付氏算法求得,做出保护逻辑判断,驱动或闭锁单元上的出口继电器,该算法有利于消除模拟通道的零漂,具有较高的可靠性。测量的电量参数通过模拟量有效值算法求得(计及11次谐波),在大屏幕液晶显示器上显示,精度较高。为保证开关拒动时使继电器不损坏,单元设有完善的防跳回路,同时还具有可靠的自保持回路及断路器控制电路。

变压器的保护配置

电力变压器的保护配置 随着企业的快速发展,供电可靠性的要求不断提高,变压器的安全运行更是必不可少的条件。而合理可靠的保护配置是变压器安全运行的必备条件。现代生产的变压器,虽然在设计和材料方面有所改进,结构上比较可靠,相对于输电线路和发电机来说,变压器故障机会也比较少,但在实际运行中,仍有可能发生备种类型的故障和异常运行情况,这会对供电可靠性和系统的正常运行带来严重影响。为了满足电力系统稳定方面的要求,当变压器发生故障时,要求保护装置快速切除故障。 第一章电力变压器的故障及不正常工作状态 (一)变压器的故障 变压器的故障可以分为油箱外和油箱内两种故障。油箱外的故障,主要是套管和引出线上发生的相间短路和接地短路。油箱内的故障包括绕组的相间短路、接地短路、匝间短路以及铁芯的烧损等。油箱内故障时产生的电弧,不仅会损坏绕组的绝缘、烧毁铁芯,而且由于绝缘材料和变压器油因受热分解而产生大量气体,有可能引起变压器油箱的爆炸。因此,当变压器发生各种故障时,保护装置应能尽快的将变压器切除。实践表明,变压器套管和引出线上的相间短路、接地短路、绕组的匝间短路是比较常见的故障形式,而变压器油箱内发生相间短路的情况比较少。 (二)变压器的不正常运行状态 变压器的不正常运行状态主要有变压器外部短路和过负荷引起的过电流;中性点直接接地电力网中,外部接地短路引起的过电流及中性点过电压;风扇故障或漏油等原因引起冷却能力的下降等。这些不正常运行状态会使绕组和铁芯过热。大容量变压器在过电压或低频率等异常运行工况下会使变压器过励磁,引起铁芯和其他金属构件过热。变压器处于不正常运行状态时,继电保护应根据其严重程度,发出告警信号,使运行人员及时发现并采取相应的措施,以确保变压器

CSC-241数字(精选)式变压器保护装置

C S C241系列数字式变压器保护测控装置综述 CSC241系列数字式变压器保护测控装置是适用于66kV及以下电压等级的变压器成套保护装置,由差动保护、后备保护、厂(所)用变保护、接地变保护和非电量保护组成。 1

3

CSC241A 数字式变压器差动保护装置 1装置简介 CSC241A 为适用于66kV 及以下电压等级的两卷变压器差动保护装置,可在开关柜就地安装。一般需与本系列CSC241B 后备保护(或CSC241C 厂用变保护)装置构成成套保护。 2主要功能 ? 反应保护区内故障的差动速断保护; ? 反应保护区内故障经二次谐波制动的比率差动保护; ? CT 断线功能; ? 差流越限告警功能; ? 故障录波; ? 9路遥信开入采集(包括非电量保护输出接点的采集及信息上传功能)、装置遥信变位、事故遥 信; 各种事件SOE 等。 3保护元件 3.1差动速断元件 当任一相差动电流大于差动速断整定值时,动作于出口。用于在变压器差动区发生严重故障情况下快速切除变压器。差动速断定值应能躲过外部故障的最大不平衡电流和空投变压器时的励磁涌流,一般取6~12倍的额定电流。 3.2比率差动元件 为了保证内部故障时差动保护灵敏动作,同时防止外部故障时及差动各侧CT 特性不一致时暂态不平衡电流引起的误动,本装置采用三段式比率差动原理,其动作方程如下: 其中,cd I 为差动保护的起动电流定值,d I 为差动电流,r I 为制动电流。1r I 为可整定的第一拐点电流,2r I 为第二拐点电流(内部固定取为2e I ,e I 为变压器高压侧额定电流),1K 为可整定制动曲线斜率,2K 为内部固定的系数(取为0.7)。 2 1I I I d &&+= ,212 1I I I r &&-= 式中,1I &和2I &分别为变压器两侧的电流,均以流入变压器为正方向。变压器两侧的电流互感 器以指向变压器为同极性。 cd I 一般整定为0.2~1.2e I ,1r I 一般整定为0.8~1.2e I ,1K 一般整定为0.2~0.7,2 r I 取为2e I ,2K 取0.7。

电力变压器保护设计规范说明

电力变压器保护设计规范说明 电力变压器保护设计规范(GB/T50062—2008) 4·0·1电压为3~110kV,容量为63MV·A及以下的电力变压器,对下列故障及异常运行方式,应装设相应的保护装置: 1,绕组及其引出线的相问短路和在中性点直接接地或经小电阻接地侧的单相接地短路。2,绕组的匝间短路。 3,外部相间短路引起的过电流。 4,中性点直接接地或经小电阻接地的电力网中外部接地短路引起的过电流及中性点过电压。5,过负荷。 6,油面降低。 7,变压器油温过高、绕组温度过高、油箱压力过高、产生瓦斯或冷却系统故障。 4.0.2容量为0.4MV·A及以上的车间内油浸式变压器、容量为0.8MV·A及以上的油浸式变压器,以及带负荷调压变压器的充油调压开关均应装设瓦斯保护,当壳内故障产生轻微瓦斯或油面下降时,应瞬时动作于信号;当产生大量瓦斯时,应动作于断开变压器各侧断路器。 瓦斯保护应采取防止因震动、瓦斯继电器的引线故障等引起瓦斯保护误动作的措施。当变压器安装处电源侧无断路器或短路开关时,保护动作后应作用于信号并发出远跳命令,同时应断开线路对侧断路器。 4.0.3对变压器引出线、套管及内部的短路故障,应装设下列保护作为主保护,且应瞬时动作于断开变压器的各侧断路器,并应符合下列规定: 1,电压为10kV及以下、容量为10MV·A以下单独运行的变压器,应采用电流速断保护。 2,电压为10kV以上、容量为10MV·A及以上单独运行的变压器,以及容量为6.3MV·A及以上并列运行的变压器,应采用纵联差动保护。 3,容量为10MV·A以下单独运行的重要变压器,可装设纵联差动保护。 4,电压为10kV的重要变压器或容量为2MV·A及以上的变压器,当电流速断保护灵敏度不符合要求时,宜采用纵联差动保护。 5,容量为0.4MV·A及以上、一次电压为10kV及以下,且绕组为三角一星形连接的变压器,可采用两相三继电器式的电流速断保护。 4.0.4变压器的纵联差动保护应符合下列要求: 1,应能躲过励磁涌流和外部短路产生的不平衡电流。 2,应具有电流回路断线的判别功能,并应能选择报警或允许差动保护动作跳闸。 3,差动保护范围应包括变压器套管及其引出线,如不能包括引出线时,应采取快速切除故障的辅助措施。但在63kV或110kV电压等级的终端变电站和分支变电站,以及具有旁路母线的变电站在变压器断路器退出工作由旁路断路器代替时,纵联差动保护可短时利用变压器套管内的电流互感器,此时套管和引线故障可由后备保护动作切除;如电网安全稳定运行有要求时,应将纵联差动保护切至旁路断路器的电流互感器。 4.0.5对由外部相间短路引起的变压器过电流,应装设下列保护作为后备保护,并应带时限动作于断开相应的断路器,同时应符合下列规定: 1,过电流保护宜用于降压变压器。 2,复合电压启动的过电流保护或低电压闭锁的过电流保护,宜用于升压变压器、系统联络变压器和过电流保护不符合灵敏性要求的降压变压器。 4.0.6外部相间短路保护应符合下列规定:

WBH-800系列微机变压器保护装置技术说明书

目录 1 概述 (3) 1.1 功能简介 (3) 1.2 保护配置 (3) 1.3 功能特点 (4) 2 基本技术参数 (5) 2.1 基本数据 (5) 2.2 功率消耗 (6) 2.3 热稳定性 (6) 2.4 输出触点 (6) 2.5 绝缘性能 (6) 2.6 冲击电压 (6) 2.7 寿命 (7) 2.8 机械性能 (7) 2.9 环境条件 (7) 2.10 抗干扰能力 (7) 3 主要技术指标 (7) 3.1 动作时间 (7) 3.2 保护定值整定范围和定值误差 (7) 3.3 记录容量 (8) 3.4 通信接口 (8) 3.5 对时方式 (8) 4 装置整体说明 (8) 4.1 硬件平台 (8) 4.2 软件平台 (9) 4.3 与综合自动化监控系统接口说明 (9) 4.4 WBH-801保护装置背视图 (10) 4.5 WBH-801保护装置端子图 (11) 4.6 WBH-802保护装置背视图 (15) 4.7 WBH-802保护装置背视图 (16) 5 WBH-801装置保护原理说明 (21) 5.1 比率差动保护 (21) 5.2 阻抗保护 (24) 5.3 复合电压判别 (26) 5.4 复合电压(方向)过流保护 (27) 5.5 零序(方向)过流保护 (30) 5.6 间隙零序保护 (33) 5.7 非全相保护 (33)

5.8 失灵启动保护 (34) 5.9 过负荷(有载调压闭锁、通风启动)保护 (34) 5.10 限时速断保护 (35) 5.11 母线充电保护 (35) 5.12 TV断线判别 (36) 6 WBH-802装置非电量保护原理 (36) 7 整定内容及整定说明 (37) 7.1 WBH-801装置整定内容及整定说明 (37) 7.2 WBH-802装置整定内容及整定说明 (41) 8 保护装置整定计算 (42) 8.1 比率差动保护整定计算 (42) 8.2 阻抗保护整定计算 (48) 8.3 复合电压判别整定计算 (49) 8.4 复合电压过流保护整定计算 (50) 8.5 零序过流保护整定计算 (52) 8.6 间隙零序保护整定计算 (53) 8.7 低压侧零序过压保护整定计算 (53) 8.8 过负荷(通风启动、有载调压闭锁)保护整定计算 (53) 9 订货须知 (53) 10 附录一:装置运行说明 (54) 10.1 键盘 (54) 10.2 面板指示灯说明 (54) 10.3 运行工况及说明 (54) 10.4 故障报文和处理措施 (54) 11 附录二:装置通讯说明(IEC 60870-5-103规约) (55) 11.1 WBH-801微机变压器保护装置的信息 (55) 11.2 WBH-802微机变压器保护装置的信息 (63)

DMP3300系列变压器保护说明书

DMP3300系列 微机变压器保护测控装置技术说明书 (V2.02) 南京磐能电力科技股份有限公司

目录 1概述 (2) 1.1 适用范围 (2) 1.2 基本配置 (2) 1.3 DMP3300系列变压器保护装置功能一览表 (3) 2 技术参数 (5) 2.1额定参数 (5) 2.2 主要技术性能 (6) 2.3测量系统及遥信精度 (7) 3装置的工作原理 (7) 3.1 差动保护 (7) 3.2方向元件 (9) 3.3复压元件 (10) 3.4三段三时限复合电压过流保护(可带方向、低电压闭锁、负序电压闭 锁) (11) 3.5充电保护(可带方向、低电压闭锁、负序电压闭锁) (12) 3.6 PT断线退电流保护 (13) 3.7两段三时限过流保护(仅适用于3320-OL和3322-OL) (13) 3.8三段三时限零序过流保护(可带方向、零序电压闭锁) (14) 3.9零序过压保护 (15) 3.10间隙零序过流保护 (16) 3.11 过负荷保护 (16) 3.12过负荷启动风冷 (17) 3.13过载闭锁有载调压 (17) 3.14 PT、CT断线告警 (17) 3.15辅助功能 (18) 4装置定值整定及接线原理图、端子图 (19) 4.1装置的安装开孔图 (19) 4.2 DMP3320变压器差动保护装置 (19) 4.3 DMP3320OL变压器差动过流一体化保护装置 (24) 4.4 DMP3322变压器差动保护装置 (26) 4.5 DMP3322OL变压器差动过流一体化保护装置 (30) 4.6 DMP3323变压器后备保护测控装置 (31) 4.7 DMP3324变压器后备保护装置 (36) 4.8 DMP3325变压器后备保护装置 (43) 5 整定说明 (48) 6调试大纲 (52)

PST_693U变压器保护测控装置

·装置概述· 1 国 电 南 自 Q/GDNZ.JB051-2007 标准备案号:708-2007 PST 693U 变压器保护测控装置 说 明 书 国电南京自动化股份有限公司 GUODIAN NANJING AUTOMATION CO.,LTD

1 PST693U 变压器保护测控装置 说明书 Ver1.1 国电南京自动化股份有限公司 2008年11月

版本声明 本说明书适用于变压器保护测控装置V1.1版本 产品说明书版本修改记录表 * 技术支持电话:(025)83421394-8120 传真:(025)83421394-8118 *本说明书可能会被修改,请注意核对实际产品与说明书的版本是否相符 * 2008年11月第2版第1次印刷 1

1 目次 1 装置概述 (1) 2技术性能及指标 (3) 2.1 额定电气参数 (3) 2.2 主要技术指标 (3) 2.3 环境条件 (4) 2.4 功率消耗 (4) 2.5 过载能力 (4) 2.6 绝缘性能 (4) 2.7 耐湿热性能 (4) 2.8 电磁兼容性 (5) 2.9 机械性能 (5) 3 功能 (6) 4 原理说明 (7) 4.1 三段式复合电压过流保护 (7) 4.2 反时限过流保护 (7) 4.3 两段式定时限负序过流保护 (8) 4.4 高压侧定时限零序过流保护 (8) 4.5 低压侧定时限零序过流保护 (8) 4.6 低压侧反时限零序过流保护 (8) 4.7 过负荷保护 (8) 4.8 过电压保护 (8) 4.9 低电压保护 (9) 4.10 非电量保护 (9) 4.11 TV断线告警 (9) 4.12 F-C闭锁功能 (9) 4.13 4-20mA直流输出(选配) (9) 5 整定 (10)

相关文档
相关文档 最新文档