HOW TO:

Install the PLC System Shutdown Upgrade

Contents:

Purpose and Description

Parts Included

Required Materials and Tools

Procedure

Troubleshooting

Appendix A: Updating the PLC Firmware in the Field

Purpose and Description:

This guide describes what is required to install the XIS upgrade to prevent the

PLC from cutting off power prematurely to the PC during system shutdown.

Hard drives have been failing on the Dell Optiplex series of PCs (models 745,

755, and 760 running Windows XP) due to longer shutdown times than previous systems running Windows 2000. The upgrade will allow the PC to complete its

shutdown before power to it is cutoff. It includes a new signal input to the PLC

from the PC that Windows XP has completed its shutdown.

The procedure assumes that the PLC will be removed and replaced by a new PLC with a pre-programmed firmware update. However, if the PLC is to stay in the

XIS, and the required firmware update downloaded to it directly, there are

additional parts and procedures required. See the additional parts required in the “Parts Included” section, and the procedure given in Appendix A for re-

programming the PLC.

IMPORTANT NOTE: All new production XIS machines with “Xray

Client” REV 2.0.2.3 or later already include the upgrades covered in

this instruction. For machines being upgraded to “Xray Client” REV

2.0.2.3, this is a required procedure. Otherwise the XIS will not have

the correct shutdown functionality.

Parts Included:

1. Hardware

A. 5” 18 AWG white jumper wire with pre-crimped spade terminals at

each end (Qty. 1).

B. * Only if the PLC is to be removed and replaced, also included:

i. Allen-Bradley MicroLogix 1000 PLC with the pre-programmed

firmware (current revision for shutdown upgrade) (Qty. 1).

NOTE: For specific Health Canada requirements (and

other future applications), certain XIS-1517 and

1818 machines will use a further-modified PLC

firmware revision.

C. * Only if the PLC is to be re-programmed in the field, also included:

i. Allen-Bradley PC-to-PLC data cable (Qty. 1).

P/N: A-B 1761CBLPM02

ii. Allen-Bradley USB dongle for use of the Allen-Bradley

“RSLogix 500 Starter” software (Qty. 1).

P/N: A-B 9509USBDONG

2. Software

A. Xray Client files (current revisions for shutdown upgrade). These are

already included in REV 2.0.2.3 and later.

i. CloseDas.exe

ii. IOcontrol.exe

iii. Shutdown.exe

B. * Only if the PLC is to be re-programmed in the field, also included:

i. Allen-Bradley “RSLogix 500 Starter” software CD-ROM (to be

installed to service engineer’s jobsite laptop).

P/N: A-B 9324RL0100ENE

3. Firmware

A. * Only if the PLC is to be re-programmed in the field:

i. PLC firmware (current revision for shutdown upgrade).

NOTE: For specific Health Canada requirements (and

other future applications), certain XIS-1517 and

1818 machines will use a further-modified PLC

firmware revision.

Required Materials and Tools:

1. USB keyboard.

2. Phillips screwdriver for terminal block connections.

3. * Only if the PLC is to be re-programmed in the field:

i. Laptop PC with a serial port (DB9).

NOTE: If the laptop does not have a serial port, a USB-serial

adapter cable and its hardware driver will be required. See

Appendix A.

4. Soldering iron and all related tools, materials, and solder.

5. USB mouse optional for convenience instead of the AOCP touchpad. If a

USB mouse is unavailable, see Figure 1 below for the equivalent left and

right-button mouse click function.

Figure 1. AOCP Touchpad’s “Mouse Click”

Equivalent Functions

Procedure:

1. Hardware Installation

For Production:

Install the PLC with the pre-programmed firmware (current

revision for shutdown upgrade). Then, follow the wiring changes

outlined in the procedure for service engineers below. This

includes a PLC to AOPC Interface Board change, and a PLC to

PLC-PC Interface Board change.

NOTE: For specific Health Canada requirements (and

other future applications), certain XIS-1517 and

1818 machines will use a further-modified PLC

firmware revision.

For Service Engineers:

Step 1A. PLC

Make sure that all standard safety precautions are

complied with, power down the XIS, and open the

cabinet to gain access to the PLC. Remove and replace

it with the PLC that is pre-programmed with the required

firmware revision for the shutdown upgrade.

NOTE: For specific Health Canada requirements

(and other future applications), certain XIS-

1517 and 1818 machines will use a further-

modified PLC firmware revision.

If the PLC is not to be replaced, but re-programmed in

the field, see the procedure in Appendix A.

Step 1B. PLC to PC-PLC Interface Board Terminal Block

i. On the terminal block of the PC-PLC interface board,

screw one end of the 5” white jumper wire to position

4 (from the left). See Figure 2 below.

ii. Screw the other end of the 5” white jumper wire to

the PLC input position I/5. This is a signal from the

PC to inform the PLC that it has completed its shut

down. See Figure 2 below.

Figure 2. PLC and PC-PLC Interface Board

After Adding the 5” White Jumper Wire

Step 1C. AOCP Interface Board

On the terminal block of the AOCP interface board,

move the spade terminal connected to position 1 over to

position 2 (from the left). This wire is going to the PLC

input position I/4 and is the key switch signal from the

AOCP. See Figure 3 below.

Figure 3. AOCP Interface Board Terminal Block

“Before and After”

2. Software Installation

For Production:

The most current “Xray Client” software revision must be pre-

installed on the PC.

For Service Engineers:

The following procedure is only for systems running a revision of

“Xray Client” software earlier than REV 2.0.2.3. For all systems

which are being upgraded at this time to “Xray Client” REV

2.0.2.3 or later, refer to the document “HOW TO: Install Xray

Client 2.0.2.3 on XIS Machines in the Field” for the software

installation.

Step 2A. Turn the system on with the AOCP system power key

switch.

IMPORTANT NOTE: Steps 2B through 2E

above must be completed within 5 seconds to

prevent the PC from shutting down due to the

new hardware upgrade. For this reason,

screen shots for each step are provided for

more detail and should be reviewed first

before beginning.

Step 2B. Once the system has completed initializing and the X-ray imaging log in screen is available, using the AOCP’s

touchpad or a USB mouse, immediately point to and

click anywhere on the log in screen (“Screen 1”) to

make it active. See Figure 4 below.

NOTE: When using the AOCP touchpad, a double-

tap on the pad is the equivalent of a left-

button mouse click.

Figure 4. X-ray Imaging Log In Screen

Step 2C. At the X-ray imaging log in screen, immediately press the AOCP’s “ENTER” key to go to the Windows XP

desktop. See Figure 5 below.

Figure 5. AOCP’s “ENTER” Key

Step 2D. On the Windows XP desktop, click on the “Shutdown”

application’s taskbar button (at bottom edge of the

screen) to maximize its dialog box. The pointer may

need to hover over the bottom edge of the screen in

order to show the taskbar if it is hidden. See Figure 6

below.

Figure 6. “Shutdown” Application’s

Button on the Taskbar

Step 2E. Close the “Shutdown” application with its upper right corner “Close” button. See Figure 7 below.

Figure 7. “Shutdown” Application’s

“Close” Button

Step 2F. Next, stop the “IOcontrol.exe” process. To do this, press and hold the “Ctrl – Alt – Delete” keys at the same time,

and then select the “Task Manager” button from the

“Windows Security” dialog box that pops up. On the

“Processes” tab in the “Windows Task Manager,” select

the “IOcontrol.exe” application, and then click on “End

Process.” See Figure 8 below.

Figure 8. Windows Task Manager

Step 2G. Navigate to the “c:\Program Files\Xray Client” folder.

If there is any problem locating the “Xray Client” folder,

follow the steps in Figure 9 and the summary below.

Figure 9. Navigating to the “Xray Client” Folder

Summary of “Figure 9. Navigating to the ‘Xray Client’

Folder”:

Fig. 9 / Step 1: Click the Windows XP “Start”

button (1-A), and then the “My Computer” menu

item (1-B).

Fig. 9 / Step 2: Double click the “Local Disk (C:)”

drive.

Fig. 9 / Step 3: Double click the “Program Files”

folder to open it.

Fig. 9 / Step 4: Double click the “Xray Client”

folder to open it and locate the files to be renamed.

Rename the following files one at a time by right-

clicking on them, and selecting “Rename” from the

context menu that pops up. See Figure 10 below.

NOTE: When using the AOCP touchpad, a tap on

the upper-right corner of the pad is the

equivalent of a right-button mouse click.

i. Rename “IOcontrol.exe” to “IOcontrol Old.exe”

ii. Rename “Shutdown.exe” to “Shutdown Old.exe”

NOTE: “CloseDas.exe” is a new file to “Xray

Client” and does not need to be renamed.

Figure 10. “Rename” File Option on a File’s

Right-Click Context Menu

Step 2H. Copy the three included “Xray Client” files

(“CloseDas.exe,” “IOcontrol.exe,” and “Shutdown.exe”)

into the same “c:\Program Files\Xray Client” folder as

above.

Step 2I. Click the Windows XP “Start” button, and then click the “Log Off” button. Next, at the Windows XP log in

screen, click the “Astrophysics” user account to log in

again and restart the X-Ray imaging application. See

Figure 11 below.

Figure 11. Restarting “Xray Client”

IMPORTANT NOTE: Step 2J must be

completed within 5 seconds to prevent the PC

from shutting down due to the new hardware

upgrade. For this reason, it should be

reviewed first before beginning.

Step 2J. Repeat Steps 2B through 2D above. This time, uncheck

the “KeySwitch” radio button, and click the “OK”

button to apply the change. Clicking the “OK” button is

required to save it. See Figure 12 below.

Figure 12. Deselecting the Shutdown Application’s

“KeySwitch” Option

Step 2K. Turn the system off with the AOCP system power key

switch.

3. Testing Procedure

The time until power is cutoff during system shutdown down (as

controlled by the PLC) has been changed from a fixed 30 seconds, to a

variable time not to exceed 1 minute. Power cutoff now depends on when

the PC completes its shutdown. Before the upgrade, power would be

cutoff regardless of whether Windows XP had completed its operations

and shutdown properly or not.

With the upgrade, the PLC will cutoff system power 1 minute after the key switch is turned off by the operator, unless it receives a signal from the PC that it has shutdown sooner (which is normal). In that case, the PLC

would cutoff power 3 seconds after the PC shutdown is complete. The 1

minute “timed-out” power cutoff would only be necessary for a frozen PC.

Under normal conditions, the PC will always shutdown well within 1

minute, and usually less than 30 seconds.

Use the following procedure to test an XIS with a completed upgrade.

Step 3A. Turn the system on with the AOCP system power key

switch.

Step 3B. Log in to the X-ray imaging application, and begin

scanning to acquire a few images.

Step 3C. Turn the system off with the AOCP system power key

switch. The tester should observe the following power

shutdown sequence:

i. The X-ray imaging application logs out.

ii. Windows XP begins closing, and then the PC shuts

down (both displays show a black screen).

iii. Three seconds after PC shutdown, the PLC cuts off

power, and all green system power indicator lights

turn off (cabinet indicator lights).

NOTE: The AOCP power indicator light turns off

with the key switch.

Troubleshooting:

This section describes troubleshooting solutions for the PLC system shutdown

upgrade.

Condition 1. At the X-ray imaging log in screen, the PC shuts down by

itself within 5 seconds.

Check that the setting being changed in Step 2J from the

software installation section is properly saved. The “OK”

button must be clicked to save the change. The “Shutoff”

application dialog box can not simply be closed after

unchecking the “KeySwitch” radio button.

Condition 2. System shutdown does not follow the proper sequence.

Step 2A. Check that the PLC firmware revision is correct.

Step 2B. Check that the wiring in Steps & has been correctly

changed and/or installed.

Step 2C. Check that the “Xray Client” software upgrade has been

installed correctly as per the instructions.

Appendix A: Updating the PLC Firmware in the Field

Service engineers who are to re-program, rather than swap out pre-programmed

PLCs in the field, need to carry some additional parts and tools. These are given above in the “Parts Included” section under the “Hardware” and “Firmware”

subsections 1C and 3A respectively, and the “Required Materials and Tools”

section under subsection 3.

Additionally, the Allen-Bradley “RSLogix 500 Starter” software must be pre-

installed on a laptop to carry to the jobsite. This is given in the “Parts Included”

section above under the “Software” subsection 2B.

NOTE: For service engineers running Windows XP or earlier on their

laptops, the following steps apply without further instructions.

For service engineers running Windows Vista and later on their

laptops, the “RSLogix 500 Starter” software will further

instructions forthcoming, both for installation and to run the

program.

Procedure:

Step 1. Make sure that the XIS is powered down.

Step 2. Connect the Allen-Bradley USB dongle to the laptop which has

the “RSLogix 500 Starter” software, and start the application

using the required revision of the PLC firmware. The shortcut

will look similar to the one immediately below (firmware revision

“REV1” used only as an example, be sure to use current revision).

Step 3. Connect the serial (DB9) end of the Allen-Bradley PC-to-PLC

data cable to the laptop. If the laptop does not have a serial port, a

USB-Serial adapter will be required, and the hardware driver for

it must be installed. See the example in Figure 13 below.

Figure 13. An Example USB-Serial Adapter Cable and

Driver on Mini CD

See Figure 14 below for a picture of the Allen-Bradley data cable.

Figure 14. Allen-Bradley PC-to-PLC Data Cable

Step 4. Make sure that all standard safety precautions are complied with, and open the XIS cabinet to gain access to the PLC. Locate and

open the data port cover on top of the PLC, and connect the other

end of the PC-to-PLC data cable to the PLC. See Figure 15

below.

Figure 15. Connecting the PC-to-PLC Data Cable to the PLC Step 5. The “RSLogix 500 Starter” application window will look as shown in Figure 16 below. Locate the “Process Status” menu

circled in Figure 16. This is the only menu that is necessary to

complete the procedure.

Figure 16. “RSLogix 500 Starter” Application Window and the

“Processor Status” Menu

Step 6. Click the “Processor Status” menu’s dropdown arrow, and click on “Download...” See the menu excerpt immediately below.

Step 7. Next, follow the steps shown in Figure 17 and the summary

below.