Agency Listings

4-Wire Photoelectric Duct Smoke Detector

The InnovairFlex ? Series are the only duct smoke detectors flexible enough to fit configurations from square to rectangular and everything in between.Features

Photoelectric, integrated low-flow technology

? Air velocity rating from 100 ft/min to 4,000 ft/min (0.5 m/s to 20.32 ? m/sec)

Versatile mounting options: square or rectangular configuration ? Plug-in sensor offers superb false alarm immunity and the latest ? sensor technology

Broad ranges for operating temperature (–4°F to 158°F) and ? humidity (0% to 95% non-condensing)

Patented sampling tube installs from front or back of the detector ? with no tools required

Increased wiring space with a newly added ?-inch conduit ? knockout

One easy-access Test/Reset button and improved LED status ? Patented interconnect feature for multi-fan shutdown ? New high contrast terminal designations

? Built-in short circuit protection from operator wiring errors ? Field selectable settings for configuring the detector ? Two DPDT Form-C relay contacts ? 24 VAC/DC or 120VAC

? Backward compatibility with existing Innovair products, including ? remote accessories

The InnovairFlex D4120 4-wire photoelectric duct smoke detector features a pivoting housing that fits both square and

rectangular footprints and mounts to round or rectangular ductwork. This unit senses smoke in the most challenging conditions, operating in airflow speeds of 100 to 4,000 feet per minute, temperatures of –4°F to 158°F, and a humidity range of 0 to 95 percent (non-condensing). A plug-in sensor head offers improved false alarm immunity and simple installation, testing, and maintenance. An improved cover design isolates the sensor head from the low-flow feature for simple maintenance.

The InnovairFlex housing provides ample wiring space, a ?-inch conduit knockout, and built-in short circuit protection to prevent damage to sensitive components during installation. High contrast terminal designations make wiring easy. With its 2:1 sensor-to-power capability, the power board of the D4120 may be used to monitor a second sensor ,D4S, simultaneously (i.e., supply and return side). As many as 50 InnovairFlex detectors can be interconnected. When one unit senses smoke, all interconnected detectors will switch their relays; only the detector sensing smoke will go into alarm, thus pinpointing the fire source.

An easy-access Test/Reset button makes it possible to test the unit with the cover on. Three DIP switches can be used to configure field selectable settings: cover tamper delay, number of sensors to be controlled, and shut down on trouble option. Each power board has two LEDs that can be used to indicate the status of connected sensors, and a quick reference imprinted on the cover explains the LED status indications (Standby, Maintenance, Trouble, and Alarm). The InnovairFlex duct smoke detector can be customized to meet local codes and specifications without additional wiring. The new InnovairFlex product line is compatible with all previous Innovair models, including remote test accessories.

WARNING: Duct smoke detectors are NOT a substitute for open area smoke detectors; NOT a substitute for early warning detection; NOT a replacement for a building’s regular fire detection system.

Refer to NFPA 72 and 90A for additional information.

A05-0419-000

InnovairFlex ? Duct Smoke Detector Specifications

Architectural/Engineering Specifications

The air duct smoke detector shall be a System Sensor InnovairFlex ? D4120 Photoelectric Duct Smoke Detector. The detector housing shall be UL listed per UL 268A specifically for use in air handling systems. The flexible housing of the duct smoke detector fits multiple footprints from square to rectangular. The detector shall operate at air velocities of 100 feet per minute to 4000 feet per minute (0.5 to 20.32 meters/second). The unit shall be capable of controlling up to 50 air handling systems when interconnected with other detectors. The detector shall be capable of providing a trouble signal in the event that the front cover is removed. It shall be capable of local testing via magnetic switch, test button on the cover, or remote testing using the SSK451 Multi-Signaling Accessory or the RTS451KEY Remote Test Station. Terminal connections shall be of the strip and clamp method suitable for 12–18 AWG wiring.Physical Specifications

Size: (Rectangular Dimensions) (Square Dimensions)14.38 in (37 cm) Length; 5 in (12.74 cm) Width; 2.5 in (6.36 cm) Depth 7.75 in (19.7 cm) Length; 9 in (22.9 cm) Width; 2.5 in (6.35 cm) Depth Weight: 2.5 lbs (1.14 kg)Operating Temperature Range:D4120 & D4S : –4° to 158°F (–20° to 70°C); D4P120: –40° to 158°F (–40° to 70°C)Storage Temperature Range:D4120 & D4S : –22° to 158°F (–30° to 70°C); D4P120: –40° to 158°F (–40° to 70°C)Operating Humidity Range:0% to 95% relative humidity non-condensing Air Duct Velocity:100 to 4000 ft/min (0.5 to 20.32 m/sec)Electrical Ratings Power supply voltage:20–29 VDC 24 VAC 50–60 Hz

120 VAC 50–60 Hz Input capacitance:270 μF max.270 μF max.N/A

Reset voltage: 3.0 VDC min. 2.0 VAC min.10 VAC min.Reset time: (with RTS451).03 to 0.3 sec..03 to 0.3 sec..03 to 0.3 sec.Reset time: (by power down)0.6 sec. max.0.6 sec. max.0.6 sec. max.Power up time:35 sec. max.35 sec. max.35 sec. max.Alarm response time:15 sec.15 sec.

15 sec.

Sensitivity Test:See detector label See detector label See detector label Current Requirements: (Using No Accessories)Max. standby current:21 mA @ 24VDC 65 mA RMS @ 24VAC 60Hz 20 mA RMS @ 120VAC 60Hz

APA151/APA45112.5 mA n/a 30 mA Max.MHR/MHW 0 mA n/a 29 mA Max.RA400Z 0 mA n/a 12 mA Max.

RTS451/RTS451KEY 0 mA/12 mA

n/a 12 mA Max.SSK4518 mA Max.16 mA Max.40 mA Max.Note: A ny combination of accessories may be used such that the given accessory loads are: 110 mA or less at the Aux output, and 50 mA or less at the Alarm output

Installing the InnovairFlex Sampling Tube

The InnovairFlex sampling tube may be installed from the front or back of the detector. The tube locks securely into place and can be removed by releasing the front or rear locking tab (front locking tab shown below right).

A05-0419-000

Wiring for 4-wire Duct Smoke Detector and Accessories

Important Notes on 2:1 Sensor-to-Power Capability ? 2:1 sensor-to-power capability is not available for all InnovairFlex models. The feature is only available on the D4120 4-wire conventional models. ? 2:1 sensor-to-power capability can be enabled using one D4120 and one D4S, or two D4S and one D4P120.

Important Interconnect Notes

? When using the interconnect feature, all interconnected units must be powered using the same independent supply.? P olarity must be maintained throughout the interconnect wiring. Connect the INT+ terminal on unit 1 to the INT+ terminal on unit 2 and so on. Similarly, connect the INT/AUX– terminal on unit 1 to the INT/AUX- terminal on unit 2 and so on.? Up to 50 D4120 units, 50 D4P120 units, or 50 units of combination may be interconnected.? U p to 10 DH100ACDC units may be interconnected. Please note that each of the 9 DH100ACDC units interconnected may be replaced by three D4P120 units. Therefore, when using the interconnect feature a single DH100ACDC can drive either 9 DH100ACDCs or 27 D4120 units.* NOTE: A larm can be reset only at the initiating device and not at the devices interconnected.

NOTE 1: 24V Power Inputs accept a non-polarized 24VDC or 24VAC 50-60Hz.

120VAC Power Inputs accept only 120VAC 50-60Hz. Connect power source to appropriate terminals of each detector. See specifications for additional power supply information.

NOTE 2: A uxiliary contacts shown in standby position. Contacts switch

during alarm as indicated by arrows. Auxiliary contacts are not to be used for connection to the control panel. See specifications for contact ratings.

NOTE 3: S upervisory contacts shown in standby position. Open contacts

indicate a trouble condition to the panel. See specifications for contact ratings.

NOTE 4: A larm Initiation contacts shown in standby position. Closed

contacts indicate an alarm condition to the panel. See specifications for contact ratings.

*Please refer to the corresponding installation manual for accessory wiring diagrams.

Accessories

System Sensor provides system flexibility with a variety of accessories, including two remote test stations and several different means of visible and audible system annunciation. As with our duct smoke detectors, all duct smoke detector accessories are UL listed.

Ordering Information

Part No.Description

D4120

4-wire photoelectric low-flow duct smoke detector Accessories D4S 4-wire photoelectric sensor component only

MHR Mini Horn, Red D4P120 4-wire photoelectric power board component only, 24 VAC/DC, 120 VAC

MHW

Mini Horn, White

2D514-wire conventional photoelectric sensor head P48-21-00

End cap for metal sampling tubes DST1Metal sampling tube duct width up to 1ft (0.3m)

PS12/24SLENSC Ceiling-mount “SMOKE” lens DST1.5 Metal sampling tube duct widths 1 ft to 2 ft (0.3 to 0.6 m) PS12/24SLENSW Wall-mount “SMOKE” lens DST3Metal sampling tube duct widths 2 ft to 4 ft (0.6 to 1.2 m)PS24LO

Mini-Alert add-on strobe (red)DST5Metal sampling tube duct widths 4 ft to 8 ft (1.2 to 2.4 m)PS24LOW

Mini-Alert add-on strobe (white)DST10

Metal sampling tube duct widths 8 ft to 12 ft (2.4 to 3.7 m)RA400Z Remote annunciator alarm LED

APA151Remote annunciator with piezo alarm RTS451Remote test station

DH400 OE-1Weatherproof enclosure

RTS451KEY

Remote test station with key lock ETX

Metal exhaust tube duct width 1ft (0.3m)SSK451

Multi-signaling accessory

M02-04-00

Test magnet

RTS451 UL S2522RA400Z UL S2522RTS451KEY UL S2522MHW UL S4011MHR UL S4011

APA151 UL S4011SSK451 UL S2522

SSK451 with PS24LOW strobe and PS12/24 LENSW lens