文档库 最新最全的文档下载
当前位置:文档库 › DH100ACDCI中文资料

DH100ACDCI中文资料

Agency Listings

4-Wire Ionization Duct Smoke Detector

System Sensor’s Innovair DH100ACDCI reduces the spread of smoke through HVAC air handling systems. As an ionization duct detector, it’s ultra-responsive to submicron-sized smoke particles typically found near a fire source.

Features

Ionization technology

An air velocity rating from 500 feet per minute to 4,000 feet per minute (2.54 meters per second to 20.32 meters per second)Patented interconnectability for multi-fan shutdown Two DPDT Form-C relay contacts 24 VAC/DC or 120/240 VAC Versatile mounting options Outside mounting tabs

A patented telescopic sampling tube Modular construction

A patented cover-tamper trouble signal A transparent cover A remote test station

Remote sounder/LED indicator options A built-in reset button

??????????????The DH100ACDCI senses smoke in velocities from 500 to 4,000 feet per minute. When smoke is detected, all interconnected Innovairs will initiate their relays. However, to quickly locate the fire source, only the detector sensing smoke will alarm. Two DPDT Form-C relay contacts, connected to auxiliary equipment, can also be configured to prevent the spread of smoke through a particular area.

Beyond its reliable performance, the DH100ACDCI is simple to install and maintain. Powered by 24 VAC/DC or 120/240 VAC, it can be easily mounted to round and rectangular ducts, from one to twelve feet in width, with outside mounting tabs. It also offers an adjustable telescopic sampling tube that can be used for duct widths up to 18 inches. The tube locks into place – no additional tools are necessary.Its modular construction allows for easy cleaning and field replacement of the power and sensor boards. Also simplifying maintenance is a transparent cover that provides convenient visual inspection. If the cover is removed, a patented cover-tamper trouble signal gives a 7-minute delay before the panel or remote accessory is notified of trouble.

At a remote location, the remote test station option ensures that a detector is functioning properly, and the remote sounder/LED indicator options signal if a detector is in alarm. However, the cover does not need to be removed if a detector needs to be reset at the detector. Simply push the built-in reset button.

WARNING: Duct smoke detectors are NOT a substitute for open area smoke detectors, NOT a substitute for early warning detection and NOT a replacement for a building’s regular fire detection system.

Refer to NFPA 72 and 90A for additional information.

268A

Innovair Duct Smoke Detector Specifications

Architectural/Engineering Specifications

The air duct smoke detector shall be a System Sensor Model DH100ACDCI Series Duct Smoke Detector. The detector housing shall be UL listed per UL 268A specifically for use in air handling systems. The detector shall operate at air velocities of 500 feet per minute to 4000 feet per minute (2.54 to 20.32 meters/ second). The unit shall be capable of controlling up to ten (10) air handling systems when interconnected with other detectors. The detector shall be capable of providing a trouble signal in the event that the front cover is removed. It shall be capable of local testing via magnetic switch or remote testing using the SSK451 Multi-Signaling Accessory or the RTS451KEY Remote Test Station. The unit shall be reset by local reset button or remote test station. The duct smoke detector housing shall incorporate an airtight smoke chamber in compliance with UL 268A, Standard for Smoke Detectors for Duct Applications. The housing shall be capable of mounting to either rectangular or round ducts without adapter brackets. An integral filter system shall be included to reduce dust and residue effects on detector and housing, thereby reducing maintenance and servicing. Sampling tubes shall either be telescoping or be easily installed by passing through the duct housing after the housing is mounted to the duct. The unit shall provide a spacial separation of no less than ?? (6.4 mm) and/or a physical barrier between the high and low voltage terminals. The enclosure shall meet all applicable NEC and NFPA standards regarding electrical junction boxes. Terminal connections shall be of the strip and clamp method suitable for 12–18 AWG wiring.

Physical Specifications

Size143?8? (37 cm.) Length; 5?? (14 cm.) Width; 2?? (7 cm.) Depth

Shipping Weight3? lbs. (1.7 kg.)

Operating Temperature Range32° to 120°F (0° to 49°C)

Operating Humidity Range10% to 93% relative humidity non-condensing

APA45112.5 mA Max.n/a30 mA Max.

PA4000 mA n/a15 mA Max.

RA400Z0 mA n/a10 mA Max.

RTS451/RTS451KEY12 mA*n/a7.5 mA Max.

SSK451 5 mA Max.9 mA Max.30 mA Max.

*Note: W hen a unit is powered at the 120 VAC or 220/240 VAC input, any combination of accessories may be used such that the given accessory loads are: 60 mA or less in the standby state; 110 mA or less in the alarm state.

A05-0315-002

A05-0315-002

Wiring Guide

System wiring diagram for 4-wire duct smoke detectors

Wiring diagram for DH100ACDCI to SSK451 and interconnect feature:

NOTE: Wiring diagram shown is for DH100ACDCI 4-wire duct smoke detector system equipped without a control panel.NOTE: A trouble condition is indicated when the green LED is not illuminated.

Important Interconnect Notes

? When using the interconnect feature, all interconnected units must be powered with the same, independent supply.? P olarity must be maintained throughout the interconnect wiring. Connect terminal 12 on unit 1 to terminal 12 on unit 2 and so on. Similarly, connect terminal 1 on unit 1 to terminal 1 on unit 2 and so on.

Wiring diagram for the DH100ACDCI to RTS451/RTS451KEY and interconnect feature:

Wiring diagram for DH100ACDCI to APA451:

UL LISTED 4-WIRE CONTROL PANEL

FIRST DETECTOR IN THE LOOP DH100ACDCI

LAST DETECTOR IN THE LOOP DH100ACDCI

SPECIFIED BY

PANEL MANUFACTURER

*NOTE: F or RTS451KEY only without a Control

Panel.

RTS451 does not have a terminal 6.NOTE: W iring diagram shown is for DH100ACDCLP

4-wire duct smoke detector system equipped without a control panel.NOTE: A trouble condition is indicated when the

green LED is not illuminated.

Coil Note:

Please note that the magnetic coil supplied with the RTS451/RTS451KEY is not required when these accessories are used with the DH100 detectors. The functionality of the magnetic coil has been designed into the circuitry of the Innovair duct smoke detectors.

Ordering Information

Part No.Description

DH100ACDCI4-wire ionization duct smoke detector

A5052Replacement ionization detector board

A5064Replacement 4-wire power board

Accessories

ST-1.5Metal sampling tube duct widths 1′–2′ (0.3–0.6 m)MOD400R Sensitivity test module

ST-3Metal sampling tube duct widths 2′–4′ (0.6–1.2 m)RA400Z Remote annunciator alarm LED

ST-5Metal sampling tube duct widths 4′–8′ (1.2–2.4 m)F36-09-11Replacement air filters (two per package)

ST-10Metal sampling tube duct widths 8′–12′ (2.4–3.7 m)M02-04-00Test magnet

T80-71-00Replacement telescoping sampling tube P48-21-00End cap for metal sampling tubes

P48-55-00Replacement end cap for T80-71-00S08-39-01Photo replacement screen

SSK451Multi-signaling accessory PA400W Mini-Alert sounder

RTS451KEY Remote test station with key lock PS24LOW Mini-Alert add-on strobe

RTS451Remote test station PS12/24SLENSW Wall-mount “SMOKE” lens

APA451Remote annunciator with piezo alarm PS12/24SLENSC Ceiling-mount “SMOKE” lens Accessories

System Sensor provides system flexibility with a variety of accessories, including two remote test stations and several different means of visible and audible system annunciation. As with our duct detectors, all duct smoke detector accessories are UL listed.

SSK451

Multi-Signaling

Accessory

(UL 268A)

SSK451

Multi-Signaling Accessory

(UL 268A)

shown with PS24LOW add-on

strobe (PS12/24SLENSW smoke lens

option available)

APA451

Piezo Annunciator

(UL S4011)

RTS451KEY

Remote Test Station

with Key (UL S2522)

PA400W

Mini-Alert Sounder

(UL S3593)

shown with PS24LOW add-on

strobe (PS12/24SLENSW smoke

lens option available)

RTS451

Remote Test Station

(UL S2522)

RA400Z

Remote Annunciator

(UL S2522)

相关文档