AUXILIARY FEATURES
?LED operating indicator ?Remote ON/OFF ?
Remote sense
SPECIFICATIONS
INPUT Voltage 85-264 VAC (continuous)
(90-264 VAC between -10 to 0°C)Frequency 47-63 Hz
Current
Full Load
120V 2 - 2.2 (RMS)240V 1 - 1.1 (RMS)Inrush
120V - 20A (TYP)240V - 40A (TYP)
OUTPUT
Total Regulation +5.0%
Ripple & Noise (peak-to-peak)
100mV or 1% (whichever is larger)(measured at 25°C with a bandwidth of 100 MHz)Hold-up Time
20mS min.
(measured at nominal input voltage, full load, 25°C)Start-up Time
1S (max)
PROTECTION Overvoltage
All models are protected against over-voltage. Control circuit is preset so output voltage does not exceed the following values:Output V 3.3 5.012
15
24
48 OVP
4.5 6.9
15.519.530
60
Overload
All models are protected against
overload and short circuit. Recovery is automatic after removal of the fault.
ISOLATION
Input to Chassis 2000VAC for 1 minute Input to Output 3000VAC for 1 minute Output to Chassis 500VAC for 1 minute Insulation 100M ?at 500VDC Leakage Current 0.2mA (max) at 120VAC, 60Hz per
UL1950, EN60950
0.75mA (max) at 254.4VAC, 60Hz per CSA22.2 No. 950
ENVIRONMENT Operating T emp.-10°C to + 50°C at full load
(derated to 50% from 50°C to 60°C)Operating Humidity 20% - 90% relative humidity (non-condensing)Storage T emp.-30°C to + 85°C
Storage Humidity
10% - 95% relative humidity (non-condensing)Shock 10G
Vibration
2G, 10 - 55 Hz, 0.75mm amplitude,for 2 hours (non-operating)
MODEL SPECIFICATIONS
4.92 (125±0.5)
0.94 (24)
1.97 (50±0.5)
0.85 (21.5)
6mm
4-M4
MECHANICAL SPECIFICATIONS
Size (W + D + H): 3.66 x 7.83 x 2.36 inches
(93 x 199 x 60 mm)
6mm
3-M47.83 (199±1)
0.20 (5)80
0.79 (20)
0.98 (25±0.5)0.77 (19.5)
0.17 (4.2)
3.94 (100±0.5)
.55 (14)
2.36 (60±1)
0.67 (17)
3.15 (25±0.5)
3.66 (93±1)
CN1
DPI +RS +V -V -RS FG L TB1
N +R S
+V -V -R S L N
F G 1.26 (32)