文档库 最新最全的文档下载
当前位置:文档库 › ABB-电子式热继电器样本

ABB-电子式热继电器样本

ABB-电子式热继电器样本
ABB-电子式热继电器样本

Electronic Overload Relays

New complete range up to 1250A

N e w

ABB

■Up to 1000V and temperature range from -25 … +70 °C ■Acc. to IEC/EN 60 947-4-1 and UL508

■Tripping classes 10, 20, 30

■ATEX / Ex-approved

■ Low-energy consumption

■Direct mounting to ABB contactors

■Separate mounting kits available

■Independent from ambient temperature

■Wide setting range Electronic overload relays…

…are environmental friendly

■ Low power consumption saves energy

■ Materials employed can be recycled

…are safe and ? exible

■ Better accuracy

■ Digital evaluation

■ Less variants

…save costs

■ smaller cabinets due to less heat dissipation ■ less inventory

Electronic overload relays from ABB A complete range from 0,1A …1250A

E16DU

E45DU

E80DU

E140DU

E200DU Motor Starter Combinations – Overview

Cost savings

?

The wide setting range and integrated tripping classes 10, 20, 30 substantially reduce the number of different types.

This is a major bene? t for planning, project implementation, inventory and logistics.? The low power consumption saves energy costs

? The low level of heat dissipation reduces cost of cooling or ventilation

?

Temperature compensation of -25 to +70 °C prevents nuisance shut-down in response to changes in temperature

and assures high precision and reliability

Technical Features

?No external power supply needed ?Low energy consumption ?Low heat dissipation ?Wide setting range

?Wide temperature range from -25 … +70 °C ?High safety standard

?Stable and precise trip curve throughout the entire life cycle ?Fast phase failure detection ?Test functions

?Manual and automatic reset ?

Stop button

Time

Ie (adjusted current)

No Tripping at 1.05 Ie

Tripping at 1.2 Ie within 2 hours

Class 10 4 - 10 sec

1.2 Ie

7.2 Ie

Class 20 6 - 20 sec

Class 30 9 - 30 sec

E320DU E500DU E800DU E1250DU

Electronic Overload Relays class 10, 20, 30

Accessories

ABB has always been committed to the issue of protecting motors. After all, any overload to a motor used in an industrial plant can give rise to production downtime and repair work, all of which drive costs up to a level many times the expense of investing in reliable overload and motor protection.Electronic overload relays protect the motor from:

■ overload

■ phase unbalance

■ phase failure

Reliable motor protection

An electronic overload relay has advantages compared to a conventional thermal overload relay in a wider range of settings and temperatures and a higher accuracy. In addition, electronic relays can be used in standard motors and for heavy-duty start-ups. A complete range of electronic overload relays from 0,1A to 1250A with tripping classes 10,20 and 30 is available. Up from construction size E45DU the tripping classes 10, 20 or 30 can be selected directly on the device.

ATEX certi? cates are available for protection of motors in explosion areas. These electronic overload relays are cost-effective – simply because you only need a few units to cover a wide measuring range. This delivers user bene? ts in terms of planning, inventory and service.

Another major advantage is the low power consumption, something which has a noticeable impact on energy costs and

the cost of housings and cooling provisions.

B r o c h u r e N o . 2

C

D C 107 012 B 0202 P r i n t e d i n t h e F e d e r a l R e p u b l i c o f G e r m a n y (11

ABB

ABB Global Contact Directory

The ABB Contact Directory (https://www.wendangku.net/doc/2111918159.html,/contacts/) helps you ? nd local contacts for ABB products in your country. Please select the relevant product group from the dropdown menu to the right or from the page.

ABB STOTZ-KONTAKT GmbH P . O. Box 10 16 80D-69006 Heidelberg

Telephone: ++49 62 21 / 701-0Telefax: ++49 62 21 / 701-729http://www.abb.de/stotzkontakt

Universal motor controller 0.16 – 850A

Tripping classes 5, 10, 20, 30Integrated inputs/outputs

Motor control and diagnostic functions Field bus connection

Thermal overload relays 0.1 – 310A Tripping classes 10, 20, 30

Electronic overload relays 0.1 – 1250A

Tripping classes 10, 20, 30

Manual Motor Starters 0.1 – 100A Tripping classes 10, 20

Integrated short circuit protection

Motor Protection from ABB

功率配电线电缆计算方法-与断路器、热继电器选择方法

功率配电线电缆计算方法 与断路器、热继电器选择方法 2019.12.4 一、电机功率与配线直径计算 首先要计算100KW负荷的线电流。 对于三相平衡电路而言,三相电路功率的计算公式是:P=1.732IUcosφ。 由三相电路功率公式可推出: 线电流公式:I=P/1.732Ucosφ 式中:P为电路功率,U为线电压,三相是380V,cos φ是感性负载功率因数,一般综合取0.8你的100KW负载的线电流: I=P/1.732Ucos φ=100000/1.732*380*0.8=100000/526.53=190A 还要根据负载的性质和数量修正电流值。 如果负载中大电机多,由于电机的启动电流很大,是工作电流的4到7倍,所以还要考虑电机的启动电流,但启动电流的时间不是很长,一般在选择导线时只按1.3到1.7的系数考虑。 若取1.5,那么电流就是285A。如果60KW负载中数量多,大家不是同时使用,可以取使用系数为0.5到0.8,这里

取0.8,电流就为228A。就可以按这个电流选择导线、空开、接触器、热继电器等设备。所以计算电流的步骤是不能省略。 导线选择: 根据某电线厂家的电线允许载流量表,选用50平方的铜芯橡皮电线,或者选70平方的铜芯塑料电线。 变压器选择: 变压器选择也有很多条件,这里就简单的用总容量除以功率因数再取整。S=P/cosφ=100/0.8=125KVA 选择大于125KVA的变压器就可以了。 50平方的铜芯电缆能承受多少电流也要看敷设方式和环境温度,还有电缆的结构类型等因素。 50平方10/35KV交联聚乙烯绝缘电缆长期允许载流量空气敷设长期允许载流量 (10KV三芯电缆)231A(35KV单芯电缆)260A直埋敷设长期允许载流量(土壤热阻系数100°C.cm/W)(10KV三芯电缆)217A(35KV单芯电缆)213A 二、根据功率配电缆的简易计算 已知电机的额定功率为22KW,额定电压为380V变压器距井场400米,试问配很截面积多大的电缆线? (铜的电阻率Ρ取0.0175)(一)有额定容量算出电机在额定功率下的额定电流

热继电器的选择和计算

看一下本题就知了, 有一台三相异步电动机额定电压为380伏,容量为10千瓦,功率因数为0.85,效率为0.95,选择交流接触器、热继电器及整定值。 解:已知U=380V,P=10KW,cosφ=0.85,η=0.95 电流I=P/(√3*U*cosφ*η)=10/(1.732*0.38*0.85*0.95)≈20A 选择交流接触器KM=Ie×(1.3~2)=26~40(A),选CJ10-40的接触器 选择热继电器FR=Ie×(1.1~1.5)=22~25(A),选JR16-20/30热元件22A的热继电器。 热元件整定值等于电动机额定电流,整定20A 答:电动机电流为20A,选40A的交流接触器,选额定电流30A热元件22A的热继电器,整定值20A。 I=P/(√3*U*cosφ*η)=10/(1.732*0.38*0.85*0.95)≈20A 、有一台三相异步电动机额定电压为380伏,容量为14千瓦,功率因数为0.85,效率为0.95,计算电动机电流。 解:已知U=380(V),cosφ=0.85,η=0.95,P=14(KW) 电流 此主题相关图片如下: 答:电动机电流29安培。 2、有一台三相异步电动机额定电压为380伏,容量为10千瓦,功率因数为0.85,效率为0.95,选择交流接触器、热继电器及整定值。 解:已知U=380V,P=10KW,cosφ=0.85,η=0.95 电流 此主题相关图片如下: 选择交流接触器KM=Ie×(1.3~2)=26~40(A),选CJ10-40的接触器 选择热继电器FR=Ie×(1.1~1.5)=22~25(A),选JR16-20/30热元件22A的热继电器。 热元件整定值等于电动机额定电流,整定20A 答:电动机电流为20A,选40A的交流接触器,选额定电流30A热元件22A的热继电器,整定值

接触器、热继选型

一、电动机额定电流的速算速查 1.电动机额定t电流的对表速查 在实际工作中,往往由于电动机铭牌的损坏、丢失,或缺乏实用维修电工手册等资料,不能确切知道电动机的额定电流。现在使用“电动机配用断路器、熔断器、接触器、电子型电动机保护器及导线选用速查表”,根据电动机的额定容量,即可查出所对应的额定电流。 例如一台Y132M-4型7.5kW电动机,从速查表查得其额定电流为15.4A。 2.电动机额定电流的速算口诀及经验公式 (1)运算口诀: 电动机额定电流(A):“电动机功率加倍”,即“一个千瓦两安培”。通常指常用的380V、功率因数在0.8左右的三相异步电动机,“将千瓦效加一倍” 即电动机的额定电流。 (2)经验公式: 电动机额定电流(A)=电动机容量(kw) 数×2 上述的速算口诀和经验公式的使用结果都是一致的,所算出的额定电流与电动机铭牌上的实际电 流数值非常接近,符合实用要求,例如一台Y132S1-2型5.5kW电动机,用速算口诀或经验公式算得其额定电流:5.5x2=1 1A。 二、电动机配用断路器的选择 低压断路器一般分为塑料外壳式(又称装置式)和框架式(又称万能式)两大类。断路器按用途可分为保护配电线路用、保护电动机用、保护照明线路用和漏电保护用等。 1.电动机保护用断路器选用原则 (1)长延时电流整定值等于电动机额定电流。 (2)瞬时整定电流:对于保护笼型电动机的断路器,瞬时整定电流等于(8-15)倍电动机额定电流,取决于被保护笼型电动机的型号、容量和起动条件。对于保护绕线转子电动机的断路器,瞬时整定电流等于(3—6)倍电动机额定电流,取决于被保护绕线转子电动机的型号、容量及起动条件。 (3) 6倍长延时电流整定值的可返回时间大于或等于电动机的起动时间。按起动负载的轻重,可选用返回时间1s、3s、5s、8s、15s中的某一档。 2.断路器规格型号的对表速查 例如一台Y160M-4型l1kW电动机,从速查表查得应配用DZ5—50型、热脱扣器额定电流为25A的断路器。 3.断路器脱扣器整定电流的速算口诀 ?电动机瞬动,千瓦20倍” “热脱扣器,按额定值” 上述口诀是指控制保护一台380V三相笼型电动机的断路器,其电磁脱扣瞬时动作整定电流,可按“千瓦”数的20倍”选用。对于热脱扣器,则按电动机的额定电流选择。 三、电动机配用熔断器的选择 选择熔断器类别及容量时,要根据负载的保护特性、短路电流的大小和使用场合的工作条件。大多数中小型电动机采用轻载全压或减压起动,起动电流一般为额定电流的5-7倍;电源容量较大。低压配电主变压器10O~4OkVA(包括并列运行容量),系统阻抗小,当发生短路故障时,短路电流较大;工作场合如窑、粉磨车间,通风条件差,出掌熟料及出磨水泥温度较高,致使工作环境温度较高。因此,选用熔断器的分断能力和熔体的额定电流,较之一般工业使用要适当加大一点。 1.熔体额定电流的对表速表 例如一台Yl12M一2型4kW电动机,从速量表查得应配用RL1-60型熔断器,熔体额定电

ABB微型断路器型号 文档

SH200-B 系列微型断路器型号 SH201-B6 SH201-B10 SH201-B13 SH201-B16 SH201-B20 SH201-B25 SH201-B32 SH201-B40 SH201-B50 SH201-B63 SH201-B6NA SH201-B10NA SH201-B13NA SH201-B16NA SH201-B20NA SH201-B25NA SH201-B32NA SH201-B40NA SH201-B50NA SH201-B63NA SH202-B6 SH202-B10 SH202-B13 SH202-B16 SH202-B20 SH202-B25 SH202-B32 SH202-B40 SH202-B50 SH202-B63 SH203-B6 SH203-B10 SH203-B13 SH203-B16 SH203-B20 SH203-B25 SH203-B32 SH203-B40 SH203-B50 SH203-B63 SH203-B6NA SH203-B10NA

SH203-B13NA SH203-B16NA SH203-B20NA SH203-B25NA SH203-B32NA SH203-B40NA SH203-B50NA SH203-B63NA SH204-B6 SH204-B10 SH204-B13 SH204-B16 SH204-B20 SH204-B25 SH204-B32 SH204-B40 SH204-B50 SH204-B63 SH200-C 系列微型断路器型号 SH201-C6 SH201-C8 SH201-C10 SH201-C13 SH201-C16 SH201-C20 SH201-C25 SH201-C32 SH201-C40 SH201-C50 SH201-C63 SH201-C6NA SH201-C8NA SH201-C10NA SH201-C13NA SH201-C16NA SH201-C20NA SH201-C25NA SH201-C32NA SH201-C40NA SH201-C50NA SH201-C63NA SH202-C6

ABB-电子式热继电器样本

Electronic Overload Relays New complete range up to 1250A N e w ABB

■Up to 1000V and temperature range from -25 … +70 °C ■Acc. to IEC/EN 60 947-4-1 and UL508 ■Tripping classes 10, 20, 30 ■ATEX / Ex-approved ■ Low-energy consumption ■Direct mounting to ABB contactors ■Separate mounting kits available ■Independent from ambient temperature ■Wide setting range Electronic overload relays… …are environmental friendly ■ Low power consumption saves energy ■ Materials employed can be recycled …are safe and ? exible ■ Better accuracy ■ Digital evaluation ■ Less variants …save costs ■ smaller cabinets due to less heat dissipation ■ less inventory Electronic overload relays from ABB A complete range from 0,1A …1250A E16DU E45DU E80DU E140DU E200DU Motor Starter Combinations – Overview

热继电器的合理选择与使用

电动机保护用热继电器的合理选择与使用 1.前言 热继电器是一种传统的保护电动机的电器,它具有与电动机容许过载特性相同的反时限动作特性,主要用于三相交流电动机的过载保护与断相保护。从目前的情况来看,由于没有选择与使用好热继电器而引起电动机烧毁的事故,仍然时有发生。如何合理地选择与使用热继电器,也仍是一个值得关注的问题。我们从长期的实际工作中,全面总结出了这方面的经验,供大家参考。 2.热继电器类型的选择 从结构上来说,热继电器分为两极型和三极型,其中三极型又分为带断相保护和不带断相保护两种,其型号及其意义如下。 另外,从热继电器的产品目录上还有额定电压、额定频率、额定工作制、使用温度范围、安装类别、防护等级等有关数据。 三极型的热继电器主要用于三相交流电动机的过载与断相保护。当电动机定子绕组为星形接法时,可以选用一般的三极型热继电器。因为星形接法的电动机,相电流等于线电流,无论电动机是过载运行还是断相运行,串接在主回路中的热元件都会因电流过大而使热继电器触头动作,保护电动机;如果电动机定子绕组为三角形接法,一般需要选用带断相保护的热继电器。因为三角形接法的电动机,当其引出线上发生一相断线(常见的是熔断器熔断)而缺相运行时,线电流I L等于电机相电流I P的1.5倍(如图1),不再是倍的关系,使得线电流不能正确反映出相电流,即串接在主回路中的热元件不能准确反映电机绕组是否真正过载,此时如果选用不带断相保护的热继电器,就不能很好地起到保护作用。 图1 热继电器产品目录上的其它数据,在类型选择时,考虑一下与热继电器实际使用情况相一致就行。

图2 除了上述通用型热继电器的选择外,还有些专用型热继电器。如大容量电动机用的自带专用互感器的JR20-160及以上的热继电器;重载起动的电动机用的3VA型热继电器等等。只要按它们各自适用的情况选择就行了。 值得提醒的是,有些类型的热继电器,如JR0、JR9、JRl4、JRl5、JRl6—A、B、C、D 等,国家已下令淘汰,选择时就不应再考虑了。 3.热继电器电流的选择 热继电器电流的选择包括热继电器额定电流的选择与热元件额定电流的选择两个方面。 1)热继电器的额定电流,选择时一般应等于或略大于电动机的额定电流;对于过载能力较弱且散热较困难的电动机,热继电器的额定电流为电机额定电流的70%左右。如果热继电器与电动机的使用环境温度不一致时,应对其额定电流作相应调整:当热继电器使用的环境温度高于被保护电动机的环境温度15℃以上时,应选择大一号额定电流等级的热继电器;当热继电器使用的环境温度低于被保护电动机的环境温度15℃以上时,应选择小一号额定电流等级的热继电器。 2)热元件的额定电流,选择时一般应略大于电动机的额定电流,取1.1~1.25倍,对于反复短时工作、操作频率高的电动机取上限。如果是过载能力弱的小功率电机,由于其绕组的线径小,过热能力差,应选择其额定电流等于或略小于电动机的额定电流。如果热继电器与电动机的环境温度不一致(如两者不在同一室内),热元件的额定电流同样要作调整,调整的情况与上述热继电器额定电流的调整情况基本相同。 4.热继电器质量的检查 在确定了热继电器的类型与电流等级之后,购买热继电器时要对其质量进行检查。我们对热继电器进行了过流试验,发现有些热继电器的热元件动作不符合所要求的安秒特性;有些构件的配合间隙过大,当双金属片过热弯曲时不能推动导板使动断触头打开;还有些制造工艺较差,构件上存在着毛刺或凹凸不平的现象,使得动断时运动受阻。因此购买热继电器时不仅只作外观检查,还要看其内部的构件配合是否合理,动作是否灵活,电流调节旋钮是否起作用,连接片是否焊牢等;然后进行校验,即按技术要求给热继电器的热元件通以L 2、1.5或2倍的额定电流,看其动作是否符合技术性能的要求,校验的具体方法按相关资料或产品说明书进行。

热继电器设置及操作

LRD系列热继电器安装设置实验报告 一、实验目的 1、了解LRD系列热继电器结构; 2、掌握LRD系列热继电器安装方法; 3、掌握LRD热继电器整定电流设置; 4、掌握LRD系列热继电器复位方式设置; 5、掌握LRD系列热继电器手动复位操作方法; 6、掌握LRDR热继电器STOP键特性。 二、实验设备 三、实验步骤及实验结果 1、LRD热继功能键及端子说明

LRD操作面板及接线端子如下图: 按键说明:RESET: 复位键 STOP: 手动停止 1-1.6A:电流设置 H/A:手动/自动复位端子说明:97-98 NO 95-96 NC 2/4/6 电机 LRD外观图左开盖板设置 2、LRD热继功能键及端子说明 LRD01~35C独立安装尺寸如下: LRD01~35C直接与接触器安装如下:

LRD接线柱将LRD接线柱直接安装在接触器端子 LRD09M7C ---LRD06C---LADN11安装示意图 3、LRD热继电流整定范围设置 设置LRD06C热继电流为1.3A

设置热继电流整定值1.4A 设定完成箭头指定1.4A方向4、LRD热继设置手动自动/自动复位 设置LRD06C为手动复位 设置LRD热继为手动复位设定完成按键指向H方向 5、LRD热继RESET 测试 测试LRD06C RESET键功能

设置LRD热继TEST 为T状态按蓝色键可复位T状态 6、LRD热继STOP停止键测试 手动测试LRD06C STOP键,测量97-98 96-97 输出 按红色按键测测量97-98 96-97 输出

四、实验注意事项 1、LRD热继设置是需选择合适工具; 2、安装热继时注意针脚的对齐;

接触器与热继电器选型表--实用.docx

施耐德电动机接触器与热继电器选型表 序 直接启动星三角启动备注功率断路器 号 接触器热继电器整定值接触器 *2接触器热继电器整定值 10.15C65N 3P D16A LC1-D09M7C LRD04C 0.56A 0.63~1A 20.37C65N 3P D16A LC1-D09M7C LRD06C 1~1.6A 1.1A 30.55C65N 3P D16A LC1-D09M7C LRD07C 1.5A 1.6~ 2.5A 40.75C65N 3P D16A LC1-D09M7C LRD07C 2A 1.6~2.5A 5 1.1C65N 3P D16A LC1-D09M7C LRD08C 2.5~4A 2.8A 6 1.5C65N 3P D16A LC1-D09M7C LRD08C 2.5~4A 3.7A 7 2.2C65N 3P D16A LC1-D18M7C LRD10C 4~6 5.3A 83C65N 3P D16A LC1-D18M7C LRD12C 5.5~87A 9 3.7C65N 3P D16A LC1-D18M7C LRD14C 7~108A

10 5.5C65N 3P D20A LC1-D18M7C LRD16C 9~1312A 117.5C65N 3P D25A LC1-D18M7C LRD21C 12~1815A LC1-D12M7C LC1-D09M7C LRD14C 7~107A 129C65N 3P D25A LC1-D25M7C LRD22C 17~2418A LC1-D18M7C LC1-D09M7C LRD16C 9~139A 1311C65N 3P D32A LC1-D32M7C LRD22C 17~2423A LC1-D18M7C LC1-D09M7C LRD16C 9~1311A 1415NSE100N3P 50A MA LC1-D40M7C LRD33 53C 30A LC1-D25M7C LC1-D12M7C LRD21C 12~1814A 23~32 15 18.5NSE100N3P 50A MA LC1-D25M7C LC1-D12M7C LRD22 17~2518A 1622NSE100N3P 50A MA LC1-D32M7C LC1-D18M7C LRD-32 23~3221A 1730NSE100N3P 50A MA LC1-D38M7C LC1-D18M7C LRD-35 30~3829A 1837NSE100N 3P 100A LC1-D50M7C LC1-D25M7C LRD-33 57 40A MA30~40 1945NSE100N 3P 100A LC1-D65M7C LC1-D38M7C LRD-33 59 47A MA48~65 2055NSE160N 3P 150A LC1-D65M7C LC1-D38M7C LRD-33 59 58A MA48~65 2175NSE160N 3P 150A LC1-D95M7C LC1-D50M7C LRD-33 63 78A MA63~80 2290 NSE250N 3P 220A LC1-D115M7C LC1-D65M7C LRD-43 65 99A

ABB S260微型断路器选型指南

ABB S260系列微型断路器选型指南 本文选自:工控商务网 规格:ABB S260微型断路器选型指南 意义:为了更快更精确筛选出客户要求的产品,提高客户的满意度和交易率 事件类别:产品选型(自动生成) 应用岗位:[业务业务助理技术后勤] 需备资质:[对S260微型断路器主要技术参数了解和熟悉] 品牌:ABB 系列:S260 品名:微型断路器客户类型:全部行业:全部 一. 名词解释 1.1额定电流: 电气设备的额定电流是指在基准环境温度下,在额定电压工作条件下,发热不超过长期发热允许温度时所允许长期通过的最大电流。 1.2分断能力: 断路器的分断能力是指该断路器安全切断故障电流的能力。 1.3脱扣器:s260系列微型断路器有电磁脱扣器与热脱扣器。 (1)电磁脱扣器: 只提供磁保护,也就是短路保护,其实际上是一个磁回力,当电流足够大时产生的 磁场力克服反力弹簧吸合衔铁打击牵引杆从而带动机构动作切断电路。 (2)热磁脱扣器: 由于每相电流都对应安装有一个电磁脱扣装置和一个热脱扣装置,在任何一相短路 或者过载时,相应的电磁脱扣装置或热脱扣装置均会动作。

1.4接线方式:两用端子可同时连接电缆和汇流排 当额定电流小于40A时,用0.75-25的导线 当额定电流为50、63A时,用0.75-35的导线 二. 了解信息 2.1 S260微型断路器的选型必须向客户了解以下技术参数信息: 2.2 S260微型断路器的系列:S260 S260OV S260UC S260(PT) S260(G) S260(M) S260H 2.3 S260微型断路器的额定电流(A):0.5、1、2、3、4、6、10、16、20、25、32、40、50、63 0.5~50(S260(G)脱扣特性为C) 3、6、10(S260(PT)) 2.4 S260微型断路器脱扣器形式:热磁式(S260、S260OV、S260UC S260(G)、S260(M)、S260H) 单磁式(S260(PT)、S260(M))2.5 极数:1、2、3、4 、1+NA 脱扣特性:B、C、D、K 注意事项

热继电器的结构及工作原理

热继电器是一种应用比较广泛的保护继电器,具有反时限的保护特性。 热继电器是依靠电流通过发热元件时所产生的热量,使双金属片受热弯曲而推动机构动作的一种电器。主要用于电动机的过载保护断相及电流不平衡运行的保护及其他 电气设备发热状态的控制。 热继电器的分类 热继电器的型式有许多种,其中常用的有: 双金属片式:利用双金属片用两种膨胀系数不同的金属,通常为锰镍铜板轧制成受热弯曲去推动杠杆而使触头动作。 热敏电阻式:利用电阻值随温度变化而变化的特性制成的热继电器。 易熔合金式:利用过载电流发热使易熔合金达到某一温度值时,合金熔化而使继电器动作。 作为电气设备主要是电动机过载保护用的热继电器种类虽很多,但使用得最多最普遍的还是双金属片式热继电器。它具有结构简单体积较小成本较低以及在选用适当的热元件的基础上能够获得较好的反时限保护特性等优点。目前,我国生产的热继电器都是双金属片式,它常与接触器组合成电磁启动器。它可按下述方法分类。 按极数分:有单极双极和三极。其中三极的又包括带有断相保护装置的和不带断 相保护装置的。 按复位方式分:自动复位触头断开后能自动返回到原来位置和手动复位。 按电流调节方式分:电流调节和无电流调节借更换热元件来达到改变整定电流的。 按温度补偿分:有温度补偿和无温度补偿。 按控制触点分:带常闭触点触点动作前是闭合的带常闭和常开触点。触点的结构形式有:转换触点桥式双断点等。

热继电器的结构及工作原理 热继电器是用于电动机或其它电气设备、电气线路的过载保护的保护电器。电动机在实际运行中,如拖动生产机械进行工作过程中,若机械出现不正常的情况或电路异常使电动机遇到过载,则电动机转速下降、绕组中的电流将增大,使电动机的绕组温度升高。若过载电流不大且过载的时间较短,电动机绕组不超过允许温升,这种过载是允许的。但若过载时间长,过载电流大,电动机绕组的温升就会超过允许值,使电动机绕组老化,缩短电动机的使用寿命,严重时甚至会使电动机绕组烧毁。所以,这种过载是电动机不能承受的。热继电器就是利用电流的热效应原理,在出现电动机不能承受的过载时切断电动机电路,为电动机提供过载保护的保护电器。 热继电器工作原理示意图如图1 图1 热继电器工作原理示意图 1——热元件,2——双金属片,3——导板,4——触点 热继电器的结构如图2所示。 图1 热继电器结构示意图 图中:1——电流调节凸轮,2——片簧(2a,2b),3——手动复位按钮,4——弓簧片,5——主金属片,6——外导板,7——内导板,8——常闭静触点,9——动触点,10——杠杆,11——常开静触点(复位调节螺钉),12——补偿双金属片,13——推杆,14——连杆,15——压簧

(完整版)断路器接触器热继电器如何选用

断路器、接触器、热继电器选择: 例1:22KW电机,额定电流44A,启动电流450A,那么如何选择断路器? 1、如果客户要求选用D型脱扣曲线的断路器,怎么选择? 选择iC65N-D50A/3P或iC65N-D63A/3P断路器。 因为D型脱扣曲线的断路器瞬时磁脱扣动作范围是10-14倍额定电流,即iC65N-D50A/3P的断路器瞬时磁脱扣动作电流是500-700A,大于22KW电机的启动电流450A(如选D40A断路器,那么此断路器瞬时磁脱扣动作电流是400-560A,小于22KW电机的启动电流450A)。同时此断路器的额定电流是50A,是22KW电机额定电流的1.14倍,当电机过载电流超过50A时,断路器还能起到过载保护功能,与热继电器一起双重保护电机过载。 2、如果客户要求选用C型脱扣曲线的断路器,怎么选择? 选择C120H-C100A/3P断路器。 因为C型脱扣曲线的断路器瞬时磁脱扣动作范围是5-10倍额定电流,即C120H-C100A/3P的断路器瞬时磁脱扣动作电流是500-1000A,大于22KW电机的启动电流450A(如选C80A断路器,那么此断路器瞬时磁脱扣动作电流是400-800A,小于22KW电机的启动电流450A)。但此断路器的额定电流是100A,是22KW电机额定电流的2.3倍,当电机过载电流超过40A 时,断路器不能起到过载保护功能,所以必须选用热继电器来保护电机过载。那么此断路器只能起到短路保护。 3、如果客户要求使用电动机保护断路器,怎么选择? 选择GV3-ME63,热脱扣设定范围40-63A(过载保护)。 因为此断路器专用于电动机保护,所以已经考虑了电机的启动电流问题,断路器瞬时磁脱扣动作电流一定是大于电机的启动电流。 选择此断路器不用再选择热继电器。但是此类断路器最大额定电流是80A,当大功率电机额定电流超过80A时,就得选择低压配电断路器,即选择例题中1或2问中的断路器。 GV系列断路器不分B、C、D脱扣曲线。 例题选择的是施耐德的断路器。 注1:断路器如果不要求一般选3P,不选4P。 注2:小型断路器(微断)如iC65N- DXXA小型断路器小于63A的电机都适用,但小型断路器的分断能力没有塑壳的大。 注3:电机保护用D曲线断路器理论上可以选用额定电流与电机额定电流相同的断路器,但建议还是高点,具体参见施耐德低压配电产品选型手册:SCDOC238 12-2。 例2:热继电器如何选择? 选择的热继电器的整定电流值等于电机的额定电流。即电机的额定电流正好在热继电器整定电流的范围内即可。 例3:接触器如何选择? 1)持续运行的设备。接触器按67-75%算,即100A的交流接触器,只能控制最大额定电流是67-75A以下的设备。(1.3-1.5倍额定电流) 2)间断运行的设备。接触器按80%算,即100A的交流接触器,只能控制最大额定电流是80A 以下的设备。(1.25倍额定电流) 3)反复短时工作的设备。接触器按116-120%算,100A的交流接触器,只能控制最大额定电流是116-120A以下的设备。(0.86倍额定电流) 还要考虑工作环境和接触器的结构形式。

热继电器选型及整定原则

https://www.wendangku.net/doc/2111918159.html,/viewDiary.html?ownerid=18161&id=113641 热继电器选型及整定原则 热继电器是电流通过发热元件产生热量,使检测元件受热弯曲而推动机构动作的一种继电器。由于热继电器中发热元件的发热惯性,在电路中不能做瞬时过载保护和短路保护。它主要用于电动机的过载保护、断相保护和三相电流不平衡运行的保护及其它电气设备状态的控制。 一、热继电器的工作原理及结构: 1、热继电器的作用和分类 在电力拖动控制系统中,当三相交流电动机出现长期带负荷欠电压下运行、长期过载运行以及长期单相运行等不正常情况时,会导致电动机绕组严重过热乃至烧坏。为了充分发挥电动机的过载能力,保证电动机的正常启动和运转,而当电动机一旦出现长时间过载时又能自动切断电路,从而出现了能随过载程度而改变动作时间的电器,这就是热继电器。显然,热继电器在电路中是做三相交流电动机的过载保护用。但须指出的是,由于热继电器中发热元件有热惯性,在电路中不能做瞬时过载保护,更不能做短路保护。因此,它不同于过电流继电器和熔断器。 按相数来分,热继电器有单相、两相和三相式共三种类型,每种类型按发热元件的额定电流又有不同的规格和型号。三相式热继电器常用于三相交流电动机,做过载保护。 按职能来分,三相式热继电器又有不带断相保护和带断相保护两种类型。 2、热继电器的保护特性和工作原理 1)热继电器的保护特性 因为热继电器的触点动作时间与被保护的电动机过载程度有关,所以在分析热继电器工作原理之前,首先要明确电动机在不超过允许温升的条件下,电动机的过载电流与电动机通电时间的关系。这种关系称为电动机的过载特性。 当电动机运行中出现过载电流时,必将引起绕组发热。根据热平衡关系,不难得出在允许温升条件下,电动机通电时间与其过载电流的平方成反比的结论。根据这个结论,可以得出电动机的过载特性,具有反时限特性,如图l中曲线1所示。 图1:电动机的过载特性和热继电器的保护特性及其配合 为了适应电动机的过载特性而又起到过载保护作用,要求热继电器也应具有如同电动机过载特性那样的反时限特性。为此,在热继电器中必须具有电阻发热元件,利用过载电流通过电阻发热元件产生的热效应使感测元件动作,从而带动触点动作来完成保护作用。热继电器中通过的过载电流与热继电器触点的动作时间关系,称为热继电器的保护特性,如图1中曲

ABB继电器的分类

对于ABB在此先给大家做一个简单的介绍:ABB主要产品包括控制产品、自动转换开关电器、断路器类产品、开关类产品、线路保护产品、开关插座、智能建筑控制系统、电网质量产品、箱壳类产品和低压配电系统。ABB由两个历史100多年的国际性企业瑞典的阿西亚公司(ASEA)和瑞士的布朗勃法瑞公司(BBC Brown Boveri) 在1988年合并而成。两公司分别成立于1883年和1891年。下面主要为大家带来的是ABB继电器的相关分类,一起来看看吧~ 1.电磁继电器 在输入电路内电流的作用下,由机械部件的相对运动产生预定响应的一种继电器。它包括直流电磁继电器、交流电磁继电器、磁保持继电器、极化继电器、舌簧继电器,节能功率继电器。 (1)直流电磁继电器:输入电路中的控制电流为直流的电磁继电器。 (2)交流电磁继电器:输入电路中的控制电流为交流的电磁继电器。 (3)磁保持继电器:将磁钢引入磁回路,继电器线圈断电后,继电器的衔铁仍能保持在线圈通电时的状态,具有两个稳定状态。 (4)极化继电器:状态改变取决于输入激励量极性的一种直流继电器。 (5)舌簧继电器:利用密封在管内,具有触点簧片和衔铁磁路双重作用的舌簧的动作来

开、闭或转换线路的继电器。 (6)节能功率继电器:输入电路中的控制电流为交流的电磁继电器,但它的电流大(一般30-100A),体积小,节电功能。 2.固态继电器 输入、输出功能由电子元件完成而无机械运动部件的一种继电器。 3.时间继电器 当加上或除去输入信号时,输出部分需延时或限时到规定的时间才闭合或断开其被控线路的继电器。 4.温度继电器 当外界温度达到规定值时而动作的继电器. 5.风速继电器 当风的速度达到一定值时,被控电路将接通或断开。 6.加速度继电器 当运动物体的加速度达到规定值时,被控电路将接通或断开。 7.其它类型的继电器 如果您想了解更多有关ABB继电器方面的资讯,推荐您联系南京首科机电咨询详情。

热继电器选用计算

热继电器选用计算 (一)一般方法 保护长期工作或间断长期工作的电动机时热继电器的选用计算方法是: (1)一般情况下,按电动机的额定电流选取,使热继电器的整定值为(0.95—1.05)I N,I N为电动机的额定工作电流),或选取整定范围的中值为电动机的额定工作电流。 (2)保护Y—Δ起动电动机,当热继电器的3个热元件分别串接在Δ联结的各相绕组内,热继电器的整定电流应按电动机的额定电流整定。 (3)保护并联电容器的补偿型电动机,只有有功电流流经热继电器,热继电器的整定电流可按下式近似进行整定: 式中 It——热继电器整定电流.A; I N——电动机额定电流,A; cosφ——电动机功率因数。 (二)作图法 用于保护反复短时工作电动机的热继电器,每小时允许的操作次数,与电动机的起动过渡过程、通电持续率及负载电流等因素有关。复合加热的热继电器,在反复短时工作下每小时允许的操作次数,可按图1所示的速查曲线选用。 间接加热的热继电器每小时允许的操作次数,比按图1速查曲线选用的次数稍高。当电动机每小时的操作次数较高时,可选用带速饱和电流互感器的热继电器。图3—1及其应用方法是根据下列公式绘制和确定的。反复短时工作允许操作频率为 式中 f。——允许操作频率,次/h; Kc——计算系数,Kc=0.8—0.9; ts——电动机起动时间,s: Ks——电动机起动电流倍数(即其起动电流与其额定电流之比); K L——电动机负载电流倍数(即其负载电流与其额定电流之比): K1——热继电器额定整定电流与电动机额定电流之比: TD——通电持续率。

(注:本资料素材和资料部分来自网络,仅供参考。请预览后才下载,期待您的好评与关注!)

ABB微型断路器型号大全

ABB微型断路器型号大全 ABB微型断路器结构设计独特,其核心在于采用由专业生产线生产的,集触头、过载保护、短路保护和自由脱扣机构于一体的金属机芯,与其它机构靠外壳定位配合的产品相比,此设计保证了产品分断的可靠,不受外界因素影响,而锤式动鐵芯快速电磁动作系统和其它技术保证了产品的限流性。 厦门ABB低压产品授权经销商 厦门狄豪自动化公司为您提供 ABB微型断路器型号大全 S250S-C系列微型断路器 1P S251S-C1 S251S-C2 S251S-C3 S251S-C4 S251S-C6 S251S-C10 S251S-C16 S251S-C20 S251S-C25 S251S-C32 S251S-C40 S251S-C50 S251S-C63 1P+NA S251SNA-C10 S251SNA-C16 S251SNA-C20 S251SNA-C25 S251SNA-C32 S251SNA-C40 S251SNA-C50 S251SNA-C63 2P S252S-C1 S252S-C2 S252S-C3 S252S-C4 S252S-C6 S252S-C10 S252S-C16 S252S-C20 S252S-C25 S252S-C32 S252S-C40 S252S-C50 S252S-C63

S253S-C6 S253S-C10 S253S-C16 S253S-C20 S253S-C25 S253S-C32 S253S-C40 S253S-C50 S253S-C63 4P S254S-C1 S254S-C2 S254S-C3 S254S-C4 S254S-C6 S254S-C10 S254S-C16 S254S-C20 S254S-C25 S254S-C32 S254S-C40 S254S-C50 S254S-C63 S250S-D系列1P S251S-D1 S251S-D4 S251S-D6 S251S-D10 S251S-D16 S251S-D20 S251S-D25 S251S-D32 S251S-D40 S251S-D50 S251S-D63 2P S252S-D1 S252S-D4 S252S-D6 S252S-D10 S252S-D16 S252S-D20

热继电器的选择和计算

热继电器的选择和计算 WTD standardization office【WTD 5AB- WTDK 08- WTD 2C】

看一下本题就知了, 有一台三相异步电动机额定电压为380伏,容量为10千瓦,功率因数为,效率为,选择交流接触器、热继电器及整定值。 解:已知U=380V,P=10KW,cosφ=,η=? 电流I=P/(√3*U*cosφ*η)=10/***≈20A ? 选择交流接触器KM=Ie×(~2)=26~40(A),选CJ10-40的接触器 选择热继电器FR=Ie×(~)=22~25(A),选JR16-20/30热元件22A的热继电器。 热元件整定值等于电动机额定电流,整定20A 答:电动机电流为20A,选40A的交流接触器,选额定电流30A热元件22A的热继电器,整定值20A。 I=P/(√3*U*cosφ*η)=10/***≈20A 、有一台三相异步电动机额定电压为380伏,容量为14千瓦,功率因数为,效率为,计算电动机电流。 ?? 解:已知U=380(V),cosφ=,η=,P=14(KW) 电流 此主题相关图片如下: 答:电动机电流29安培。 2、有一台三相异步电动机额定电压为380伏,容量为10千瓦,功率因数为,效率为,选择交流接触器、热继电器及整定值。

解:已知U=380V,P=10KW,cosφ=,η= 电流 此主题相关图片如下: 选择交流接触器KM=Ie×(~2)=26~40(A),选CJ10-40的接触器 ?? 选择热继电器FR=Ie×(~)=22~25(A),选JR16-20/30热元件22A的热继电器。 ?? 热元件整定值等于电动机额定电流,整定20A ?? 答:电动机电流为20A,选40A的交流接触器,选额定电流30A热元件22A的热继电器,整定值20A。 3、一台三相交流异步电动机,其型号规格为Y112M-4,4KW;额定电压380V、△接法;cosφ=;η=.计算该电动机的额定电流和保护用的熔体规格和热继电器的动作电流整定值是多少? 解:电动机的额定电流为 此主题相关图片如下: 保护用的熔体规格为 Ir=(~)I=(~)×=~ ?热继电器的电流整定值 ???? IZ=×I=×= 答:该电动机的额定电流为,保护用的熔体规格可选20A,热继电器的保护整定值应调在 4、一台三相异步电动机额定电压380V;额定电流28A;cosφ=;η=.计算电动机的功率是多少?交流接触器应选多大规格?保护用熔断器的熔体应选多大? 解:电动机功率为P=3UeIe cosφη=3××28××≈14KW 保护用的熔体规格为 ? Ir=(~)Ie=(~)×28=42~70A 交流接触器的电流规格为 ? Icj=(~2)Ie=(~2)×28=~56A

热继电器型号大全

热继电器型号 热继电器得额定电流应大于电动机额定电流。然后根据该额定电流来选择热继电器得型号。热继电器得热元件得额定电流应略大于电动机额定电流。当电动机启动电流为其额定电流得6倍及启动时间不超过5S时,热无件得整定电流调节到等于电动机得额定电流;当电动机得启动时间较长、拖动冲击性负载或不允许停车时,热元件整定电流调节到电动机额定电流得1、1-1、15倍。 型号机型额定 TK-E02A-C热过载继电器0、1-0、15A TK-E02B-C热过载继电器0、13-0、2A TK-E02C-C热过载继电器0、15-0、24A TK-E02D-C热过载继电器0、2-0、3A TK-E02E-C热过载继电器0、24-0、36A TK-E02F-C热过载继电器0、3-0、45A TK-E02G-C热过载继电器0、36-0、54A TK-E02H-C热过载继电器0、48-0、72A TK-E02J-C热过载继电器0、64-0、96A TK-E02K-C热过载继电器0、8-1、2A TK-E02L-C热过载继电器0、95-1、45A TK-E02M-C热过载继电器1、4-2、2A TK-E02N-C热过载继电器1、7-2、6A TK-E02P-C热过载继电器2、2-3、4A TK-E02R-C热过载继电器2、8-4、2A TK-E02S-C热过载继电器4-6A TK-E02T-C热过载继电器5-8A TK-E02U-C热过载继电器6-9A TK-E02V-C热过载继电器7-11A TK-E02W-C热过载继电器9-13A TK-E02X-C热过载继电器12-18A TK-E02Q-C热过载继电器16-22A TK-E02Y-C热过载继电器20-25A TK-E2S-C热过载继电器4-6A TK-E2U-C热过载继电器5-8A TK-E2V-C热过载继电器6-9A TK-E2W-C热过载继电器7-11A TK-E2X-C热过载继电器9-13A TK-E2B-C热过载继电器12-18A TK-E2E-C热过载继电器24-36A TK-E2I-C热过载继电器32-42A TK-E2H-C热过载继电器40-50A TK-E3V-C热过载继电器7-11A TK-E3W-C热过载继电器9-13A TK-E3X-C热过载继电器12-18A TK-E3B-C热过载继电器18-26A TK-E3E-C热过载继电器24-36A

热继电器的选择和计算

热继电器的选择和计算 Document serial number【UU89WT-UU98YT-UU8CB-UUUT-UUT108】

看一下本题就知了, 有一台三相异步电动机额定电压为380伏,容量为10千瓦,功率因数为,效率为,选择交流接触器、热继电器及整定值。解:已知U=380V,P=10K W,c o sφ=,η=?电流I=P/(√3*U*c o sφ*η)=10/***≈20A ? 选择交流接触器KM=Ie×(~2)=26~40(A),选CJ10-40的接触器 选择热继电器FR=Ie×(~)=22~25(A),选JR16-20/30热元件22A的热继电器。 热元件整定值等于电动机额定电流,整定20A 答:电动机电流为20A,选40A的交流接触器,选额定电流30A热元件22A的热继电器,整定值20A。 I=P/(√3*U*cosφ*η)=10/***≈20A 、有一台三相异步电动机额定电压为380伏,容量为14千瓦,功率因数为,效率为,计算电动机电流。 解:已知U=380(V),cosφ=,η=,P=14(KW) 电流 此主题相关图片如下:

答:电动机电流29安培。 2、有一台三相异步电动机额定电压为380伏,容量为10千瓦,功率因数为,效率为,选择交流接触器、热继电器及整定值。 解:已知U=380V,P=10KW,cosφ=,η= 电流 此主题相关图片如下: 选择交流接触器KM=Ie×(~2)=26~40(A),选CJ10-40的接触器 选择热继电器FR=Ie×(~)=22~25(A),选JR16-20/30热元件22A 的热继电器。 热元件整定值等于电动机额定电流,整定20A 答:电动机电流为20A,选40A的交流接触器,选额定电流30A热元件22A 的热继电器,整定值20A。 3、一台三相交流异步电动机,其型号规格为Y112M-4,4KW;额定电压380 V、△接法;cosφ=;η=.计算该电动机的额定电流和保护用的熔体规格和热继电器的动作电流整定值是多少 解:电动机的额定电流为 此主题相关图片如下: 保护用的熔体规格为 Ir=(~)I=(~)×=~ 热继电器的电流整定值