DigitAx User Guide Issue code: dgxu4

11-1

11List of Parameters

11.1 Variable parameters

Note

R–W = Read–write parameter RO = Read-only parameter

Selection of Pr0, Pr1, Pr2, and Pr3 is controlled by Pr17, which receives its coding from the values of Pr18, Pr19 and Pr20, as selected by b16 and

–3000 to 3000 RPM when Pr99 = 200 to 3000

If the DC bus voltage falls below the value of Pr5,the Drive stops automatically.(See Auto Stop function )Permits the user to apply a correction to an offset in the analog speed reference which would cause slow rotation of the motor when zero speed is intended.resonance in the mechanical transmission, or by high inertia of the driven load.

Slope in milliseconds per 1000 RPM.

DigitAx User Guide Issue code: dgxu4

11-2

Slope in milliseconds per 1000 RPM.

Value of the resolver phase correction . Refer to Resolver Phasing in Chapter 10 Getting Started.+24V = 1

The indications are as follows:

Normal control

Range: 0 to 3

Select the required digital reference.

Position control

Range: 0 to 255Resolution: 1

When Pr21 = 1, sequential selector Pr19 is enabled.This parameter can be set only at the control keypad, not by using serial communications . Available values are as follows:

300, 600 1200, 2400, 4800, 9600, 19200The host computer must be set at the same Baud rate as the Drive.

DigitAx User Guide Issue code: dgxu411-3

Selects the source parameter for terminal B8.

DigitAx User Guide Issue code: dgxu4

11-4

from the Drive, as a percentage of I pk .

I 2

t region.

DBE140 to DBE750: 20% to 50%DBE1100S to DBE2200: 20% to 67%

Defines a window either side of the value

programmed in Pr27 within which it is assumed that the motor shaft is correctly orientated when Speed in RPM adopted during shaft orientation. See Pr27.Enter the value for the motor.Refer also to Pr57, b42 and b96.

If the motor exceeds this limit, an over-speed trip occurs . See b87.When Pr68 = 0, pulses per revolution = 256When Pr68 = 1, pulses per revolution = 512When Pr68 = 2, pulses per revolution = 1024

When Pr68 = 3, pulses per revolution = 2048

Note

When Pr68 is set at 3, the maximum permissible speed is 3000 RPM Pr70. For each resulting pulse, the motor shaft will rotate Pr70/16384 part of a revolution. Refer also When the Drive is set up to operate in position control with a frequency input signal, Pr71 is used to add integral gain to eliminate steady-state

position error.

DigitAx User Guide Issue code: dgxu4

11-5

Displays a value proportional to the power dissipated in the braking circuit . When Pr81reaches 100, parameter b95 is set at 1.

Shows the shaft position at all times.Displays the cause of the last trip . Pr98 is cleared when the Drive is reset by setting b03 at 1. When Pr98 is interrogated using Serial Communications, a number representing the trip is transmitted . The numbers are as follows:

11.2 Bit parameters

Set at 1 to enable the security code to be changed Refer to terminal B14.

DigitAx User Guide Issue code: dgxu4

11-6

and reset the last alarm store . Display will show rSt during reset . Refer to Pr98.

Note

Set b2 at 0 or apply 0V to terminal B14 to disable the Drive before resetting the

alarm.b4 = 0 indicates the Drive is disabled (by b2 = 0, an

alarm, or the Drive enable signal being removed

from terminal B14).

b4 = 1 indicates the Drive is enabled.

application . The d isplay shows dEf while default values are loaded. Related to b1 and b99

.Refer to b8.

When b6 = 0, the reference is the speed loop output.

When b6 = 1, analog or digital current reference selected.

Change speed with or without ramps.When b7 = 0, ramps are disabled.When b7 = 1, ramps are enabled.

When b8 = 0, analog torque reference is selected.When b8 = 1, digital torque reference is selected (see Pr8).Indicates the logic level present on terminal B6.

When the input at terminal B6 is 0V selection is by software only . Refer to b18.

When the input at terminal B6 is +24V, and b53 = 1,

the stop function is to stop in position.

If the input at terminal B6 is +24V, b53 = 0, and b22 = 0, b9 = 0, the stop function is to hold zero speed without ramps.When the input at terminal B6 is +24V, b53 = 0, and Indicates the logic input state at terminal B14.

When the logic state at B14 is 0, b10 is 0 and the

Drive is not enabled.

When the logic state at B14 is 1, b10 is 1 and the Drive is enabled depending on the setting of b2.Selects the current limit.

When b12 is set at 0, refer to b13.

When b12 is set at 1, the output signal represents the motor current (16V pk-pk ≡ I peak ).

When b12 = 0, b13 is used to select the signal source.When b13 is set at 0, clamped current demand (Pr40) is selected (±10V ≡ ±100%).

When b13 is set at 1, post-ramp speed reference is selected (5V ≡ 6000RPM request).

When b17 is set at 0 and b14 is set at 0, pulse-train

input is selected (terminal C7).

When b17 is set at 0 and b14 is set at 1, analog

speed reference (±10V) is selected (terminals B9

and B10).

Selects the function of terminals B4 and B5.When b16 is set at 0, terminals B4 and B5 are used to control the application of an offset count to the 32-bit buffer.

When b16 is set at 1, terminals B4 and B5 are used

Selects analog speed reference at terminals B9 and B10 or digital reference.

When b17 is set at 0, analog speed reference is selected.

When b17 is set at 1, digital speed reference is selected; b14 has no effect.

Selects the stop function without an input applied to terminal B6.

When b18 = 0, the stop function is controlled by applying a signal to terminal B6. Refer to b9.

When b18 = 1, and b53 = 1, the stop function is to stop to position with ramp and hold.When b18 = 1, b53 = 0, and b22 = 0, the stop

function is to stop without ramps and hold.

When b18 = 1, b53 = 0, and b22 = 1, the stop

function is to stop with ramps and hold.Refer also to b7, b9, b23.When b21 is set at 0, BCC is disabled.

When b21 is set at 1, BCC enabled.See Chapter 13 Serial Communications .Note

Stopping with orientation always uses ramps irrespective of the setting of b22 (see b53).When b23 is set at 0, without ramps is selected.When b23 is set at 1, with ramps is selected.When b33 is set at 0, at least one alarm is active.When b33 is set at 1, no alarm is active.

The status of this parameter is produced as a logic signal on terminal B15.

Indicates the direction of rotation when seen at the drive shaft end of the motor.

b53 = 0, b41 = 0 indicates motor not at zero speed.b53 = 1, b41

= 0 indicates shaft not orientated.b53 = 0, b41 = 1 indicates motor at zero speed.b53 = 1, b41 = 1 indicates shaft is oriented . See Pr27.

b42 = 0 indicates motor not at speed — motor speed is outside the range defined by Pr56 and Pr57.

b42 = 1 indicates motor At speed — motor speed is within the range defined by Pr56 and Pr57.

Indicates whether the speed loop is operating linearly or is in saturation.

b48 = 0 indicates the speed loop is in linear operation.

b48 = 1 indicates the speed loop is saturated.

When b49 is set at 0, resolver phasing is inactive.When b49 is set at 1, resolver phasing is enabled.

returns to rdY or the speed value after 8 seconds without a key stroke.

When b50 is set at 1, the display continues to show the value of the last parameter to have been selected.When b51 is set at 1, 7 data bits with even parity is selected.

Note

This parameter can be adjusted only at the keypad, not by using serial communications.When b52 is set at 1, Terminal mode is selected.When b53 is set at 0, stop and hold is selected.When b53 is set at 1, stop, orientate, and hold is selected.See Pr27.b55 = 0 indicates no external trip.b55 = 1 indicates external trip active.

When b56 is set at 0, external trip is disabled.When b56 is set at 1, external trip is enabled.

b81 = 1 indicates a digital output is short-circuit to 0V.

(<400V).See Pr4.b85 = 0 indicates heat-sink temperature below permitted maximum.

b85 = 1 indicates heat-sink temperature above permitted maximum.b86 = 0 indicates no fault.

b86 = 1 indicates a fault present.

b87 = 0 indicates the speed is within limits.

b87 = 1 indicates the speed has exceeded the limit Set b88 at 0 for zero speed when terminal B6 is at +24V.Set b88 at 1 for zero speed when terminal B6 is at 0V.

b91 = 0 indicates heat-sink temperature <75°C (167°F).

b95 = 0 indicates Normal.

b95 = 1 indicates Overload.

DigitAx User Guide Issue code: dgxu4

11-10

Defines the type of signal given by the At-speed status parameter b42.

When b96 is set at 0, absolute is selected.When b96 is set at 1, relative is selected.

When b96 is set at 1 (relative) the At-speed status held in b42 is related to the Speed Reference input,so that b42 = 1 (At speed) when the motor speed is between the two limits, as follows:

Greater than [Speed reference] – Pr56Less than [Speed reference] + Pr57

When b96 is set at 0 (Absolute) the At-speed

status held in b42 responds to the absolute values set in Pr56 and Pr57, so that b42 = 1 (At speed)when the motor speed speed is between the two limits, as follows:

Greater than Pr56Less than Pr57

Refer also to Pr56, Pr57 and b42.

Saves new parameter values in the EEPROM . The display shows SAVE while parameters are being saved . b99 is related to b1 and b5.When b99 is set at 0, no saving occurs.When b99 is set at 1, parameters are saved.