CONTENTS
POWER CABLES
35kV XLPE Insulation Power Cable of 35kV or lower..................................................................................6 0.6/1kV 0.6/1kV PVC Insulation Power Cable.................................................................................................21 10kV Rated Voltage 10kV or Lower Aerial Insulation Cable.......................................................................26 A.A.C.& A.C.S.R.................................................................................................................................31 Ship Power Cable With PVC lnsulation & Sheath..............................................................................34 Power Cable with Silica Rubber Insulation & Sheath.........................................................................35
ELECTRIC EQUIPMENTS INSTALLATION WIRES CABLES
( ) PVC Insulation Cable(Wire)...............................................................................................................38 General-purpose Soft Rubber Sheath Cable.....................................................................................40 PVC Insulation & Sheath Control Cable.............................................................................................42 Ship Control Cable with PVC Insulation & Sheath.............................................................................52
SPECIAL CABLES
0.6/1kV 0.6/1kV Soft Power Cable with PVC Insulation..................................................................................54 Metallic Shielded Power Cable..........................................................................................................56 Cable for Nuclear Power Station........................................................................................................60 Power Cable with PVC Insulation & Nylon Sheath.............................................................................65

Compensational Wire & Cable for Thermocouple..............................................................................67 Heat-resistant Control Cable with Fluoroplastics Insulation & PVC Sheath......................................75 ( ) Heat-resistant (Control) Cable with Fluoroplastics Insulation & Sheath............................................82 Intrinsic Safety Type Decentralized Control System Signal Cable for Explosion-proof Circuit ........88 Control Cable with XLPE Insulation & PVC Sheath..........................................................................93 Low Smoke & Halogen Flame-retardant Control Cable....................................................................97 Low Smoke, Halogen-free & Flame-retardant Control Cable...........................................................99 Fire-resistant Cable.........................................................................................................................101 ( ) Computer (Shielded) Cable.............................................................................................................103 Intrinsic Safety Type Signal Control Cable......................................................................................111 Signal Cable ...................................................................................................................................115 Instrument Cable.............................................................................................................................118 Ship RF Cable.................................................................................................................................119 Cell PE Insulation Coaxial RF Cable for Cable Distribution System...............................................122 Guiding Cable with PE Insulation ...................................................................................................124 Local Telecommunication Cable.....................................................................................................126 RF Cable with Solid Core & PE Insulation......................................................................................127 ( ) Irradiated XLPE Insulation Cable (Wire).........................................................................................130 70 ( ) 70 Soft Cable (Wire) for Motor Coil Connection..........................................................................144 90 ( ) 90 Soft Cable (Wire) for Motor Coil Connection..........................................................................146 180 ( ) 180 Soft Cable (Wire) for Motor Winding Connection.................................................................148

Fire-resistant Cable with Oxygen-separation Layer ...............................................................149 Heat-resistant Silica Rubber Control Cable............................................................................151 Self-Thermal Control Heating Cable.......................................................................................159 AF-125 AF-125 Fluoroplastics Installation Wire..................................................................................163 AF-170 AF-170 Fluoroplastics Installation Wire..................................................................................164 AF-200.AF-260 AF-200.AF-260 Fluoroplastics Installation Wire.....................................................................165 ( ) Butadiene PVC Compound Cable (Wire)...............................................................................166 Load-bearing Propection Cable..............................................................................................168


35kV
XLPE Insulation Power Cable of 35kV or lower
50Hz 35kV
The cable is used to transmit power on the power transmission and distribution line of A.C.50Hz,rated voltage 35kV or lower .In comparison with PVC insulation cable ,it boasts not only excellent electric character,mechanical character,heat and aging-resistant character,environmental stress-resistant character and chemical corrosion-resistant character,but simple structure,light weight ,no restriction by laying drop,and high temperature allowance for longterm working(90 )as well.
Executive standard : as section extrusion insulated power cable & accessories rated voltage 1kV(Um=1.2kV)-35kV (Um=40.5kV) in GB12706.1-12706.4-2002 or IEC60502-1997
90
: GB/T12706.1~12706.4-2002 (Um=1.2kV) 35kV(Um=40.5kV) IEC60502-1997
1kV
Working Conditions: 1. 2. ( 20(d+D) D 5 5% d 90 250 15(d+D) 5% ) 0
1.Environment temperatue should be no lower than0 for laying the cable, otherwise the cable should be preheated. 2.The minimum cable bending radius is stipulated as follows: single core :20(d+D) 5%;3cores: 15(d+D) 5%; (D for actual cable outer diameter,d for that of conductor ) The highest rated temperature of the conductor is 90 , no higher than 250 in time of short circuit ( lasting no longer than 5 seconds)
Type ,Description &Application Occasion Type
Cu YJV Al YJLV
Description
Application Occasion
XLPE insulation PVC sheath power cable To be laid indoors, in tunnel, cable furrow, and pipe, or under soft soil, the cable couldn,t bear mechanical force outside.
YJY
YJLY
XLPE insulation PE sheath power cable
YJV22
YJLV22 XLPE insulation steel tape armored PVC sheath power cable To be laid underground , the cable could bear mechanical force outside, but it couldn t bear XLPE insulation steel tape armored PVC sheath power cable great pulling force.
YJV32 YJLV32 ZRRemarks:We may produce the cable with steel wire armor structure as user?s demand, for example YJV32, YJLV32 types,etc. Code prefix “ZR-” should be added to the original code in ordering on flame-retardant cable.
YJV23
YJLV23
6

Rated Voltage,Nominal Cross-section Area &Core Numbers:
Type Cu Al Core No 1 3 2 3+1 3+2 4+1 5 1 3 2 3+1 3+2 4+1 5 0.6/1 1.5~400 1.5~300 1.5~150 4~400 50~240 1.5~35 4~400 2.5~300 4~150 4~300 50~240 2.5~35 3.6/6 25~500 25~300 25~500 25~300 6/6 6/10 25~500 25~300 25~500 25~300 -
Rated Voltage 8.7/10 8.7/15 25~500 25~300 25~500 25~300 -
(kV) 18/20 18/30 50~500 50~300 50~500 50~300 21/35 50~500 50~300 50~500 50~300 26/35 50~500 50~300 50~500 50~300 -
12/20 35~500 35~300 35~500 35~300 -
YJV YJY
YJLV YJLY
YJV22 YJV23
YJLV22 YJLV23
Power Cables
Structural Size & Major Technical Parameters:
0.6/1kV 0.6/1kV single core,XLPE insulation ,PVC sheath power cable
YJV
YJLV
single core
Cable Nominal Cross Insulation Sheath Outer Section Area Thickness Thickness Diameter mm 2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300 400 mm 0.7 0.7 0.7 0.7 0.7 0.7 0.9 0.9 1.0 1.1 1.1 1.2 1.4 1.6 1.7 1.8 2.0 mm 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 2.0 2.0 2.0 2.5 2.5 mm 5.8 6.2 6.7 7.2 8.0 8.9 10.4 11.5 13.0 14.0 16.4 17.8 20.6 22.5 24.9 27.3 34.1
Approximate Cable Weight Cu Kg/Km 53 68 87 110 115 220 345 424 555 770 1040 1290 1590 1944 2510 3076 3642 Al Kg/Km -53 64 73 95 120 190 207 245 336 455 550 650 804 1021 1238 1455
D.C.Conductor Resistance Cu /Km 12.1 7.41 4.61 3.08 1.83 1.15 0.727 0.524 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 0.0601 0.0470 Al /Km 12.1 7.41 4.61 3.08 1.91 1.20 0.868 0.641 0.443 0.320 0.253 0.206 0.164 0.125 0.100 0.0778
Current-loading Capacity Testing Voltage kV 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 in the air Cu A 22 30 39 50 70 94 124 154 191 241 297 346 399 465 552 652 777 Al A ----53 85 99 118 150 185 231 268 308 365 427 502 590 to be laid underground Cu A 40 54 71 91 123 158 201 244 292 355 433 496 554 624 726 819 934 Al A ----95 156 159 191 224 283 338 387 430 490 568 639 701
7

YJV YJLV
2
2 cores
0.6/1kV 0.6/1kV 2 cores,XLPE insulation ,PVC sheath power cable
Cable Nominal Cross Insulation Sheath Outer Section Area Thickness Thickness Diameter mm 2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 mm 0.7 0.7 0.7 0.7 0.7 0.7 0.9 0.9 1.0 1.1 1.1 1.2 1.4 mm 1.8 1.8 1.8 1.8 1.8 1.8 1.8 1.8 1.8 1.8 1.8 1.9 2.0 mm 9.4 10.2 11.2 12.2 15.2 17.3 20.4 22.4 20.2 22.5 25.4 28.3 31.3
Approximate Cable Weight Cu kg/km 103 131 168 216 328 461 659 868 1116 1514 2017 2526 3139 Al kg/km -99 118 142 189 245 329 413 489 644 830 1026 1286
D.C.Conductor Resistance Testing Voltage Cu ?/km 12.1 7.41 4.61 3.08 1.83 1.15 0.727 0.524 0.387 0.268 0.193 0.153 0.124 Al ?/km -12.1 7.41 4.61 3.08 1.91 1.20 0.868 0.641 0.443 0.320 0.253 0.206 kV 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5
Current-loading Capacity in the air Cu A 25 33 44 55 77 101 140 173 218 264 331 379 433 Al A ----59 78 106 130 150 191 256 293 336 to be laid underground Cu A 36 47 63 78 105 136 189 217 258 315 377 422 482 Al A ----80 104 139 169 198 246 293 334 372
YJV YJLV
3
3 cores
Approximate Cable Weight Al kg/km -140 175 210 260 340 470 600 730 970 1240 1540 1940 2248 2723 3218
0.6/1kV 0.6/1kV 3 cores,XLPE insulation ,PVC sheath power cable
Nominal Insulation Sheath Cross Thickness Thickness Section Area mm 2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300 mm 0.7 0.7 0.7 0.7 0.7 0.7 0.9 0.9 1.0 1.1 1.1 1.2 1.4 1.6 1.7 1.8 mm 1.5 1.5 1.5 1.5 1.5 1.5 2.0 2.0 2.0 2.0 2.0 2.5 2.5 2.5 2.5 3.0
Cable Outer Diameter Cu mm kg/km 9.4 145 10.7 185 11.8 250 12.9 320 14.6 450 16.5 640 20.8 940 23.2 1260 26.4 1670 29.9 2280 33.3 3020 37.8 3795 41.7 4750 44.6 5654 50.1 7243 55.6 8832
D.C.Conductor Resistance Cu /Km 12.1 7.41 4.61 3.08 1.83 1.15 0.727 0.524 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 0.0601 Al /Km -12.1 7.41 4.61 3.08 1.91 1.20 0.868 0.641 0.443 0.320 0.253 0.206 0.164 0.125 0.100
Current-loading Capacity Testing Voltage kV 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 in the air Cu A 21 28 37 46 63 84 109 132 159 195 237 273 310 355 416 473 Al A ----48 65 85 102 123 152 184 213 241 277 326 372 to be laid underground Cu A 25 33 44 54 73 94 120 144 169 205 245 278 309 347 399 446 Al A ----56 72 93 111 131 159 190 216 240 271 312 351
8

YJV YJLV
4
4 cores
Approximate Cable Weight
0.6/1kV 0.6/1kV 4 cores,XLPE insulation ,PVC sheath power cable
Nominal Cable Insulation Sheath Cross Thickness Thickness Outer Section Area Diameter mm 2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300 mm 0.7 0.7 0.7 0.7 0.7 0.7 0.9 0.9 1.0 1.1 1.1 1.2 1.4 1.6 1.7 1.8 mm 1.5 1.5 1.5 1.5 1.5 2.0 2.0 2.0 2.0 2.0 2.5 2.5 3.0 3.0 3.0 3.5 mm 10.6 11.5 12.8 14.0 15.9 19.1 22.7 25.4 29.0 32.9 37.7 41.6 47.6 50.6 56.4 62.2
D.C.Conductor Resistance Cu /Km 12.1 7.41 4.61 3.08 1.83 1.15 0.727 0.524 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 0.0601 Al /Km -12.1 7.41 4.61 3.08 1.91 1.20 0.868 0.641 0.443 0.320 0.253 0.206 0.164 0.125 0.100
Current-loading Capacity Testing Voltage kV 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 in the air Cu A 21 28 37 46 63 84 109 132 159 195 237 273 310 355 416 473 Al A ----48 63 85 102 123 152 184 213 241 277 326 372 to be laid underground Cu Al A A 25 -33 -44 -54 -73 56 94 72 120 93 144 111 169 131 205 159 245 190 278 216 309 240 347 271 399 312 446 351
Cu kg/km 139 150 253 337 501 778 1160 1554 2148 2928 3954 4925 6238 7562 9660 11758
Al kg/km 84 107 151 198 291 455 696 905 1235 1640 2294 2865 3618 4395 5603 6585
Power Cables
YJV YJLV
3+1
3+1 cores
0.6/1kV (3+1) 0.6/1kV (3+1) cores,XLPE insulation ,PVC sheath power cable
Nominal Cross Section Area mm 2 4 6 10 16 25 35 50 70 95 120 150 185 240 300
Insulation Sheath Thickness Thickness mm 0.7 0.7 0.7 0.7 0.9 0.9 1.0 1.1 1.1 1.2 1.4 1.6 1.7 1.8 mm 1.5 1.5 1.5 2.0 2.0 2.0 2.0 2.0 2.5 2.5 3.0 3.0 3.0 3.5
Cable Outer Diameter mm 12.5 13.7 15.4 17.5 21.8 23.8 27.4 31.0 34.8 39.7 42.9 47.4 52.7 58.0
Approximate Cable Weight Cu kg/km 236 316 460 679 1065 1368 1901 2585 3718 4443 5326 6628 8501 10320 Al kg/km 180 210 380 375 586 821 1141 1463 2231 2665 3190 3842 5001 5679
D.C.Conductor Resistance Cu /Km 4.61 3.08 1.83 1.15 0.727 0.524 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 0.0601 Al /Km 7.41 4.61 3.08 1.91 1.20 0.868 0.641 0.443 0.320 0.253 0.206 0.164 0.125 0.100 Testing Voltage kV 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5
Current-loading Capacity in the air Cu A 37 46 63 84 109 132 159 195 237 273 310 355 416 473 Al A --48 64 85 102 123 152 184 213 241 277 326 372 to be laid underground Cu Al A A 44 -54 -73 56 94 72 120 93 144 111 169 131 205 159 245 190 278 216 309 240 347 271 399 312 446 351
9

YJV YJLV
3+2
3+2 cores
0.6/1kV (3+2) 0.6/1kV 5(3+2) cores,XLPE insulation ,PVC sheath power cable
Cable Nominal Cross Insulation Sheath Section Area Thickness Thickness Outer Diameter mm 2 50 70 95 120 150 185 240 mm 2 25 35 50 70 70 95 120 mm 1.0 1.1 1.1 1.2 1.4 1.6 1.7 mm 0.9 0.9 1.0 1.1 1.1 1.1 1.2 mm 1.8 2.0 2.1 2.3 2.4 2.5 2.7 mm 28.2 32.8 37.0 41.4 44.5 49.2 54.7
Approximate Cable Weight Cu kg/km 2268 3116 4176 5375 6305 7889 10051 Al kg/km 1003 1345 1741 2213 2574 3178 3980
D.C.Conductor Resistance Cu /Km 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 Al /Km 0.641 0.443 0.320 0.253 0.206 0.164 0.125 Testing Voltage kV 3.5 3.5 3.5 3.5 3.5 3.5 3.5
Current-loading Capacity in the air Cu A 159 195 237 273 310 355 416 Al A 123 152 184 213 241 277 326 to be laid underground Cu A 169 205 245 278 309 347 399 Al A 131 159 190 216 240 271 312
YJV YJLV
4+1
4+1 cores
0.6/1kV (4+1) 0.6/1kV 5(4+1) cores,XLPE insulation ,PVC sheath power cable Current-loading Capacity Testing Voltage kV 3.5 3.5 3.5 3.5 3.5 3.5 3.5 in the air Cu A 159 195 237 273 310 355 416 Al A 123 152 184 213 241 277 326 to be laid underground Cu A 169 205 245 278 309 347 399 Al A 131 159 190 216 240 271 312
Nominal Cross Insulation Sheath Cable Section Area Thickness Thickness Outer Diameter mm 2 50 70 95 120 150 185 240 mm 2 25 35 50 70 70 95 120 mm 1.0 1.1 1.1 1.2 1.4 1.6 1.7 mm 0.9 0.9 1.0 1.1 1.1 1.1 1.2 mm 1.8 2.0 2.1 2.3 2.4 2.5 2.7 mm 28.2 32.8 37.0 41.4 44.5 49.2 54.7
Approximate Cable Weight Cu kg/km 2268 3116 4176 5375 6305 7889 10051 Al kg/km 1003 1345 1741 2213 2574 3178 3980
D.C.Conductor Resistance Cu /Km 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 Al /Km 0.641 0.443 0.320 0.253 0.206 0.164 0.125
YJV YJLV
5
5 cores
0.6/1kV 5 0.6/1kV 5cores,XLPE insulation ,PVC sheath power cable Current-loading Capacity Testing Voltage kV 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 in the air Cu A 21 28 37 46 63 84 109 132 Al A ----48 63 85 102 to be laid underground Cu A 25 33 44 54 73 94 120 144 Al A ----56 72 93 111
Approximate Nominal Cable Weight Cable Insulation Sheath Cross Thickness Thickness Outer Section Area Diameter Cu Al mm 2 mm mm mm kg/km kg/km 0.7 1.5 9.4 145 -1.5 2.5 0.7 1.5 10.7 185 140 4 0.7 1.5 11.8 250 175 6 0.7 1.5 12.9 320 210 0.7 1.5 14.6 450 260 10 0.7 1.5 16.5 640 340 16 25 0.9 2.0 20.8 940 470 35 0.9 2.0 23.2 1260 600
D.C.Conductor Resistance Cu /Km 12.1 7.41 4.61 3.08 1.83 1.15 0.727 0.524 Al /Km -12.1 7.41 4.61 3.08 1.91 1.20 0.868
10

0.6/1kV 0.6/1kV 2 cores,XLPE insulation ,steel tape armored,PVC sheath power cable
YJV22
YJLV22
2
2 cores
Approximate Cable Weight Cu kg/km 325 387 538 700 939 1174 1393 2132 2694 3276 3997 Al kg/km 228 254 310 372 468 558 610 906 1108 1330 1637 D.C.Conductor Resistance Cu /km 4.61 3.08 1.83 1.15 0.727 0.524 0.387 0.268 0.193 0.153 0.124 Al /km 7.41 4.61 3.08 1.91 1.20 0.868 0.641 0.443 0.320 0.253 0.206 Testing Voltage kV 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 Current-loading Capacity in the air Cu A 49 61 82 119 146 176 212 257 265 367 414 Al A --64 105 111 135 162 200 205 284 320 to be laid underground Cu Al A A 59 -73 -97 74 126 123 162 127 195 152 230 198 281 219 339 262 386 300 433 336
Nominal Cross Section Area mm 2 4 6 10 16 25 35 50 70 95 120 150
Cable Insulation Sheath Thickness Thickness Outer Diameter mm 0.7 0.7 0.7 0.7 0.9 0.9 1.0 1.1 1.1 1.2 1.4 mm 1.8 1.8 1.8 1.8 1.8 1.8 1.8 1.8 1.9 2.0 2.1 mm 14.4 15.4 18.4 20.5 23.6 25.6 23.4 26.2 29.5 33.0 36.1
Power Cables
0.6/1kV 0.6/1kV 3 cores,XLPE insulation ,steel tape armored,PVC sheath power cable
YJV22
YJLV22
3
3 cores
Approximate Cable Weight Cu kg/km 273 321 390 471 622 1005 1371 1724 2247 3023 3825 4642 5767 6892 8017 9142 Al kg/km -208 254 144 404 650 891 1121 1573 1965 2486 3017 3749 4480 5215 5946 D.C.Conductor Resistance Cu /km 12.1 7.41 4.61 3.08 1.83 1.15 0.727 0.524 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 0.0601 Al /km -12.1 7.41 4.61 3.08 1.91 1.20 0.868 0.641 0.443 0.320 0.253 0.206 0.164 0.125 0.100 Testing Voltage kV 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 Current-loading Capacity in the air Cu A 21 28 37 47 63 84 110 134 161 197 239 275 314 354 414 470 Al A ----49 64 85 104 124 153 185 214 242 277 325 370 to be laid underground Cu Al A A 25 -33 -43 -54 -71 55 92 70 118 92 141 110 167 129 203 158 242 188 274 213 305 237 341 267 392 308 438 344
Nominal Cross Section Area mm 2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300
Cable Insulation Sheath Thickness Thickness Outer Diameter mm 0.7 0.7 0.7 0.7 0.7 0.7 0.9 0.9 1.0 1.1 1.1 1.2 1.4 1.6 1.7 1.8 mm 1.5 1.5 1.5 1.5 1.5 2.0 2.0 2.0 2.0 2.5 2.5 2.5 3.0 3.0 3.0 3.5 mm 13.0 13.9 15.0 16.1 17.8 21.5 24.8 27.2 30.4 35.3 38.7 42.2 47.5 52.8 58.1 63.4
11

0.6/1kV 0.6/1kV 4 cores,XLPE insulation ,steel tape armored,PVC sheath power cable
YJV22
YJLV22
4
4 cores
Approximate Cable Weight Cu kg/km 307 367 454 557 791 1210 1672 2127 2802 3785 4829 6033 7356 8679 10002 12325 Al kg/km 209 250 309 379 538 823 1134 1446 1906 2574 3284 4103 5002 5902 6802 8381 D.C.Conductor Resistance Testing Voltage kV 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 Current-loading Capacity in the air Cu A 21 28 37 47 63 84 110 134 161 197 239 275 314 354 414 470 Al A ----49 64 85 104 124 153 185 214 242 277 325 370 to be laid underground Cu Al A A 25 -33 -43 -54 -71 55 92 70 118 92 141 110 167 129 203 158 242 188 274 213 305 237 341 267 392 308 438 344
Nominal Cross Section Area mm 2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300
Insulation Sheath Thickness Thickness mm 0.7 0.7 0.7 0.7 0.7 0.7 0.9 0.9 1.0 1.1 1.1 1.2 1.4 1.6 1.7 1.8 mm 1.5 1.5 1.5 1.5 1.5 2.0 2.0 2.0 2.0 2.5 2.5 2.5 3.0 3.0 3.0 3.5
Cable Outer Diameter mm 13.8 14.7 16.0 17.2 20.1 23.1 26.7 29.4 33.0 38.3 42.1 47.4 52.2 57.0 61.8 66.6
Cu ?/km 12.1 7.41 4.61 3.08 1.83 1.15 0.727 0.524 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 0.0601
Al ?/km -12.1 7.41 4.61 3.08 1.91 1.20 0.868 0.641 0.443 0.320 0.253 0.206 0.164 0.125 0.100
0.6/1kV (3+1) 0.6/1kV (3+1) cores,XLPE insulation, steel tape armored,PVC sheath power cable
YJV22 YJLV22
3+1
3+1cores
Approximate Cable Weight Cu kg/km --443 513 741 1135 1556 1896 2518 3393 4349 5365 6468 7571 8674 9777 Al kg/km --288 372 519 795 1089 1327 1763 2375 3044 3756 4528 5299 6072 6844 D.C.Conductor Resistance Cu ?/km --4.61 3.08 1.83 1.15 0.727 0.524 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 0.0601 Al ?/km --7.41 4.61 3.08 1.91 1.20 0.868 0.641 0.443 0.320 0.253 0.206 0.164 0.125 0.100 Testing Voltage kV --3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 Current-loading Capacity in the air Cu A 21 28 37 47 63 84 110 134 161 197 239 275 314 354 414 470 Al A ----49 64 85 104 124 153 185 214 242 277 325 370 to be laid underground Cu Al A A 25 -33 -43 -54 -71 55 92 70 118 92 141 110 167 129 203 158 242 188 274 213 305 237 341 267 392 308 438 344
Nominal Cross Section Area mm 2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300
Cable Insulation Sheath Thickness Thickness Outer Diameter mm --0.7 0.7 0.7 0.7 0.9 0.9 1.0 1.1 1.1 1.2 1.4 1.6 1.7 1.8 mm --1.5 1.5 1.5 2.0 2.0 2.0 2.0 2.5 2.5 2.5 3.0 3.0 3.0 3.5 mm --15.7 15.9 19.6 22.5 25.8 27.8 31.4 36.4 40.2 44.1 48.7 53.5 58.9 63.5
12

0.6/1kV (3+2) 0.6/1kV 5(3+2) cores,XLPE insulation ,steel tape armored,PVC sheath power cable
YJV22
YJLV22
3+2
3+2 cores
Approximate Cable Weight Cu kg/km 2876 4150 5345 6696 7746 9499 11878 Al kg/km 1611 2379 2910 3534 4015 4788 5807 D.C.Conductor Resistance Testing Voltage Cu /km 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 Al /km 0.641 0.443 0.320 0.253 0.206 0.164 0.125 kV 3.5 3.5 3.5 3.5 3.5 3.5 3.5 Current-loading Capacity in the air Cu A 161 197 239 275 314 354 414 Al A 124 153 185 214 242 277 325 to be laid underground Cu A 167 203 242 274 305 341 392 Al A 129 158 188 213 237 267 308
Nominal Cross Section Area mm 2 50 70 95 150 120 185 240
Insulation Sheath Thickness Thickness mm 0.9 0.9 1.0 1.1 1.1 1.1 1.2 mm 2.0 2.2 2.3 2.5 2.6 2.7 2.9
Cable Outer Diameter mm 32.7 38.3 42.6 47.2 50.5 55.3 61.2
mm 2 mm 25 1.0 35 1.1 50 1.1 70 1.2 70 1.4 95 1.6 120 1.7
(4+1) 0.6/1kV 0.6/1kV 5(4+1) cores,XLPE insulation ,steel tape armored,PVC sheath power cable
Power Cables
YJV22
YJLV22
4+1
4+1 cores
Approximate Cable Weight Cu kg/km 3153 4554 5896 7248 8620 10520 13199 Al kg/km 1730 2562 3176 3770 4383 5240 6369 D.C.Conductor Resistance Cu /km 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 Al /km 0.641 0.443 0.320 0.253 0.206 0.164 0.125 Testing Voltage kV 3.5 3.5 3.5 3.5 3.5 3.5 3.5 Current-loading Capacity in the air Cu A 161 197 239 275 314 354 414 Al A 124 153 185 214 242 277 325 to be laid underground Cu Al A A 167 129 203 158 242 188 274 213 305 237 341 267 392 308
Nominal Cross Section Area mm 2 50 70 95 120 150 185 240 mm 2 25 35 50 70 70 95 120
Insulation Sheath Cable Thickness Thickness Outer Diameter mm 1.0 1.1 1.1 1.2 1.4 1.6 1.7 mm 0.9 0.9 1.0 1.1 1.1 1.1 1.2 mm 2.0 2.2 2.4 2.5 2.6 2.8 3.0 mm 33.9 39.9 44.7 48.7 52.7 57.9 64.2
0.6/1kV 0.6/1kV 5 cores,XLPE insulation ,steel tape armored,PVC sheath power cable
YJV22
YJLV22
5
5 cores
Approximate Cable Weight Cu kg/km 252 359 472 713 1053 1583 2134 Al kg/km ---392 539 780 1009 D.C.Conductor Resistance Testing Voltage Cu /km 7.41 4.61 3.08 1.83 1.15 0.727 0.524 Al /km 12.1 7.41 4.61 3.08 1.91 1.20 0.868 kV 3.5 3.5 3.5 3.5 3.5 3.5 3.5 Current-loading Capacity in the air Cu A 28 37 47 63 84 110 134 Al A ---49 64 85 104 to be laid underground Cu Al A A 33 -43 -54 -71 55 92 70 118 92 141 110
Nominal Cross Section Area mm 2 2.5 4 6 10 16 25 35
Cable Insulation Sheath Outer Thickness Thickness Diameter mm 0.7 0.7 0.7 0.7 0.7 0.9 0.9 mm 1.8 1.8 1.8 1.8 1.8 1.9 2.1 mm 17.0 18.3 19.7 23.5 26.0 31.0 34.3
13

YJV YJLV (
single core)
3.6/6kV 3.6/6kV single core, XLPE insudation,PVC sheath power cable
20
Nominal Cable Insulation Sheath Cross Section Thickness Thickness Outer Diameter Area mm 2 25 35 50 70 95 120 150 185 240 300 400 mm 2.5 2.5 2.5 2.5 2.5 2.5 2.5 2.5 2.8 2.8 3.0 mm 1.8 1.8 1.8 1.8 1.8 1.8 1.8 1.9 1.9 2.0 2.1 mm 19.0 20.0 22.0 23.0 25.0 26.0 28.0 30.0 32.0 35.0 39.0 Approximate Cable Weight D.C.Conductor Resistanceat 20 Cu /km 0.727 0.524 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 0.0601 0.0470 Al /km 1.200 0.868 0.641 0.443 0.320 0.253 0.206 0.164 0.125 0.100 0.0778 Current-loading Capacity Current-loading Capacity to be laid Conductor in the air underground Cu A 165 205 245 305 370 430 490 560 665 765 890 Al A 130 155 190 235 290 335 380 435 515 595 695 Cu A 160 190 225 275 330 375 426 480 555 630 725 Al A 120 145 175 215 255 290 330 370 435 490 565 Cu kA 3.69 5.15 7.31 10.2 13.8 17.4 21.7 26.7 34.6 43.1 57.4 Al kA 2.42 3.37 4.79 6.68 9.68 11.4 14.2 17.5 22.6 28.2 37.6
Shielding Layer
Cu kg/km 617 736 903 1129 1407 1676 1990 2358 2935 3648 4675
Al kg/km 459 515 587 687 807 918 1043 1190 1420 1754 2149
Cu Tape
kA 1.075 1.074 1.072 1.070 1.069 1.068 1.067 1.064 1.241 1.239 1.240
YJV YJLV (
single core)
6/6kV,6/10kV 6/6kV,6/10kV single core,XLPE insulation ,PVC sheath power cable
20
Nominal Cable Insulation Sheath Cross Section Thickness Thickness Outer Diameter Cu Area mm 2 mm mm mm kg/km 3.4 1.8 21.0 25 685 35 3.4 1.8 22.0 807 3.4 1.8 23.0 50 977 70 3.4 1.8 25.0 1207 95 3.4 1.8 27.0 1489 3.4 1.8 28.0 1762 120 3.4 1.9 30.0 150 2080 3.4 2.0 32.0 185 2453 240 3.4 2.1 34.0 3100 300 3.4 2.2 36.0 3723 400 3.4 2.3 40.0 4728 Approximate Cable Weight Al kg/km 527 586 661 765 889 1004 1133 1285 1584 1829 2203 D.C.Conductor Resistanceat 20 Cu /km 0.727 0.524 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 0.0601 0.0470 Al /km 1.200 0.868 0.641 0.443 0.320 0.253 0.206 0.164 0.125 0.100 0.0778 Current-loading Capacity
Current-loading Capacity
Shielding Layer
to be laid in the air underground Conductor Cu A 165 205 245 305 370 430 490 560 665 765 890 Al A 130 155 190 235 290 335 380 435 515 595 695 Cu A 160 190 225 275 330 375 426 480 555 630 725 Al A 120 145 175 215 255 290 330 370 435 490 565 Cu kA 3.69 5.15 7.31 10.2 13.8 17.4 21.7 26.7 34.6 43.1 57.4 Al kA 2.42 3.37 4.79 6.68 9.68 11.4 14.2 17.5 22.6 28.2 37.6
Cu Tape
kA 1.083 1.082 1.080 1.079 1.077 1.077 1.076 1.251 1.250 1.246 1.245
14

YJV YJLV (
single core)
8.7/10kV,8.7/15kV 8.7/10kV,8.7/15kV single core,XLPE insulation ,PVC sheath power cable
20
Nominal Cable Cross Insulation Sheath Section Thickness Thickness Outer Diameter Cu Area 2 mm mm mm mm kg/km 25 4.5 1.8 23.0 775 35 4.5 1.8 4.0 889 50 4.5 1.8 26.0 1073 70 4.5 1.8 27.0 1308 95 4.5 1.8 29.0 1596 120 4.5 1.9 30.0 1874 150 4.5 1.9 32.0 2194 185 4.5 2.0 34.0 2649 240 4.5 2.1 36.0 3234 300 4.5 2.1 38.0 3865 400 4.5 2.3 42.0 4830 Approximate Cable Weight D.C.Conductor Resistanceat 20 Cu /km 0.727 0.524 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 0.0601 0.0470 Al /km 1.200 0.868 0.641 0.443 0.320 0.253 0.206 0.164 0.125 0.100 0.0778 Current-loading Capacity
Current-loading Capacity
Shielding Layer
to be laid in the air underground Conductor Cu A 165 205 245 305 370 430 490 560 665 765 890 Al A 130 155 190 235 290 335 380 435 515 595 695 Cu A 160 190 225 275 330 375 426 480 555 630 725 Al A 120 145 175 215 255 290 330 370 435 490 565 Cu kA 3.69 5.15 7.31 10.2 13.8 17.4 21.7 26.7 34.6 43.1 57.4 Al kA 2.42 3.37 4.79 6.68 9.03 11.4 14.2 17.5 22.6 28.2 37.6
Al kg/km 617 678 757 866 996 1116 1250 1481 1719 1971 2354
Cu Tape
kA 1.094 1.092 1.091 1.090 1.086 1.266 1.265 1.264 1.262 1.261 1.256
Power Cables
YJV YJLV (
single core)
12/20kV 12/20kV single core,XLPE insulation ,PVC sheath power cable
20
Nominal Cable Cross Insulation Sheath Section Thickness Thickness Outer Diameter Area mm 2 mm mm mm ---25 35 5.5 1.8 26.0 5.5 1.8 28.0 50 5.5 1.9 29.0 70 5.5 1.9 31.0 95 5.5 2.0 33.0 120 150 5.5 2.0 34.0 185 5.5 2.1 36.0 240 5.5 2.1 38.0 300 5.5 2.2 41.0 400 5.5 2.3 44.0 Approximate Cable Weight Cu kg/km -990 1166 1407 1700 1982 2338 2771 3363 4000 5024 Al kg/km -769 851 965 1100 1224 1436 1603 1848 2106 2498 D.C.Conductor Resistanceat 20 Cu /km -0.524 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 0.0601 0.0470 Al /km -0.868 0.641 0.443 0.320 0.253 0.206 0.164 0.125 0.100 0.0778 Current-loading Capacity
Current-loading Capacity
Shielding Layer
to be laid in the air underground Conductor Cu A -205 245 305 370 430 490 560 665 765 890 Al A -155 190 235 290 335 380 435 515 595 695 Cu A -190 225 275 330 375 426 480 555 630 725 Al A -145 175 215 255 290 330 370 435 490 565 Cu kA -5.51 7.31 10.2 13.8 17.4 21.7 26.7 34.6 43.1 57.4 Al kA -3.37 4.79 6.68 9.03 11.4 14.2 17.5 22.6 28.2 37.6
Cu Tape
kA -1.096 1.095 1.091 1.272 1.271 1.270 1.267 1.266 1.265 1.260
15

YJV YJLV (
single core)
18/20kV 18/30/kV 18/20kV 18/30/kV single core,XLPE insulation,PVC sheath power cable
20
Nominal Cable Cross Insulation Sheath Section Thickness Thickness Outer Diameter Cu Area 2 mm mm mm mm kg/km 50 8.0 2.0 33.0 1426 70 8.0 2.0 35.0 1752 95 2.1 36.0 8.0 2062 120 8.0 2.1 38.0 2358 150 8.0 2.2 40.0 2699 185 8.0 2.2 41.0 3100 240 8.0 2.3 44.0 3709 300 8.0 2.4 46.0 4364 400 8.0 2.5 49.0 5517 Approximate Cable Weight Al kg/km 1110 1310 1462 1600 1752 1932 2194 2470 2991 D.C.Conductor Resistanceat 20 Cu /km 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 0.0601 0.0470 Al /km 0.641 0.443 0.320 0.253 0.206 0.164 0.125 0.100 0.0778 Current-loading Capacity
Current-loading Capacity
Shielding Layer
to be laid in the air underground Conductor Cu A 245 305 370 425 485 555 650 745 870 Al A 190 235 285 330 375 430 505 580 680 Cu A 225 275 330 375 420 425 555 630 720 Al A 175 215 255 290 325 370 430 490 565 Cu kA 7.31 10.2 13.8 17.4 21.7 26.7 34.6 43.1 57.4 Al kA 4.79 6.68 9.03 11.4 14.2 17.5 22.6 28.2 37.6
Cu Tape
kA 1.284 1.281 1.280 1.279 1.278 1.275 1.274 1.271 1.270
YJV YJLV (
single core)
21/35kV 21/35kV single core,XLPE insulation,PVC sheath power cable
20
Nominal Cable Cross Insulation Sheath Section Thickness Thickness Outer Diameter Area 2 mm mm mm mm 50 9.3 2.1 36.0 70 2.1 37.0 9.3 95 9.3 2.2 39.0 120 2.2 41.0 9.3 150 9.3 2.3 42.0 185 9.3 2.3 44.0 240 9.3 2.4 46.0 300 9.3 2.5 49.0 400 9.3 2.6 52.0 Approximate Cable Weight D.C.Conductor Resistanceat 20 Cu /km 0.4936 0.3420 0.2465 0.1956 0.1588 0.1271 0.0971 0.0788 0.615 Al /km 0.8220 0.5681 0.4105 0.3247 0.2645 0.2107 0.1608 0.1289 0.1010 Current-loading Capacity Current-loading Capacity to be laid in the air underground Conductor Cu A 245 305 370 425 485 555 650 745 870 Al A 190 235 285 330 375 430 505 580 680 Cu A 225 275 330 375 420 425 555 630 720 Al A 175 215 255 290 325 370 430 490 565 Cu kA 7.31 10.2 13.8 17.4 21.7 26.7 34.6 43.1 57.4 Al kA 4.79 6.68 9.03 11.4 14.2 17.5 22.6 28.2 37.6
Shielding Layer
Cu kg/km 1652 1913 2229 2531 2878 3285 3904 4568 5737
Al kg/km 1336 1471 1630 1773 1931 2117 2388 2674 3212
Cu Tape
kA 1.286 1.285 1.234 1.280 1.279 1.279 1.276 1.275 1.272
YJV YJLV (
single core)
26/35kV 26/35kV single core,XLPE insulation,PVC sheath power cable
20
Nominal Cable Cross Insulation Sheath Section Thickness Thickness Outer Diameter Area Cu mm 2 mm mm mm kg/km 50 10.5 2.2 38.0 1803 70 10.5 2.2 40.0 2070 95 10.5 2.3 42.0 2393 120 2.3 43.0 10.5 2699 150 10.5 2.4 45.0 3052 185 10.5 2.4 47.0 3465 240 10.5 2.5 49.0 4092 300 10.5 2.6 51.0 4867 400 10.5 2.7 55.0 5949 Approximate Cable Weight D.C.Conductor Resistanceat 20 Cu /km 0.4936 0.3420 0.2465 0.1956 0.1588 0.1271 0.0971 0.0788 0.615 Al /km 0.8220 0.5681 0.4105 0.3247 0.2645 0.2107 0.1608 0.1289 0.1010 Current-loading Capacity Current-loading Capacity to be laid in the air underground Conductor Cu A 245 305 370 425 485 555 650 745 870 Al A 190 235 285 330 375 430 505 580 680 Cu A 225 275 330 375 420 425 555 630 720 Al A 175 215 255 290 325 370 430 490 565 Cu kA 7.31 10.2 13.8 17.4 21.7 26.7 34.6 43.1 57.4 Al kA 4.79 6.68 9.03 11.4 14.2 17.5 22.6 28.2 37.6
Shielding Layer
Al kg/km 1487 1628 1793 1942 2104 2294 2577 2982 3424 16
Cu Tape
kA 1.288 1.286 1.283 1.282 1.282 1.279 1.278 1.277 1.274

YJV YJLV (3
3 cores) 20
Approximate Cable Weight
3.6/6kV 3.6/6kV 3 cores,XLPE insulation,PVC sheath power cable
Current-loading Capacity
Nominal Insulation Sheath Cable Cross Outer Section Thickness Thickness Diameter Area mm 2 25 35 50 70 95 120 150 185 240 300 mm 2.5 2.5 2.5 2.5 2.5 2.5 2.5 2.5 2.6 2.8 mm 2.1 2.2 2.3 2.4 2.5 2.6 2.8 2.9 3.0 3.1 mm 39.0 41.0 44.0 48.0 52.0 55.0 59.0 62.0 68.0 74.0
20 D.C.Conductor Resistance
Short Circuit Current
Conductor
Shielding Layer
in the air Cu kg/km 1888 2287 2783 3551 4483 5338 6279 7565 9304 11371 Al kg/km 1414 1624 1836 2225 2683 3065 3438 4061 4858 5689 Cu /km 0.727 0.524 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 0.0601 Cu /km 1.200 0.868 0.641 0.443 0.320 0.253 0.206 0.164 0.125 0.100 Cu A 120 140 165 210 255 290 330 375 435 495 Al A 90 110 130 165 200 225 255 295 345 390
to be laid underground Cu A 125 155 180 220 265 300 340 380 435 485 Al A 100 120 140 170 210 235 360 300 345 390
Cu kA 3.69 5.15 7.31 10.2 13.8 17.4 21.7 26.7 34.6 43.1
Al kA 2.42 3.37 4.79 6.68 9.03 11.4 14.2 17.5 22.6 28.2
Cu Tape
kA 2.958 2.958 2.958 2.958 2.958 2.958 2.958 2.958 3.031 3.031
Power Cables
YJV YJLV (3
3 cores)
Approximate Cable Weight
6/6kV, 6/10kV 6/6kV, 6/10kV 3 cores,XLPE insulation,PVC sheath power cable
20
Nominal Cross Insulation Sheath Cable Section Thickness Thickness Outer Diameter Area mm 2 25 35 50 70 95 120 150 185 240 300 mm 3.4 3.4 3.4 3.4 3.4 3.4 3.4 3.4 3.4 3.4 mm 2.3 2.3 2.4 2.6 2.7 2.8 2.9 3.0 3.2 3.3 mm 43.0 45.0 48.0 52.0 56.0 59.0 63.0 66.0 72.0 77.0 D.C.Conductor Resistanceat 20
Current-loading Capacity in the air to be laid underground Cu A 125 155 180 220 265 300 340 380 435 485 Al A 100 120 140 170 210 235 360 300 345 390
Current-loading Capacity Conductor
Shielding Layer
Cu kg/km 2132 2491 3091 3884 4778 5595 6732 7954 7929 11855
Al kg/km 1658 1828 2144 2558 2978 3322 3891 4450 5183 6173
Cu /km 0.727 0.524 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 0.0601
Cu /km 1.200 0.868 0.641 0.443 0.320 0.253 0.206 0.164 0.125 0.100
Cu A 120 140 165 210 255 290 330 375 435 495
Al A 90 110 130 165 200 225 255 295 345 390
Cu kA 3.69 5.15 7.31 10.2 13.8 17.4 21.7 26.7 34.6 43.1
Al kA 2.42 3.37 4.79 6.68 9.03 11.4 14.2 17.5 22.6 28.2
Cu Tape
kA 2.958 2.958 2.958 2.958 2.958 2.958 2.958 2.958 3.031 3.031
17

YJV YJLV (3
3 cores)
8.7/10kV, 8.7/15kV 8.7/10kV,8.7/15kV 3 cores,XLPE insulation,PVC sheath power cable
20
Nominal Insulation Sheath Cable Cross Section Thickness Thickness Outer Diameter Area mm 2 mm mm mm 25 4.5 2.4 48.0 35 4.5 2.5 50.0 50 4.5 2.6 53.0 4.5 2.7 57.0 70 95 4.5 2.8 61.0 120 4.5 2.9 64.0 150 4.5 3.1 68.0 185 4.5 3.2 72.0 240 4.5 3.3 77.0 300 4.5 3.5 82.0 Approximate Cable Weight 20 D.C.Conductor Resistance Cu /km 0.727 0.524 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 0.0601 Al /km 1.200 0.868 0.641 0.443 0.320 0.253 0.206 0.164 0.125 0.100
Current-loading Capacity
Short Circuit Current
Conductor
Shielding Layer
in the air Cu kg/km 2486 2963 3481 4036 5147 6116 7187 8379 10391 12336 Al kg/km 2102 2300 2534 2911 3348 3843 4346 4874 5845 6653 Cu A 120 140 165 210 355 290 330 375 435 495 Al A 90 110 130 165 200 225 255 295 345 390
to be laid underground Cu A 125 155 180 220 265 300 340 380 435 485 Al A 100 120 140 170 210 235 360 300 345 390
Cu kA 3.69 5.15 7.31 10.2 13.8 17.4 21.7 26.7 34.6 43.1
Al kA 2.42 3.37 4.79 6.68 9.03 11.4 14.2 17.5 22.6 28.2
Cu Tape
kA 2.958 2.958 2.958 2.958 2.958 2.958 3.031 3.031 3.031 3.031
YJV YJLV (3
3 cores) 20
Approximate Cable Weight
12/20kV 12/20kV 3 cores,XLPE insulation,PVC sheath power cable 20 D.C.Conductor Resistance Cu /km -0.524 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 0.0601 Cu /km -0.868 0.641 0.443 0.320 0.253 0.206 0.164 0.125 0.100
Current-loading Capacity
Short Circuit Current
Conductor
Shielding Layer
Nominal Insulation Sheath Cable Cross Section Thickness Thickness Outer Diameter Area mm 2 25 35 50 70 95 120 150 185 240 300 mm -5.5 5.5 5.5 5.5 5.5 5.5 5.5 5.5 5.5 mm -2.7 2.8 2.9 3.0 3.1 3.2 3.3 3.5 3.6 mm -55.0 58.0 62.0 66.0 69.0 72.0 76.0 81.0 86.0
in the air Cu kg/km -3233 3810 4710 5693 6546 7580 8836 10830 12795 Al kg/km -2570 2862 3384 3894 4272 4739 5331 6284 7113 Cu A -140 165 210 355 290 330 375 435 495 Al A -110 130 165 200 225 255 295 345 390
to be laid underground Cu A -155 180 220 265 300 340 380 435 485 Al A -120 140 170 210 235 360 300 345 390
Cu kA -5.15 7.31 10.2 13.8 17.4 21.7 26.7 34.6 43.1
Al kA -3.37 4.79 6.68 9.03 11.4 14.2 17.5 22.6 28.2
Cu Tape
kA -2.958 2.958 2.958 3.031 3.031 3.031 3.031 3.031 3.031
YJV22
YJLV22(3
3.6/6kV 3.6/6kV 3 cores,XLPE insulation, steel tape armored,PVC sheath power cable 3 cores)
20
Nominal Insulation Sheath Cable Cross Section Thickness Thickness Outer Diameter Area mm 2 25 35 50 70 95 120 150 185 240 300 mm 2.5 2.5 2.5 2.5 2.5 2.5 2.5 2.5 2.5 2.5 mm 2.3 2.3 2.4 2.5 2.7 2.8 2.9 3.0 3.2 3.5 mm 44.0 46.0 49.0 53.0 57.0 60.0 64.0 68.0 74.0 81.0 Approximate Cable Weight 20 D.C.Conductor Resistance Cu /km 0.727 0.524 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 0.0601 Cu /km 12.00 0.868 0.641 0.443 0.320 0.253 0.206 0.164 0.125 0.100
Current-loading Capacity
Short Circuit Current
Conductor
Shielding Layer
in the air Cu kg/km 2829 3301 3855 4845 5797 6735 7924 9216 11236 14437 Al kg/km 2355 2638 3908 3519 3998 4462 5083 5712 6690 8755
3~5mm
to be laid underground Cu A 125 155 180 220 265 300 340 380 435 485 Al A 100 120 140 170 210 235 360 300 345 390
Cu A 120 140 165 210 355 290 330 375 435 495
Al A 90 110 130 165 200 225 255 295 345 390
Cu kA 3.69 5.15 7.31 10.2 13.8 17.4 21.7 26.7 34.6 43.1
Al kA 2.42 3.37 4.79 6.68 9.03 11.4 14.2 17.5 22.6 28.2
Cu Tape
kA 2.958 2.958 2.958 2.958 2.958 2.958 2.958 2.958 30.31 3.031
Remarks: The approximate outer diameter of the cable with thin steel wire armor should be larger by 3~5mm on the basis.
18

6/6kV 6/10kV 6/6kV 6/10kV 3 cores,XLPE insulation, steel tape armored,PVC sheath power cable
YJV22 YJLV22(3
3 cores) 20
Approximate Cable Weight 20 D.C.Conductor Resistance Cu /km 0.727 0.524 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 0.0601 Al /km 1.200 0.868 0.641 0.443 0.320 0.253 0.206 0.164 0.125 0.100
Current-loading Capacity
Short Circuit Current
Conductor
Shielding Layer
Nominal Cable Cross Insulation Sheath Section Thickness Thickness Outer Diameter Area mm 2 25 35 50 70 95 120 150 185 240 300 mm 3.4 3.4 3.4 3.4 3.4 3.4 3.4 3.4 3.4 3.4 mm 2.4 2.5 2.6 2.7 2.9 3.0 3.1 3.2 3.3 3.4 mm 48.0 50.0 53.0 57.0 62.0 65.0 69.0 72.0 78.0 84.0
in the air Cu kg/km 3190 3731 4396 5198 6350 7257 8383 9741 11854 14861 Al kg/km 2716 3086 3449 3872 4551 4984 5542 6237 7039 9178
3~5mm
to be laid underground Cu A 125 155 180 220 265 300 340 380 435 485 Al A 100 120 140 170 210 235 360 300 345 390
Cu A 120 140 165 210 255 290 330 375 435 495
Al A 90 110 130 165 200 225 255 295 345 390
Cu kA 3.69 5.15 7.31 10.2 13.8 17.4 21.7 26.7 34.6 43.1
Al kA 2.42 3.37 4.79 6.68 9.03 11.4 14.2 17.5 22.6 28.2
Cu Tape
kA 2.958 2.958 2.958 2.958 2.958 2.958 2.958 2.958 3.031 3.031
Remarks: The approximate outer diameter of the cable with thin steel wire
Power Cables
armor should be larger by 3~5mm on the basis.
8.7/10kV 8.7/15kV 8.7/10kV 8.7/15kV 3 cores,XLPE insulation, steel tape armored,PVC sheath power cable
YJV22 YJLV22(3
3 cores) 20
Approximate Cable Weight Cu kg/km 3796 4252 4829 5834 6885 7807 8995 10493 13381 15564 Al kg/km 3323 3589 3881 4508 5085 5534 6154 6989 8835 9881
3~5mm
Nominal Cable Cross Insulation Sheath Outer Section Area Thickness Thickness Diameter mm2 25 35 50 70 95 120 150 185 240 300 mm 4.5 4.5 4.5 4.5 4.5 4.5 4.5 4.5 4.5 4.5 mm 2.6 2.6 2.8 2.9 3.0 3.1 3.2 3.3 3.6 3.7 mm 53.0 56.0 59.0 63.0 67.0 70.0 74.0 78.0 84.0 89.0
20 D.C.Conductor Resistance Cu /km 0.727 0.524 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 0.0601 Al /km 1.200 0.868 0.641 0.443 0.320 0.253 0.206 0.164 0.125 0.100
Current-loading Capacity
Short Circuit Current
Conductor
Shielding Layer
in the air Cu A 120 140 165 210 355 290 330 375 435 495 Al A 90 110 130 165 200 225 255 295 345 390
to be laid underground Cu A 125 155 180 220 265 300 340 380 435 485 Al A 100 120 140 170 210 235 360 300 345 390
Cu kA 3.69 5.15 7.31 10.2 13.8 17.4 21.7 26.7 34.6 43.1
Al kA 2.42 3.37 4.79 6.68 9.03 11.4 14.2 17.5 22.6 28.2
Cu Tape
kA 2.958 2.958 2.958 2.958 2.958 2.958 3.031 3.031 3.031 3.031
Remarks:The approximate outer diameter of the cable with thin steel wire armor should be larger by 3~5mm on the basis.
19

12/20kV
YJV22 YJLV22 (3
3 cores)
12/20kV 3 cores,XLPE insulation, steel tape armored,PVC sheath power cable
20
Nominal Insulation Sheath Cable Cross Section Thickness Thickness Outer Diameter Area mm 2 25 35 50 70 95 120 150 185 240 300 mm -5.5 5.5 5.5 5.5 5.5 5.5 5.5 5.5 5.5 mm -2.8 2.9 3.0 3.2 3.3 3.4 3.5 3.7 3.9 mm -60.0 63.0 68.0 72.0 75.0 79.0 83.0 89.0 94.0 Approximate Cable Weight 20 D.C.Conductor Resistance
(1
Current-loading Capacity
)
Shielding Layer
Short Circuit Current(1s)
Conductor
in the air Cu kg/km -4659 5430 6327 7446 8382 7906 11954 14027 16437 Al kg/km -3997 4482 5001 5646 6109 6865 8450 9481 10755
3~5mm
to be laid underground Cu A -155 180 220 265 300 340 380 435 485 Al A -120 140 170 210 235 360 300 345 390
Cu /km -0.524 0.387 0.268 0.193 0.153 0.124 0.0991 0.0754 0.0601
Al /km -0.868 0.641 0.443 0.320 0.253 0.206 0.164 0.125 0.100
Cu A -140 165 210 355 290 330 375 435 495
Al A -110 130 165 200 225 255 295 345 390
Cu kA -5.15 7.31 10.2 13.8 17.4 21.7 26.7 34.6 43.1
Al kA -3.37 4.79 6.68 9.03 11.4 14.2 17.5 22.6 28.2
Cu Tape
kA -2.958 2.958 2.958 3.031 3.031 3.031 3.031 3.031 3.031
Remarks:The approximate outer diameter of the cable with thin steel wire armor should be larger by 3~5mm on the basis.
Cable Length 100m 10 5% 30m ; 0.
It should be generally no shorter than 100 meters per piece. The cable no shorter than 30 meters is allowed for delivery, which accounts for no more than 10% of the total. It depends on final both agreements with length error of no more than 0.5%.
20

0.6/1kV
0.6/1kV PVC Insulation Power Cable
0.6/1kV
It is used to transmit and distribute power on the power line of A.C.rated voltage 0.6/1kV.
Executive standard : GB/T12706.1(equal to IEC60502)
GB/T12706.1
IEC60502
Working Conditions 1. 2. 160 3. 0 70 5
1.Long-term working temperature of the cable should be no higher than 70 . 2.The conductor tempeature should be no higher than 160 at time of short circuit (It lasts no more than 5 minutes ). 3.Environment temperature should be no lower than 0 for laying the cable .
Power Cable
Type ,Description &Application Occasion
Type Description Application Occasion
Cu
Al
VV
VLV
PVC insulation & sheath power cable
to be laid indoors, in tunnel, cable furrow, or pipe, the cable couldn t bear mechanical force outside.
VV22
VLV22
PVC insulation, steel tape armor, PVC sheath power cable
to be laid underground , the cable could bear certain mechanical force , but it couldn t bear great pulling force.
: ZR NH
Remarks: We aslo produce flame-retardant type and fire-resistant type power cables.Prefix ‘ZR’ means flame-retardant type,’NH’means fire-resistant type.
Type
mm2
Core Number Nominal Cross-section Area
Cu VV -VV22 VV -VV22 VV -VV22 VV VV22 VV VV22
:
Al -VLV VLV22 -VLV VLV22 -VLV VLV22 VLV VLV22 VLV VLV22
1 2 3 4 3+1
1.5~400 2.5~400 10~400 1.5~185 2.5~185 4~185 1.5~300 2.5~300 4~300 4~185 4~185 4~240 4~185
Remarks:We also produce 5-core cable as user s demand.
21

电线的选择

安全电压分为42V,36V,24V,12V和6V五个等级. 要弄监控摄像头,一个监控摄像头2A,电源线是1.5平方电线,请问如距离250米,距离200米能带多少个监控摄像头,150能带多少个,100米能带多少个. 线路过长线阻增大,载流量会降低的,一般几十米内铜芯电线1.5平方可以载流约9A。可根据有公式求出线阻、再求线损压降。R=电阻率*L/S,(L是长度,S是平方,铜线电阻率为0.0172),U=RI 0.75平方或者1.5平方电线能够安全承担多少个40W的灯泡。 0.75平方电线最大载流量12A, 1.5平方电线最大载流量22A(穿管最大18A). ,40W灯泡电流为40 / 220=0.18 A 最大载流量除以每个灯泡的电流就可以接多少个(必须留一定裕量)"电线负载电流值1平方1.5平方2.5平方4平方 国标GB4706.1-1992/1998规定的电线负载电流值(部分) 1平方铜芯线允许长期负载电流为:6A---8A 1.5平方铜芯线允许长期负载电流为:8A---15A 2.5平方铜芯线允许长期负载电流为:16A---25A 4平方铜芯线允许长期负载电流为:25A---32A

6平方铜芯线允许长期负载电流为:32A---40A 8.家庭电路设计,2000年前,电路设计一般是:进户线4—6 mm2,照明1.5 mm2,插座2.5 mm2,空调4 mm2专线。2000 年后,电路设计一般是:进户线6—10 mm2,照明2.5 mm2,插座4 mm2,空调6 mm2专线。 9.电线重量:1.5平方约重2.2公斤,2.5约重3.3公斤,4平方约重4.8公斤,6平方约重6.8公斤,快递以实际重量为准,只供参考. 电线火线为红色,零线可选颜色有:红、黄、蓝、绿、棕、白、黑、双色几种。单芯电线1.5平方电线,用于灯具照明,单芯电线2.5平方电线,用于插座。单芯电线4平方电线用于3匹空调以上,单芯电线6平方电线用于总进线,双色线用于接地线。二芯、三芯护套电线是做明线使用,多用于工地上施工用,家装不太用到。三芯护套电线2.5平方可用于柜式空调上用。 4平方电线可以承受的最大功率多少2009-03-02 21:19 单相电源1KW约是4.5A,8KW约是36A。4平方电线(独根的塑铜线)载流量约是30A,小一些,换6平方线(单跑电源).你的表和闸都必须换大的。不用这么大功率吧,最小4KW,也可以的。

电缆选型手册范本

目录 一. 概述 (2) 二. 围……………………………………………………………………………2-3 三. 参考标准及参数取值依据 (3) 四. 符号说明………………………………………………………………………3-4 五. IEC 287-3-2/1995标准电力电缆截面经济最佳化计算方法的应用………4-11 六. 电力电缆经济截面最佳化数据查找的使用方法……………………………11-12 七. 电缆经济截面与发热截面总费用比较及投资回收年计算…………………12-15 八. 经济截面的校验条件..................................................................16-17 附录1 铜芯电力电缆综合造价统计表................................................18-19 附录2 电缆造价类别的平均A值 (20) 附录3 电缆型号与电缆造价类别对照表 (20) 附录4-1 铜芯电力电缆经济电流围(I-A类别)………………………………21-23 附录4-2 铜芯电力电缆经济电流围(II-A类别)………………………………24-26 附录4-3 铜芯电力电缆经济电流围(III-A类别)………………………………27-29 附录4-4 铜芯电力电缆经济电流围(IV-A类别)………………………………30-32 附录4-5 铜芯电力电缆经济电流围(V-A类别)……………………………… 33-35 附录5 铜芯电力电缆经济电流密度计算数据及图表(不同电价)...............36-40 附录6 电缆导体交流电阻及感抗......................................................41-42 附录 7 铜芯电力电缆允许载流量表 (42) 附录8 损耗费用辅助量F─Tmax─P关系的统计值 (43) 附录9 最大负载利用小时Tmax与最大负载损耗小时τ和cosΦ的关系 (43) 附录10 不同行业的年最大负载利用小时Tmax,(h) (44) 九. 参考资料 (44)

工程电线电缆种类及选型计算

工程电线电缆种类及选型计算 广义的电线电缆亦简称为电缆。狭义的电缆是指绝缘电缆。它可定义为:由下列部分组成的集合体,一根或多根绝缘线芯,以及它们各自可能具有的包覆层,总保护层及外护层。电缆亦可有附加的没有绝缘的导体。 我国的电线电缆产品按其用途分成下列五大类: 1.裸电线; 2.绕组线; 3.电力电缆; 4.通信电缆和通信光缆; 5.电气装备用电线电缆。 电线电缆的基本结构:

1.导体:传导电流的物体,电线电缆的规格都以导体的截面表示。 2.绝缘:外层绝缘材料按其耐受电压程度。 电(线)缆工作电流计算公式: 单相 I=P÷(U×cosΦ) P-功率(W);U-电压(220V);cosΦ-功率因素(0.8);I-相线电流(A)。 三相 I=P÷(U×1.732×cosΦ) P-功率(W);U-电压(380V);cosΦ-功率因素(0.8);I-相线电流(A)。 一般铜导线的安全截流量为5-8A/平方毫米,铝导线的安全截流量为3-5A/平方毫米。 在单相220V线路中,每1KW功率的电流在4-5A左右,在三相负载平衡的三相电

路中,每1KW功率的电流在2A左右。 也就是说在单相电路中,每1平方毫米的铜导线可以承受1KW功率荷载;三相平衡电路可以承受2-2.5KW的功率。 但是电缆的工作电流越大,每平方毫米能承受的安全电流就越小。 电缆允许的安全工作电流口诀: 十下五(十以下乘以五)。 百上二(百以上乘以二)。 二五三五四三界(二五乘以四,三五乘以三)。 七零九五两倍半(七零和九五线都乘以二点五)。 穿管温度八九折(随着温度的变化而变化,在算好的安全电流数上乘以零点八或零点九)。 铜线升级算(在同截面铝芯线的基础上升一级,如二点五铜芯线就是在二点五铝芯线上升一级,则按四平方毫米铝芯线算)。 裸线加一半(在原已算好的安全电流数基础上再加一半)。 电线电缆规格型号说明:

常用电缆种类及选型计算方法

电缆种类及选型计算 电缆种类及选型计算 一、电缆的定义及分类 广义的电线电缆亦简称为电缆。狭义的电缆是指绝缘电缆。它可定义为:由下列部分组成的集合体,一根或多根绝缘线芯,以及它们各自可能具有的包覆层,总保护层及外护层。电缆亦可有附加的没有绝缘的导体。 我国的电线电缆产品按其用途分成下列五大类: 1.裸电线 2.绕组线 3.电力电缆 4.通信电缆和通信光缆 5.电气装备用电线电缆 电线电缆的基本结构: 1.导体传导电流的物体,电线电缆的规格都以导体的截面表示 2.绝缘外层绝缘材料按其耐受电压程度 二、工作电流及计算 电(线)缆工作电流计算公式: 单相 I=P÷(U×cosΦ)

P-功率(W);U-电压(220V);cosΦ-功率因素(0.8);I-相线电流(A) 三相 I=P÷(U×1.732×cosΦ) P-功率(W);U-电压(380V);cosΦ-功率因素(0.8);I-相线电流(A) 一般铜导线的安全截流量为5-8A/平方毫米,铝导线的安全截流量为3-5A/平方毫米。 在单相220V线路中,每1KW功率的电流在4-5A左右,在三相负载平衡的三相电路中,每1KW 功率的电流在2A左右。 也就是说在单相电路中,每1平方毫米的铜导线可以承受1KW功率荷载;三相平衡电路可以承受2-2.5KW的功率。 但是电缆的工作电流越大,每平方毫米能承受的安全电流就越小。 电缆允许的安全工作电流口诀: 十下五(十以下乘以五) 百上二(百以上乘以二) 二五三五四三界(二五乘以四,三五乘以三) 七零九五两倍半(七零和九五线都乘以二点五) 穿管温度八九折(随着温度的变化而变化,在算好的安全电流数上乘以零点八或零点九) 铜线升级算(在同截面铝芯线的基础上升一级,如二点五铜芯线就是在二点五铝芯线上升一级,

电线电缆种类及选型计算

电线电缆种类及选型计算! 广义的电线电缆亦简称为电缆。狭义的电缆是指绝缘电缆。它可定义为:由下列部分组成的集合体,一根或多根绝缘线芯,以及它们各自可能具有的包覆层,总保护层及外护层。电缆亦可有附加的没有绝缘的导体。 我国的电线电缆产品按其用途分成下列五大类: 1.裸电线; 2.绕组线; 3.电力电缆; 4.通信电缆和通信光缆; 5.电气装备用电线电缆。 电线电缆的基本结构: 1.导体:传导电流的物体,电线电缆的规格都以导体的截面表示。 2.绝缘:外层绝缘材料按其耐受电压程度。

电(线)缆工作电流计算公式: 单相 I=P÷(U×cosΦ) P-功率(W);U-电压(220V);cosΦ-功率因素(0.8);I-相线电流(A)。 三相 I=P÷(U×1.732×cosΦ) P-功率(W); U-电压(380V); cosΦ-功率因素(0.8); I-相线电流(A)。 一般铜导线的安全截流量为5-8A/平方毫米,铝导线的安全截流量为3-5A/平方毫米。在单相220V线路中,每1KW功率的电流在4-5A左右,在三相负载平衡的三相电路中,每1KW功率的电流在2A左右。 也就是说在单相电路中,每1平方毫米的铜导线可以承受1KW功率荷载;三相平衡电路可以承受2-2.5KW的功率。 但是电缆的工作电流越大,每平方毫米能承受的安全电流就越小。

电缆允许的安全工作电流口诀: 十下五(十以下乘以五)。 百上二(百以上乘以二)。 二五三五四三界(二五乘以四,三五乘以三)。 七零九五两倍半(七零和九五线都乘以二点五)。 穿管温度八九折(随着温度的变化而变化,在算好的安全电流数上乘以零点八或零点九)。 铜线升级算(在同截面铝芯线的基础上升一级,如二点五铜芯线就是在二点五铝芯线上升一级,则按四平方毫米铝芯线算)。 裸线加一半(在原已算好的安全电流数基础上再加一半)。

电线电缆选用基本原则

电线电缆选用基本原则 一、电线电缆选用的一般原则 在选用电线电缆时,一般要注意电线电缆型号、规格(导体截面)的选择。 ⒈电线电缆型号的选择 选用电线电缆时,要考虑用途,敷设条件及安全性;例如, 根据用途的不同,可选用电力电缆、架空绝缘电缆、控制电缆等; 根据敷设条件的不同,可选用一般塑料绝缘电缆、钢带铠装电缆、钢丝铠装电缆、防腐电缆等; 根据安全性要求,可选用不延燃电缆、阻燃电缆、无卤阻燃电缆、耐火电缆等。 ⒉电线电缆规格的选择 确定电线电缆的使用规格(导体截面)时,一般应考虑发热,电压损失,经济电流密度,机械强度等选择条件。 根据经验,低压动力线因其负荷电流较大,故一般先按发热条件选择截面,然后验算其电压损失和机械强度;低压照明线因其对电压水平要求较高,可先按允许电压损失条件选择截面,再验算发热条件和机械强度;对高压线路,则先按经济电流密度选择截面,然后验算

其发热条件和允许电压损失;而高压架空线路,还应验算其机械强度。若用户没有经验,则应征询有关专业单位或人士的意见。一般电线电缆规格的选用参见下表: 电线电缆规格选用参考表

说明:1.同一规格铝芯导线载流量约为铜芯的0.7倍,选用铝芯导线可比铜芯导线大一个规格,交联聚乙烯绝缘可选用小一档规格,耐火电线电缆则应选较大规格。 2.本表计算容量是以三相380V、Cosφ=0.85为基准,若单相220V、Cosφ=0.85,容量则应×1/3。 3.当环境温度较高或采用明敷方式等,其安全载流量都会下降,此时应选用较大规格;当用于頻繁起动电机时,应选用大2~3个规格。 4.本表聚氯乙烯绝缘电线按单根架空敷设方式计算,若为穿管或多根敷设,则应选用大2~3个规格。

电力电缆选型手册

电力电缆选型手册.doc 目录一. 概述 2 二. 范围2-3 三. 参考标准及参数取值依据3 四. 符号说明3-4 五. IEC 287-3-2/1995标准电力电缆截面经济最佳化计算方法的应用4-11 六. 电力电缆经济截面最佳化数据查找的使用方法11-12 七. 电缆经济截面与发热截面总费用比较及投资回收年计算12-15 八. 经济截面的校验条件16-17 附录1 铜芯电力电缆综合造价统计表18-19 附录 2 电缆造价类别的平均 A 值20 附录3 电缆型号与电缆造价类别对照表20 附录4-1 铜芯电力电缆经济电流范围I-A 类别21-23 附录4-2 铜芯电力电缆经济电流范围II-A 类别24-26 附录4-3 铜芯电力电缆经济电流范围III-A 类别27-29 附录4-4 铜芯电力电缆经济电流范围IV-A 类别30-32 附录4-5 铜芯电力电缆经济电流范围V-A 类别33-35 附录5 铜芯电力电缆经济电流密度计算数据及图表不同电价36-40 附录6 电缆导体交流电阻及感抗41-42 附录7 铜芯电力电缆允许载流量表42 附录8 损耗费用辅助量F─Tmax─P 关系的统计值43 附录9 最大负载利用小时Tmax 与最大负载损耗小时τ 和cosΦ 的关系43 附录10 不同行业的年最大负载利用小时Tmax,h 44 九. 参考资料44电力电缆经济选型实用手册一.概述导体的经济电流密度是选择导体的必要条件之一。 当选择导体的诸多技术条件如发热温升、机械强度及电压降要求等得到控制或改善时,往往是经济电流密度起着支配作用。 实践证明,经济电流密度对于选择导体进而节省能源,改善环

电缆卷筒选型

电缆卷筒的选型 乔敏 电缆卷筒又称电缆卷盘或电缆卷线器,以其安装空间小、维护方便、使用可靠及成本低等特点取代滑触线而成为移动传输领域(动力、数据及流体介质)的主流解决方案。 一、卷筒的分类 电缆卷筒根据驱动形式分为非电动式和电动式两大类;按电缆排列方式分为轴向单排和轴向多排两种;按集电滑环位置分为滑环内装式和滑环外装式两种形式;按卷绕材料分为电缆卷筒和软管卷筒。其中非电动式包括:弹力(TA)式、重锤(ZC)式、磁耦合式(JQC);电动式包括:磁耦合式(JQD)、力矩电机式(KDO)、磁滞式(CZ)和变频控制式(BP)。 二、卷筒设计参数 电缆卷筒的技术难点是要保证卷绕速度与设备移动速度的同步,同时还要保证卷绕过程中电缆所受拉力适中。因此,电缆卷筒设计时应综合考虑以下因素: 1、电缆规格及种类: 电缆截面积从1.0~240mm2,电缆外径直接影响卷盘的轴向尺寸及动力需求。电缆截面超过35 mm2时不应选择非电动式卷筒(配重式可放宽至50 mm2),扁电缆只能选用轴向单排的卷盘。电缆应选择YCW型(动力电缆)和CEFR型(控制信号电缆)等,较柔软且有一定的抗拉强度。电缆的外径和单重力求准确。 2、卷绕长度: 影响卷盘的径向尺寸及动力需求,长度越长,对动力要求越高。非电动式电缆卷筒难以完成大行程的卷绕。地面电源锚位也直接影响电缆卷筒的选型,常见的电源锚位有端部供电和中点供电两种。中点供电不能选择非电动磁耦合式(JQC系列)。 3、设备移动速度 影响电动式电缆卷筒的电动机功率和传动比。当设备移动速度超过60米/分时,应选择变频控制式(BP系列)。 4、装机高度 影响电动式电缆卷筒的电动机功率,安装高度越高,对动力需求越大。安装时不能超过设计要求。 以上4个参数是电缆卷筒设计选型的依据,应综合考虑,还应电缆卷筒的结构与布置方式,以满足实际工况需求。 三、卷筒原理、性能及应用范围 1、弹力式(TA系列) a. 工作原理: 弹力式电缆卷筒的工作原理与钢卷尺相似,利用蜗卷弹簧为动力来收卷电缆。当电缆被拉出时,收紧蜗卷弹簧而储能,当外力撤消时,弹簧释能,卷筒将自动收卷电缆。 b. 性能及特点: 安装简单,同步性能好,电缆张力小,但弹簧易疲劳,使用寿命短。 c. 适用范围: 适用电缆:截面积35mm2以下的动力电缆和24芯以下的信号电缆; 卷绕长度:不超过30m; 适用设备:如电磁吸盘、抓斗、电动台车等。 2、重锤式(ZC系列) a. 工作原理: 重锤式电缆卷线筒是利用重锤被提升而储能的原理,自动卷取电缆的机械装置。当拉出电缆时,带动电缆卷盘旋转,从而带动与电缆卷筒同轴相联的钢丝绳卷筒转动,提升重锤而

电缆的种类和选型

电缆种类及选型计算 一、电缆的定义及分类 广义的电线电缆亦简称为电缆。狭义的电缆是指绝缘电缆。它可定义为:由下列部分组成的集合体,一根或多根绝缘线芯,以及它们各自可能具有的包覆层,总保护层及外护层。电缆亦可有附加的没有绝缘的导体。 我国的电线电缆产品按其用途分成下列五大类:1.裸电线 2.绕组线 3.电力电缆 4.通信电缆和通信光缆 5.电气装备用电线电缆 电线电缆的基本结构: 1.导体传导电流的物体,电线电缆的规格都以导体的截面表示 2.绝缘外层绝缘材料按其耐受电压程度 二、工作电流及计算 电(线)缆工作电流计算公式: 单相 I=P÷(U×cosΦ)

P-功率(W);U-电压(220V);cosΦ-功率因素 (0.8);I-相线电流(A) 三相 I=P÷(U×1.732×cosΦ) P-功率(W);U-电压(380V);cosΦ-功率因素 (0.8);I-相线电流(A) 一般铜导线的安全截流量为5-8A/平方毫米,铝导线的安全截流量为3-5A/平方毫米。 在单相220V线路中,每1KW功率的电流在4-5A左右,在三相负载平衡的三相电路中,每1KW功率的电流在2A左右。 也就是说在单相电路中,每1平方毫米的铜导线可以承受1KW功率荷载;三相平衡电路可以承受 2-2.5KW的功率。 但是电缆的工作电流越大,每平方毫米能承受的安全电流就越小。 电缆允许的安全工作电流口诀: 十下五(十以下乘以五) 百上二(百以上乘以二)

二五三五四三界(二五乘以四,三五乘以三) 七零九五两倍半(七零和九五线都乘以二点五) 穿管温度八九折(随着温度的变化而变化,在算好的安全电流数上乘以零点八或零点九) 铜线升级算(在同截面铝芯线的基础上升一级,如二点五铜芯线就是在二点五铝芯线上升一级,则按四平方毫米铝芯线算) 裸线加一半(在原已算好的安全电流数基础上再加一半) 三、常用电(线)缆类型 线缆规格型号含义: 电线型号中:字母B表示布电线,字母V表示塑料中的聚氯乙烯,字母R表示软线(导体为很多细丝绞在一起)。还有铜芯符号、硬线(常见的单芯导体)符号省略没有表示。 常用线缆类型: BV-表示单铜芯聚氯乙烯普通绝缘电线,无护套线。适用于交流电压450/750V及以下动力装置、日用电器、仪表及电信设备用的电线电缆。

电线电缆绝缘材料的选择

电线电缆绝缘材料的选择 10.0 PVC胶粒
10.1 基本配方
VC粉:主体一般常用S60、S65、S70﹔
可塑剂:主要目的在调整软硬度,提高耐寒绝缘等作用﹔
填充剂:目的在增强加热,光之安全性,及绝缘性﹔
改质剂:依特性要求添加﹔
安定剂:抑制PVC内之少量游离Cl-分解﹔
防火剂:增强耐烧性﹔
染颜料:颜色调配。
10.2 硬度
国际上常以shore A表示之,而国内软硬度常以P%表示,例如:50kg之PVC料,可塑剂40kg时是以80P,50gPVC料,可塑剂55kg时是以110P表示即可塑剂愈多P数愈大,PVC 胶粒愈软而萧氏硬度(shore A)度数愈大,PVC胶粒愈硬。
10.3 移行说明
电气用品之外壳……等常用的塑料材质大部份为PS,ABS,HIPS,电线为PVC塑材料时,由于含有可塑剂(软化剂),而有此可塑剂会移行者,会将PS,ABS,HIPS塑料壳侵蚀,因此有非移行的要求,也就是PVC材料不能移。
10.3.1 移行的试验方法
将试片(ABS,或PS或HIPS)两片(长50x宽50x厚20mm),中间夹PVC电线,再上下两层用玻璃盖住并用500±5g砝码压住,施以不同时间(24,48,72小时)不同温度(50℃,60℃,70±2℃)之条件下,测试(条件由客户设定),测试后取出试片,用肉眼观察,试片上不能很轻易的看出痕迹,亦即需极费眼力才能看出来。
ABS = Acrylonitrile Butadiene Styrene Terpolymer
苯乙烯,丁二烯,丙烯,参聚合体
S = POL YSTRRENE 聚苯乙烯
HIPS = High Impact Polystyrene 高冲击聚苯乙烯
10.3.2 PVC胶粒应具下列性质
耐热性( Thermal Stability ) ﹔
硬度( Hardness )﹔
安全性( Safety )﹔
老化性( Aging Properties ) ﹔
机械性质( Mechanical Properties )﹔
耐燃性( non-flammability )﹔
电气特性( Electrical Properties )﹔
耐候性( Weather ability )﹔
光安定性( Light Stability )﹔
低温特性( Low Temperature Properties )。
11.0 塑料常用特性名词解释
11.1 抗张强度:(Tensile Strength)
将试样(如哑铃片……等)拉断时所需要之应力,用之单位为PSI或kg/mm2。
11.2 热变形(Heat Distortion)
将材料适当的取样后,将其加热至一定之温度后,试验该材料之外形改变情况。其计算公式如下:
11.3 热冲击(Heat Shock)——试验材料稳定性方法之一,将材料在特定的时间内卷绕于规定之圆棒上,暴露于高温中,不得有龟裂现象发生。
11.4 冷弯(Cold Bend)——将电缆之试样绕在规定之圆棒(Mandrel)上,而置于特定温度之冷室中,通常为零下之温度。再将试样取出作弯曲试验,则可试验出材料之破坏程度或有无缺点。
11.5 延伸(Elongation)——试样拉断时的伸长情形
11.6 焊接性(日文:半田性)——PVC芯线等在焊接或热镀时其塑料部份后缩收,所以其材质要经X—RAY处理成架桥,或改其塑料本身性质,如:SR—PVC。
11.7 老化(Aging)——仿真电缆经长时间的使用后,其物理性(抗张延伸)改变的情形。
11.8 额定温度(Temperature Rating)——绝缘材料在连续使用之情况下,其基本特性不会发生变化或损失时,所能容许之最高温度。如交连PE 为90℃,PVC有60℃,75℃,90℃,105℃,PE为75℃等。
11.9 额定电压(V oltage Rating)——依照规定或标准可连续实施于各种电缆电缆之最高允许电压。
11.10 绝缘阻抗(Insulation Resistance)——加于绝缘体两极间之电压与电流之比,以公式表示为R=E/I,其单位一般用MΩ(百万欧姆表示之)。
11.11 耐电压(介质强度)(DielectricStrength)——绝缘材质在破坏之前所能承受之电压,介质强度在材料中是一个非常重要特性,在同一种耐电压情况下,介质强度好的材质,其绝缘厚度可以较薄。
12.0 塑料之耐燃测试
依UL规定UL Standard 94 分为水平燃烧(94—HB)及垂直燃烧
94V-0,94V-1,94V-2。
13.0 发泡
目的:在改变或降低成品的电容(介电常数)并使成品轻量化,小型化,进而节省材料,达到提高品质与降低成本的最终目的,一般常用方法
(a) 物理发泡
(b) 化学发泡,化学发泡在加热过程中,发泡剂分解

所有电缆规格型号解释

【引用】所有电缆规格型号解释 2011-04-14 08:45:23| 分类:默认分类 | 标签: |字号大中小订阅 本文引用自流学《所有电缆规格型号解释》 电力电缆的型号及品种主要有以下几个方面35kV及以下电力电缆型号及产品表示方法 1.用汉语拼音第一个字母的大写表示绝缘种类、导体材料、内护层材料和结构特点。如用Z代表纸(zhi);L代表铝(lv);Q代表铅(qian);F代表分相(fen);ZR代表阻燃(zuran);NH代表耐火(naihuo)。 2.用数字表示外护层构成,有二位数字。无数字代表无铠装层,无外被层。第一位数字表示铠装,第二位数字表示外被,如粗钢丝铠装纤维外被表示为41。 3.电缆型号按电缆结构的排列一般依次序为:绝缘材料;导体材料;内护层;外护层。; 4.电缆产品用型号、额定电压和规格表示。其方法是在型号后再加上说明额定电压、芯数和标称截面积的阿拉伯数字。如VV42-10 3×50表示铜芯、聚氯乙稀绝缘、粗钢线铠装、聚氯乙稀护套、额定电压10kV、3芯、标称截面积50mm2的电力电缆。 电力电缆型号各部分的代号及其含义 1.绝缘种类:V代表聚氯乙稀;X代表橡胶;Y代表聚乙烯;YJ代表交联聚乙烯;Z代表纸。 2.导体材料:L代表铝;T(省略)代表铜。 3.内护层:V代表聚氯乙稀护套;Y聚乙烯护套;L铝护套;Q铅护套;H橡胶护套;F氯丁橡胶护套。 4.特征:D不滴流;F分相;CY充油;P贫油干绝缘;P屏蔽;Z直流。 5.控制层:0无;2双钢带;3细钢丝;4粗钢丝。 6.外被层:0无;1纤维外被;2聚氯乙稀护套;3聚乙烯护套。 7.阻燃电缆在代号前加ZR;耐火电缆在代号前加NH。 充油电缆型号及产品表示方法 充油电缆型号由产品系列代号和电缆结构各部分代号组成。自容式充油电缆产品系列代号CY。外护套结构从里到外用加强层、铠装层、外被层的代号组合表示。绝缘种类、导体材料、内护层代号及各代号的排列次序以及产品的表示方法与35kV及以下电力电缆相同。如CYZQ102 220/1×4表示铜芯、纸绝缘、铅护套、铜带径向加强、无铠装、聚氯乙稀护套、额定电压220kV、单芯、标称截面积400mm2的自容式充油电缆。充油电缆外护层代号含义为 1.加强层:1代表铜带径向加强;2代表不锈钢带径向加强;3钢带径向加强;4不锈钢带径向、窄不锈钢带纵向加强。 2.铠装层:0无铠装;2钢带铠装;4粗钢丝铠装。 3.外被层:1纤维层;2聚氯乙稀护套;3聚乙烯护套。 一、电线平方数及直径换算方法知识 电线的规格在国际上常用的有三个标准:分别是美制(AWG)、英制(SWG)和我们的(CWG)。 几平方是国家标准规定的的一个标称值,几平方是用户根据电线电缆的负荷来选择电线电缆。 电线平方数是装修水电施工中的一个口头用语,常说的几平方电线是没加单位,即平方毫米。 电线的平方实际上标的是电线的横截面积,即电线圆形横截面的面积,单位为平方毫米。 一般来说,经验载电量是当电网电压是220V时候,每平方电线的经验载电量是一千瓦左右。 铜线每个平方可以载电1-1.5千瓦,铝线每个平方可载电0.6-1千瓦。因此功率为1千瓦的电器只需用一平方的铜线就足够了。 具体到电流,短距送电时一般铜线每平方可载3A到5A的电流。散热条件好取5A/平方毫米,不好取3A/平方毫米。

电缆桥架类型分析 标准型号及设计选型

电缆桥架类型分析标准型号及设计选型 用途:电缆桥架适用于电压10千伏以下的电力电缆以及控制电缆、照明配线等室内、室外架空电缆沟、隧道的敷设。 优点:桥架具有品种全、应用广、强度大、结构轻、造价低、施工简单、配线灵活、安装标准、外形美观、维护检修方便等。 一、种类: 1.按材料分 1)钢质电缆桥架(不锈钢) 2)铝合金电缆桥架 3)玻璃钢电缆桥架(手糊和机压两种) 4)防火阻燃桥架(阻燃板(无机)、阻燃板加钢质外壳、钢质加防火涂料) 2.按形式分 1)槽式 2)托盘式 3)梯级式 4)组合式 3.按表面处理分 1)冷镀锌及锌镍合金 2)喷塑 3)喷漆 4)热镀锌 5)热喷锌 二、执行标准: 1.JB/T10216-2000《电控配电用电缆桥架》 2.企业标准:Q/321182AEG001-1997 3.QB/T1453-92电缆桥架 4.JB/T6743-93户内户外钢制电缆桥架防腐环境技术要求 5.DB32/144-1996电缆用防火槽合 标准适用范围:有于工业与民用建筑室内外、高低压输配电工程的电缆桥架。

三、技术条件: 1.正常使用条件 1)安装地点的海拔高度不超过2000米。 2)不同气候的环境选用不同气候环境等级的参数、按温度、湿度、防火等情况选定。2.特殊使用条件 1)敷设在不同化学腐蚀环境:盐雾、硫化氢、氯化氢等。 2)敷设在消防线路中。 3)敷设在海拔2000米以上。 3.电缆桥架的结构要求 1)防护等级:无孔托盘(槽式)户内不低于IP30 户外不低于IP33 2)防护等级:耐火桥架户内不低于IP40 户外不低于IP44 材料应符合自身的相关标准 钢制宜采用冷轧钢板GB/T700-1988 GB/T11253 铝制GB/T3880和GB/6892 玻璃钢GB/T15568 耐火桥架GB8624-1997中B级 3)常用规格 高40 50 60 80 100 150 200 宽60 80 100 150 200 250 300 400 500 600 800 1000 1200 4)板材厚度 钢制桥架允许最小板厚: 宽B 允许最小板厚& B1<00 1.0 100≤B<150 1.2 150≤B<400 1.5 400≤B≤800 2.0 800<B<1000 2.5 1000<B<1200 3.0 连接片的厚度至少按桥架同等板厚选用也可选厚一个等级 盖板的板厚可以按桥架的厚度选低一个等级

电线电缆的选型及方法

电线电缆的选型及方法 ⒈型号的选择 选用电线电缆时,要考虑用途,敷设条件及安全性等; 根据用途的不同,可选用电力电缆、架空绝缘电缆、控制电缆等; 根据敷设条件的不同,可选用一般塑料绝缘电缆、钢带铠装电缆、钢丝铠装电缆、防腐电缆等; 根据安全性要求,可选用阻燃电缆、无卤阻燃电缆、耐火电缆等。 ⒉电线电缆规格的选择 确定电线电缆的使用规格(导体截面)时,应考虑发热,电压损失,经济电流密度,机械强度等条件。 根据经验,低压动力线因其负荷电流较大,故一般先按发热条件选择截面,然后验算其电压损失和机械强度;低压照明线因其对电压水平要求较高,可先按允许电压损失条件选择截面,再验算发热条件和机械强度;对高压线路,则先按经济电流密度选择截面,然后验算其发热条件和允许电压损失;而高压架空线路,还应验算其机械强度。若用户没有经验,则应征询有关专业单位或人士的意见。一般电线电缆规格的选用参见下表: 电线电缆规格选用参考表

3、同一规格铝芯导线载流量约为铜芯的0.7倍,选用铝芯导线可比铜芯导线大一个规格,交联聚乙烯绝缘可选用小一档规格,耐火电线电缆则应选较大规格。 4、本表计算容量是以三相380V、Cosφ=0.85为基准,若单相220V、Cosφ=0.85,容量则应× 1/3。 3、当环境温度较高或采用明敷方式等,其安全载流量都会下降,此时应选用较大规格;当用于頻繁起动电机时,应选用大2~3个规格。 5、本表聚氯乙烯绝缘电线按单根架空敷设方式计算,若为穿管或多根敷设,则应选用大2~3个规格。 6、以上数据仅供参考,最终设计和确定电缆的型号和规格应参照有关专业资料或电工手册。 7.运输中严禁从高处扔下电缆或装有电缆的电缆盘,特别是在较低温度时(一般为5℃左右及以下),扔、摔电缆将有可能导致绝缘、护套开裂。 8.尽可能避免在露天以裸露方式存放电缆,电缆盘不允许平放。 9.吊装包装件时,严禁几盘同时吊装。在车辆、船舶等运输工具上,电缆盘要用合适方法加以固定,防止互相碰撞或翻倒,以防止机械损伤电缆。 10.电缆严禁与酸、碱及矿物油类接触 ,要与这些有腐蚀性的物质隔离存放.贮存

民用建筑电气设计中电线电缆的选型及敷设要求86779

民用建筑电气设计中电线电缆的选型及敷设要求 发布日期:2015-04-29 来源:《电气&智能建筑》作者:张晓萍张渊张哲 核心提示:文章梳理了住宅建筑电气设计中电线电缆的选型,简述除住宅外其它民用建筑电气设计中电线电缆的选型;并探讨配电线路的敷设要求。 1 前言 电线电缆作为建筑电气不可或缺的组成部分,它的运用范围极其广泛。随着建筑物内电气负荷的日益增长,线缆燃烧造成的电气火灾也频繁发生。同时,一旦火灾发生,消防设备的安全可靠运行,也需要电线电缆的保障。因此,建筑电气中电线电缆的选用,不仅关系到用电设备的正常使用,关系到建筑电气的工程造价,更重要的是关系到电气使用的安全性,甚至建筑内人员的人身安全。本文更多的从消防的角度结合工程经验,根据《电力工程电缆设计规范》、《住宅建筑电气设计规范》、《民用建筑电气设计规范》、《建筑设计防火规范》等国家规范和上海市工程建设规范《民用建筑电线电缆防火设计规程》的规定,按普通、消防负荷两部分,从消防供电干线、应急照明和火灾自动报警等三方面,梳理了各级别民用建筑应选用的电线电缆型式及其敷设方式。 2 常用电力电缆类型 在目前的建筑电气设计中,常用的线缆可分为以下几类:普通线缆、阻燃线缆、耐火线缆、无卤低烟线缆和矿物绝缘电缆。对应上述的各类线缆,不同的厂家有不同的产品,但基本的要求和定义是一致的。本文仅列举笔者设计中常用的线缆类型。 (1)普通线缆 主要指聚氯乙烯绝缘电线BV线和交联聚乙烯绝缘聚氯乙烯护套绝缘电力电缆YJV. (2)阻燃线缆 难以着火并具有阻止或延缓火焰蔓延能力的电线电缆。该线缆通常指能通过GB/T183 80.3(等同IEC60332-3)试验合格的电线电缆。包括具有阻燃性的聚氯乙烯绝缘电线ZRB V线和具有阻燃性的交联聚乙烯绝缘聚氯乙烯护套绝缘电力电缆ZRYJV. (3)耐火线缆 在规定温度和时间的火焰燃烧下,仍能保持线路完整性的电线电缆。通常指通过GB/T12666.6(等效IEC60331)试验合格的电线电缆。包括具有耐火性的聚氯乙烯绝缘电线N HBV线和具有耐火性的交联聚乙烯绝缘聚氯乙烯护套绝缘电力电缆NHYJV. (4)无卤低烟线缆

电线电缆选用的一般原则

简介:在选用电线电缆时,一般要注意电线电缆型号、规格(导体截面)的选择。 一、电线电缆选用的一般原则 在选用电线电缆时,一般要注意电线电缆型号、规格(导体截面)的选择。 ⒈电线电缆型号的选择 选用电线电缆时,要考虑用途,敷设条件及安全性;例如, 根据用途的不同,可选用电力电缆、架空绝缘电缆、控制电缆等; 根据敷设条件的不同,可选用一般塑料绝缘电缆、钢带铠装电缆、钢丝铠装电缆、防腐电缆等; 根据安全性要求,可选用不延燃电缆、阻燃电缆、无卤阻燃电缆、耐火电缆等。 ⒉电线电缆规格的选择 确定电线电缆的使用规格(导体截面)时,一般应考虑发热,电压损失,经济电流密度,机械强度等选择条件。 根据经验,低压动力线因其负荷电流较大,故一般先按发热条件选择截面,然后验算其电压损失和机械强度;低压照明线因其对电压水平要求较高,可先按允许电压损失条件选择截面,再验算发热条件和机械强度;对高压线路,则先按经济电流密度选择截面,然后验算其发热条件和允许电压损失;而高压架空线路,还应验算其机械强度。若用户没有经验,则应征询有关专业单位或人士的意见。一般电线电缆规格的选用参见下表: 电线电缆规格选用参考表

说明: 1.同一规格铝芯导线载流量约为铜芯的0.7倍,选用铝芯导线可比铜芯导线大一个规格,交联聚乙烯绝缘可选用小一档规格,耐火电线电缆则应选较大规格。 2.本表计算容量是以三相380V、Cosφ=0.85为基准,若单相220V、 Cosφ=0.85,容量则应×1/3。 3.当环境温度较高或采用明敷方式等,其安全载流量都会下降,此时应选用较大规格;当用于頻繁起动电机时,应选用大2~3个规格。 4.本表聚氯乙烯绝缘电线按单根架空敷设方式计算,若为穿管或多根敷设,则应选用大2~3个规格。 5 以上数据仅供参考,最终设计和确定电缆的型号和规格应参照有关专业资料或电工手册。 二、电线电缆的使用特性 产品使用特性详见具体产品目录。 三、电线电缆的运输和保管 ⒈运输中严禁从高处扔下电缆或装有电缆的电缆盘,特别是在较低温度时(一般为5℃左右及以下),扔、摔电缆将有可能导致绝缘、护套开裂。 ⒉尽可能避免在露天以裸露方式存放电缆,电缆盘不允许平放。

常见电线电缆的规格型号、电气安装配管符号表示方法

配电系统图符号母含义、常见电线电缆的规格型号、电气安装配管符号表示方法配电系统图怎么看,符号,字母含义等 从电源引入端开始向配出端顺序看: 1、SCB10-2000 10/0.4 D/Yn11 干式变压器,10KV/0.4KV,容量2000KVA,高压侧三角形接法,低压侧为星形接法,连接组别为D/Yn11(星三角11点接法); 2、TMY-3[2*(125*10)]+1*(125*10) 低压进线柜主母线或低压水平母线规格,125*10硬铜排,3条相线为双排,PEN为单排; 3、MT40H1/3P MIC5.0 I=3200A 低压总进线自动(万能)断路器,施耐德品牌,电流规格4000A,整定电流(长延时)3200A,性能要求查厂家样本; 4、4000/5A 进线侧电流互感器变比,4000/5 5、NS100H/3P I=100A GPU3-60II 浪涌保护辅助回路,配施耐德NS100H/3P开关、GPU3-60II浪涌吸收保护器; 6、D1:MNS 1000*1000*2200 低压柜编号、型号,MNS系列,进线柜尺寸为1000宽、1000深、2200高; 7、D2、D3:无功功率补偿 电容补偿柜 8、GLR-1250/3P,ZWK ARC-12/J 带熔断器隔离开关1250A/3P,无功功率自动补偿控制器(安科瑞品牌)12路; 9、FYS-0.22 浪涌吸收保护(避雷器); 10、NT100-100A 熔断器,100A; 11、LC1-DPK12M7C 施耐德产接触器,需要查产品样本(略),用于自动切换电容器组; 12、FK-Dr30/440/7 电容器组回路串接电抗器,防止瞬间切换过电流; 13、10*MKPg0.44-30-3 10组电容器,MKPg0.44型号,30KVar、三相; 14、D7,含4套NS系列断路器 低压出线柜,NS400N/3P 200A表示施耐德NS400N断路器,400A框架,整定电流为200A; 15、112KW WDZA-YJY-4*185+E95 该出线回路为112KW负荷,出线电缆为无卤低烟A级阻燃(交联聚乙烯绝缘、交联聚乙烯护套),规格为4*185+E95,E95表示PE线规格95; 16、ACR220E、300/5 安科瑞品牌仪表(出线回路电流表),配300/5电流互感器; 17、D9,含MT25H1/3P MIC5.0 I=1600A及2000/5A 低压母联柜,断路器为MT25H1/3P MIC5.0,整定电流1600A,配2000/5A电流互感器。 18、标注:3-7-N3之类 不同的设计人员有不同的习惯,这里表示第3套变配电系统(对应变压器T3)、第7面低压柜、第3条出线回路(该柜内的第3个抽屉); 19、补充

电缆种类及选型选择

电缆种类及选型选择

————————————————————————————————作者:————————————————————————————————日期:

电缆种类及选型计算 电缆种类及选型计算 一、电缆的定义及分类 广义的电线电缆亦简称为电缆。狭义的电缆是指绝缘电缆。它可定义为:由下列部分组成的集合体,一根或多根绝缘线芯,以及它们各自可能具有的包覆层,总保护层及外护层。电缆亦可有附加的没有绝缘的导体。 我国的电线电缆产品按其用途分成下列五大类: 1.裸电线 2.绕组线 3.电力电缆 4.通信电缆和通信光缆 5.电气装备用电线电缆 1、电力电缆 产品主要用在发、配、输、变、供电线路中的强电电能传输,通过的电流大(几十安至几千安)、电压高(220V至500kV及以上)。产品主要特征是:在导体外挤(绕)包绝缘层,如架空绝缘电缆,或几芯绞合(对应电力系统的相线、零线和地线),如二芯以上架空绝缘电缆,或再增加护套层,如塑料/橡套电线电缆。主要的工艺技术有拉制、绞合、绝缘挤出(绕包)、成缆、铠装、护层挤出等,各种产品的不同工序组合有一定区别。 2、通讯电缆及光纤 随着近二十多年来,通讯行业的飞速发展,产品也有惊人的发展速度。从过去的简单的电话电报线缆发展到几千对的话缆、同轴缆、光缆、数据电缆,甚至组合通讯缆等。该类产品结构尺寸通常较小而均匀,制造精度要求高。 3、裸电线及裸导体制品 此类产品主要用在城郊、农村、用户主线、开关柜等。主要特征是:纯的导体金属,无绝缘及护套层,如钢芯铝绞线、铜铝汇流排、电力机车线等;加工工艺主要是压力加工,如熔炼、压延、拉制、绞合/紧压绞合等

电线及电缆截面的选择及计算

低压导线截面的选择,有关的文件只规定了最小截面,有的以变压器容量为依据,有的选择几种导线列表说明,在供电半径上则规定不超过。本文介绍一种简单公式作为导线选择和供电半径确定的依据,供电参考。 1 低压导线截面的选择 选择低压导线可用下式简单计算: S=PL/CΔU%(1) 式中P——有功功率,kW; L——输送距离,m; C——电压损失系数。 系数C可选择:三相四线制供电且各相负荷均匀时,铜导线为85,铝导线为50;单相220V供电时,铜导线为14,铝导线为。 (1)确定ΔU%的建议。根据《供电营业规则》(以下简称《规则》)中关于电压质量标准的要求来求取。即:10kV及以下三相供电的用户受电端供电电压允许偏差为额定电压的±7%;对于380V则为407~354V;220V单相供电,为额定电压的+5%,-10%,即231~198V。就是说只要末端电压不低于354V和198V就符合《规则》要求,而有的介绍ΔU%采用7%,笔者建议应予以纠正。 因此,在计算导线截面时,不应采用7%的电压损失系数,而应通过计算保证电压偏差不低于-7%(380V线路)和-10%(220V 线路),从而就可满足用户要求。 (2)确定ΔU%的计算公式。根据电压偏差计算公式,Δδ%

=(U2-U n)/U n×100,可改写为:Δδ=(U1-ΔU-U n)/U n,整理后得: ΔU=U1-U n-Δδ.U n (2) 对于三相四线制用(2)式:ΔU=400-380-(-×380)=,所以ΔU%=ΔU/U1×100=400×100=;对于单相220V,ΔU=230-220-(-×220)=32V,所以ΔU%=ΔU/U1×100=32/230×100=。 低压导线截面计算公式 三相四线制:导线为铜线时, S st=PL/85×=×10-3mm2(3) 导线为铝线时, S sl=PL/50×=×10-3mm2(4) 对于单相220V:导线为铜线时, S dt=PL/14×=×10-3mm2(5) 导线为铝线时, S dl=PL/×=×10-3mm2(6) 式中下角标s、d、t、l分别表示三相、单相、铜、铝。所以只要知道了用电负荷kW和供电距离m,就可以方便地运用(3)~(6)式求出导线截面了。如果L用km,则去掉10-3。 需说明的几点 用公式计算出的截面是保证电压偏差要求的最小截面,实际选用一般是就近偏大一级。再者负荷是按集中考虑的,如果负荷分散,所求截面就留有了一定裕度。 考虑到机械强度的要求,选出的导线应有最小截面的限制,